Concept

Concept


Produits : MP-C
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
24/11/2023

Triac Outputs

arrow1_rotationOutputs arrow1_rotationSpécifications

The triac outputs can be used in many applications to switch 24 VAC on or off for external loads such as actuators, relays, or indicators. Triacs are silent and do not suffer from relay contact wear.

The outputs can be configured as one of the following types:

  • Digital output

  • Digital pulsed output

  • Pulse width modulated output

  • Tristate output

  • Tristate pulsed output

Outputs

The DO triac outputs are designed to switch 24 VAC. The common terminals can be connected to 24 VAC or to ground. The DO triac outputs share common terminals as follows:

  • DO1 and DO2 share common terminal COM1 (on MP-C-15A, -18A, and -18B).

  • DO3 and DO4 share common terminal COM2 (on MP-C-15A, -18A, and -18B).

  • DO5 and DO6 share common terminal COM3 (on MP-C-15A and -18B).

  • DO7 and DO8 share common terminal COM4 (on MP-C-18B).

The terminals are opto-isolated from the controller.

 
action_zoom_plus_stroke Triac output internal configuration
Figure : Triac output internal configuration

R V1 and R V2 are varistors (95 V, 2 J) for protection of the triac.

R 1 = 47 ohm

C 1 = 22 nF

Déclaration

Optionally, to protect the triac outputs from damage in the event of external wiring short circuit, you can connect an in-line fuse (3 A) in series with the COM terminal.

Spécifications

Channels, MP-C-15A
6, DO1 to DO6
Channels, MP-C-18A
4, DO1 to DO4
Channels, MP-C-18B
8, DO1 to DO8
Channels, MP-C-24A
0
Channels, MP-C-36A
0
Channels, MP-C-24A-M
0
Channels, MP-C-36A-M
0
Output rating (for each triac output)
Max. 0.5 A
Voltage
24 VAC +/-20 %
Commons
COM1 for DO1 and DO2 (on MP-C-15A, -18A, -18B)
  
COM2 for DO3 and DO4 (on MP-C-15A, -18A, -18B)
  
COM3 for DO5 and DO6 (on MP-C-15A, -18B)
  
COM4 for DO7 and DO8 (on MP-C-18B only)
The common terminals can be connected to 24 VAC or to ground.
Common voltage, high side output
24 VAC
Common voltage, low side output
0 VAC (ground)
Minimum pulse width
100 ms
Triac output protection
MOV and snubber across each triac output
  
MOV from triac COM to ground