earth_america
user_standard Accedi
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concetto

Concetto


Prodotti: MP-V
Funzionalità: Hardware
Versione del prodotto: 3.3, 2022, 2023, 2024, 7.0
23/07/2021

MP-V Built-in Power Supply

The MP-V has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz input power.

The built-in power supply is based on a half-wave rectified, non-isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

To power the controller, use a Class 2 (EN 60742) transformer supplying a nominal 24 VAC at 50/60 Hz. Per maggior informazioni, consulta MP-V Controllers .

A separate, local 24 VAC step-down transformer is recommended to power each BACnet/IP device. The transformer with appropriate VA rating may also be used to power the locally connected I/O devices. The separate transformer helps to avoid problems with ground loops, 24 VAC induced EMI on LAN, low or distorted AC voltage level at the controller, and excess transformer load due to the half-wave power supply, which can result in intermittent equipment detected faults, loss of communications, or equipment damage.

Avviso

EQUIPMENT DAMAGE

Use a separate, local 24 VAC step-down transformer to power each BACnet/IP device.

Failure to follow these instructions can result in equipment damage.

Avviso

CONTROLLER DEVICE DAMAGE

Do not power the SpaceLogic device with a 24 VAC transformer that is used to power devices that contain non-isolated full-wave rectifier power supplies.

Failure to follow these instructions can result in equipment damage.

  • Hardware Overview
  • MP-V Controllers