earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Comment faire pour

Comment faire pour


Produits : IP-IO , MP-C
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
20/06/2023

Installing MP-C Display

You install an MP-C Display module on the MP-C or IP-IO module to enable manual override control of the analog and digital outputs. The MP-C Display module cannot be removed.

Afficher plus
action_close

The MP-C can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

Installation orientation restrictions

The restrictions on installing the device in various orientations differ between the different MP-C controller models ( Pour plus d'informations, voir MP-C Models .). In this regard, the MP-C models can be divided in the following categories:

  • MP-C models without “-M” in the product name:

    MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A

  • MP-C models with “-M” in the product name:

    MP-C-24A-M and MP-C-36A-M

Déclaration

CONTROLLER DAMAGE

Follow the installation orientation restrictions that apply to the specific MP-C controller model.

Failure to follow these instructions can result in equipment damage.

MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the MP-C controller models MP-C-15A, MP-C-18A, MP-C-18B, MP-C-24A, and MP-C-36A can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

Installing the MP-C rotated 180 degrees from the horizontal position with device label text up and down (“e” in the figure), face down from a ceiling (“d” in the figure), or face up on a horizontal surface (“f” in the figure) is not supported.

 
action_zoom_plus_stroke Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated in normal conditions, 0 to 50 °C (32 to 122 °F)
Figure : Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated in normal conditions, 0 to 50 °C (32 to 122 °F)

When the MP-C is used for rooftop applications, -40 to +60 °C (-40 to +140 °F), the device should be installed horizontally, with the device label text in the upright position reading left to right. See “a” in the following figure. Any other installation orientation (“b”, “c”, “d”, “e”, and “f” in the figure) may exceed the controller's thermal specifications, which can damage the controller.

 
action_zoom_plus_stroke Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated at -40 to +60 °C (-40 to +140 °F)
Figure : Installation orientation restrictions for the MP-C models MP-C-15A, -18A (example), -18B, -24A, and -36A operated at -40 to +60 °C (-40 to +140 °F)
MP-C-24A-M and MP-C-36A-M

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the MP-C controller models MP-C-24A-M and MP-C-36A-M can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

  • Face down from a ceiling. See “d” in the following figure.

  • Up and down, which means that the device is rotated 180 degrees from the horizontal position and with the device label text up and down. See “e” in the following figure.

  • Face up on a horizontal surface. See “f” in the following figure.

 
action_zoom_plus_stroke Installation orientations for the MP-C models MP-C-24A-M and MP-C-36A-M (example) operated in normal conditions, 0 to 50 °C (32 to 122 °F)
Figure : Installation orientations for the MP-C models MP-C-24A-M and MP-C-36A-M (example) operated in normal conditions, 0 to 50 °C (32 to 122 °F)

Installation on a DIN rail

A DIN rail is a common and convenient technique for installing the MP-C along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the MP-C rail and adjacent rails or other devices.

The MP-C is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke Example of an MP-C controller installed on a horizontal DIN rail
Figure : Example of an MP-C controller installed on a horizontal DIN rail
DIN rail end clip

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

Déclaration

EQUIPMENT DAMAGE

Use an end clip (part number SXWDINEND10001) when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
Figure : End clip for DIN 35 fixed across the DIN rail

Installation in a cabinet

All MP-C controller models are recommended to be installed in a cabinet, unless local regulations allow an exception.

Déclaration

The device should be installed within an enclosure such as a control cabinet for isolation to exposed live parts.

The MP-C controller can be installed in a standard DIN enclosure/cabinet.

 
action_zoom_plus_stroke MP-C controllers installed on horizontal DIN rails in a cabinet
Figure : MP-C controllers installed on horizontal DIN rails in a cabinet

When installing MP-C controllers in a cabinet, it is recommended to provide ample space between the DIN rails and controllers for sufficient ventilation.

Screw terminals

Most of the MP-C controller models have removable screw terminal blocks for the power input and onboard I/O. The screw terminal blocks are easy to install and remove from the device. You can replace the controller in seconds because no terminal wiring is affected. The terminal blocks are installed on the device at delivery. Spare terminal blocks can be ordered separately using the part number SXWMPCCON10001.

For high-power relay outputs, a two-position fixed terminal block is used. The high-power relay output is only available on the MP-C-15A and MP-C-18A models. Pour plus d'informations, voir MP-C Onboard I/O .

The MP-C controller models with “-M” in the product name, MP-C-24A-M and MP-C-36A-M, have fixed screw terminals for the power input and onboard I/O and a removable screw terminal block for connection to the BACnet MS/TP (RS-485) network.

MP-C Display

All MP-C controller models, except MP-C-24A-M and MP-C-36A-M, can be equipped with MP-C Display (part number SXWMPCDSP10001), which is an add-on module that enables manual override control of analog and digital outputs. The module consists of an LCD display and keys. The module is designed for permanent installation.

