How to

How to


Products: MP-V
Functionalities: Hardware
Product version: 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024, 7.0
5/18/2018

Installing an AM-135 Shaft Adapter on a 9.5 mm (0.375 inch) Diameter Damper Shaft

You install an AM-135 shaft adapter on a 9.5 mm (0.375 inch) diameter damper shaft to be able the use the MP-V for a damper with that shaft diameter.

Show More
action_close

The MP-V incorporates an integral actuator and the device is designed for over-the-shaft damper installation.

 
action_zoom_plus_stroke MP-V installed over the damper shaft
Figure: MP-V installed over the damper shaft

The MP-V can be used with dampers that are opened in clockwise (CW) position as well as dampers opened in counter-clockwise (CCW) position. You use WorkStation or the Commission mobile application to configure the MP-V actuator direction of rotation accordingly.

 
action_zoom_plus_stroke MP-V components
Figure: MP-V components

The MP-V is typically installed with the air flow sensor barbed fittings pointing down (orientation B in the figure below). The MP-V can also be installed with the barbed fittings pointing left (A), right (C), or up (D).

 
action_zoom_plus_stroke Supported installation orientations
Figure: Supported installation orientations

With a downward extension, the available area around the damper shaft must measure:

  • 160 mm (6 inches) down from the lower edge of the shaft,

  • 120 mm (4.5 inches) to the right,

  • 45 mm (1.75 inches) to the left, and

  • 45 mm (1.75 inches) above the shaft.

Ensure that the location allows enough clearance for servicing.

The MP-V actuator is designed to be installed over a 12.7 mm (0.5 inch) diameter round damper shaft with a minimum of 54 mm (2.125 inches) exposed damper shaft length.

When the damper shaft diameter is less than 12.7 mm (0.5 inch), an adapter is required. An adapter with part number AM-135 can be ordered from Schneider Electric to enable installation on a 9.5 mm (0.375 inches) diameter damper shaft.

 
action_zoom_plus_stroke AM-135 damper shaft adapter
Figure: AM-135 damper shaft adapter
Important:

The cutout section of the shaft adapter must be positioned such that the damper shaft mounting screws are tightened against the damper shaft and not the adapter cylinder.

When the exposed damper shaft length is less than 54 mm (2.125 inches) but greater than 22.2 mm (0.875 inch), you move the damper shaft mounting screws from the actuator collar to the alternative screw holes on the MP-V actuator.

 
action_zoom_plus_stroke Alternative position of the mounting screws for shorter damper shaft lengths
Figure: Alternative position of the mounting screws for shorter damper shaft lengths

The MP-V also has two mounting brackets, which allow you to choose the mounting bracket that best accomodates the available access space in the VAV mounting area. You position the anti-rotation clip in the desired mounting bracket.

 
action_zoom_plus_stroke Two mounting brackets
Figure: Two mounting brackets

The MP-V onboard air flow sensor is connected to an air velocity probe in the VAV box using two tubes. A dip in the tubing helps prevent moisture from entering the MP-V and damaging the air flow sensor. The dip should extend below the elevation of the barbed fittings. This applies to all MP-V orientations.

 
action_zoom_plus_stroke Tubing dip
Figure: Tubing dip
Notice

AIR FLOW SENSOR DAMAGE

  • Do not expose the VAV controller's air flow sensor inputs to moisture during installation or operation.

  • Create a tubing dip that extends below the elevation of the barbed fittings to help prevent moisture from entering the VAV controller. This applies to all controller orientations.

Failure to follow these instructions can result in equipment damage.

When operating in an unusually dusty environment, it is recommended to connect an in-line air filter (Schneider Electric part number 01-2100-272 or equivalent filter) on the high side pressure tube from the VAV box. The filter should be positioned close to the VAV box. The low flow of the sensor helps prevent most of the dust migration. The filter adds protection to help prevent dust from entering the velocity measurement tube in a dusty environment.

Note:

The recommendation to connect an air filter applies to MP-V hardware versions that have an air flow sensor of flow-through type. For more information, see Differences Between MP-V Hardware Versions .

 
action_zoom_plus_stroke Air filter
Figure: Air filter

The MP-V is delivered with terminal blocks installed on the device. Spare terminal blocks can be ordered separately using the part number SXWMPVCON10001.

The terminal blocks are removable. You can quickly and easily replace an MP-V because no terminal wiring is affected.

When the MP-V is powered up for the first time, the MP-V software automatically performs an actuator travel and damper position calibration. The calibration operation drives the damper actuator in the close direction and registers the position when the actuator encounters the stop. The software then drives the actuator in the open direction and registers the position when the stop is encountered. The software uses that information to scale the 0 to 100% span. Mechanical obstructions hindering the damper actuator rotation during the calibration process can adversely affect the calibration results and thus the VAV damper operation. In that case, after removing the mechanical obstruction, you can manually run a recalibration. For more information, see Configuring a Damper Command .

Important:

Initial calibration of actuator travel and damper position is performed automatically when the MP-V is powered up for the first time. If you subsequently press the manual override button, you must recalibrate the MP-V manually. For more information, see Configuring a Damper Command .

Notice

VAV DAMPER NOT PROPERLY CONTROLLED

  • Ensure that the VAV controller is properly installed and secured prior to application of the 24 VAC power.

  • Ensure that the VAV controller damper actuator can rotate freely between the fully open and fully closed positions.

Failure to follow these instructions can result in the VAV damper not being properly controlled by the VAV controller.

To install an AM-135 shaft adapter on a 9.5 mm (0.375 inch) diameter damper shaft
  • Slide the AM-135 shaft adapter onto the 9.5 mm (0.375 inch) diameter damper shaft with the cutout section pointing away from the VAV box.

    Important:

    When using the alternative positions for shorter damper shaft lengths, slide the AM-135 shaft adapter onto the damper shaft with the cutout section facing the VAV box.

     
    action_zoom_plus_stroke

You can now install MP-V.

Important:

When using an AM-135 shaft adapter, position the cutout section of the adapter cylinder to match the damper shaft mounting screw positions, before you tighten the screws against the damper shaft through the cutout section. Do not tighten the screws against the adapter cylinder.

 
action_zoom_plus_stroke

  • MP-V Device Installation
  • Installing MP-V on a Damper that Rotates Counter-Clockwise (CCW) to Open
  • Installing MP-V on a Damper that Rotates Clockwise (CW) to Open
  • Moving the Damper Shaft Mounting Screws to the Alternative Positions for Short Shafts Only on MP-V