Déclaration

CONTROLLER DEVICE DAMAGE

Do not try to remove the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

Do not try to remove the MP-C Display module as it may damage the enclosure and the module. Once installed, the MP-C Display module cannot be removed.

 
action_zoom_plus_stroke MP-C Display installed on MP-C
Figure : MP-C Display installed on MP-C

Afficher plus
action_close

The IP-IO module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

A DIN rail is a common and convenient technique for installing the IP-IO module along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the IP-IO module rail and adjacent rails or other panel-mounted devices.

The IP-IO module is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke IP-IO module installed on a horizontal DIN rail
Figure : IP-IO module installed on a horizontal DIN rail

The restrictions on installing the device in other orientations differ depending on the operating conditions.

Déclaration

CONTROLLER DEVICE DAMAGE

Follow the installation orientation restrictions that apply to the specific BACnet/IP device.

Failure to follow these instructions can result in equipment damage.

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the IP-IO module can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

Installing the IP-IO module rotated 180 degrees from the horizontal position with device label text up and down (“e” in the figure), face down from a ceiling (“d” in the figure), or face up on a horizontal surface (“f” in the figure) is not supported.

 
action_zoom_plus_stroke Installation orientation restrictions for the IP-IO module operated in normal conditions, 0 to 50 °C (32 to 122 °F)
Figure : Installation orientation restrictions for the IP-IO module operated in normal conditions, 0 to 50 °C (32 to 122 °F)

When the IP-IO module is used for rooftop applications, -40 to +60 °C (-40 to +140 °F), the device should be installed horizontally, with the device label text in the upright position reading left to right. See “a” in the following figure. Any other installation orientation (“b”, “c”, “d”, “e”, and “f” in the figure) may exceed the IP-IO module's thermal specifications, which can damage the module.

 
action_zoom_plus_stroke  Installation orientation restrictions for the IP-IO module operated at -40 to +60 °C (-40 to +140 °F)
Figure : Installation orientation restrictions for the IP-IO module operated at -40 to +60 °C (-40 to +140 °F)

All IP-IO module models are recommended to be installed in a cabinet, unless local regulations allow an exception.

Déclaration

The device should be installed within an enclosure such as a control cabinet for isolation to exposed live parts.

The IP-IO module can be installed in a standard DIN enclosure/cabinet.

 
action_zoom_plus_stroke IP-IO modules installed on horizontal DIN rails in a cabinet
Figure : IP-IO modules installed on horizontal DIN rails in a cabinet

When installing IP-IO modules in a cabinet, it is recommended to provide ample space between the DIN rails and modules for sufficient ventilation.

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

Déclaration

EQUIPMENT DAMAGE

Use an end clip (part number SXWDINEND10001) when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
Figure : End clip for DIN 35 fixed across the DIN rail

The IP-IO module is delivered with terminal blocks installed on the device.

The terminal blocks are removable. You can replace an IP-IO module in seconds because no terminal wiring is affected. The only exception is the high power relay output on the IP-IO-UIO5DOFA4 model, which uses a two-position fixed terminal block due to current requirements.

All IP-IO module models can be equipped with MP-C Display (part number SXWMPCDSP10001), which is an add-on module that enables manual override control of analog and digital outputs. The module consists of an LCD display and keys. The module is designed for permanent installation.

Déclaration

CONTROLLER DEVICE DAMAGE

Do not try to remove the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

Do not try to remove the MP-C Display module as it may damage the enclosure and the module. Once installed, the MP-C Display module cannot be removed.

 
action_zoom_plus_stroke MP-C Display installed on an IP-IO module
Figure : MP-C Display installed on an IP-IO module

Déclaration

EQUIPMENT DAMAGE

Take proper precautions before handling the display module to prevent damage from electrostatic discharge.

Failure to follow these instructions can result in equipment damage.

Déclaration

EQUIPMENT DAMAGE

Disconnect power to the MP-C or IP-IO module before installing the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

Déclaration

CONTROLLER DEVICE DAMAGE

Do not try to remove the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

Déclaration

MP-C controller models with “-M” in the product name do not support the override display unit (MP-C Display).

To install MP-C Display
  1. Disconnect power to the MP-C or IP-IO module.

  2. Locate the blank face plate on the MP-C or IP-IO module.

     
    action_zoom_plus_stroke
  3. Push and hold the two tabs on the blank face plate.

     
    action_zoom_plus_stroke
  4. Remove the blank face plate by pulling it straight out.

     
    action_zoom_plus_stroke
  5. Install the MP-C Display module in place of the blank face plate.

     
    action_zoom_plus_stroke
  • MP-C Device Installation
  • Installing MP-C on a DIN Rail
  • Installing MP-C on a Flat Surface
  • IP-IO Module Device Installation
  • Installing an IP-IO Module on a DIN Rail
  • Installing an IP-IO Module on a Flat Surface