earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos MP-C
Funcionalidades: Hardware
Versión del producto: 2023, 2024, 7.0
20/06/2023

MP-C-24A Screw Terminals

MP-C-24A has 24 I/O points and the controller is equipped with seven pluggable terminal blocks.

Peligro Peligro

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, MP-C-24A
Figura: Screw terminals and other connectors, MP-C-24A

The terminal blocks are used as follows:

  • One 3-position pluggable terminal block for the power input

  • One 6-position pluggable terminal block for the four universal inputs/outputs of type Uc

  • One 8-position pluggable terminal block for the four relay outputs

  • Four 6-position pluggable terminal blocks for the 16 universal inputs/outputs of type Ub

Tabla: Screw Terminals, MP-C-24A

Terminal number

Designation

Usage

Power input

1

24 VAC/DC

24 VAC, 50/60 Hz, 28 VA

Positive lead (+) when operating the device from 24-30 VDC, 15 W

2

 
action_zoom_plus_stroke
/ –

Earth ground lead of 24 VAC transformer connects to terminals 2 or 3.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 15 W

3

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Universal inputs/outputs

4

Uc1

Universal input/output, type Uc

5

RET

Internally connected to all earth ground and RET terminals

6

Uc2

Universal input/output, type Uc

7

Uc3

Universal input/output, type Uc

8

RET

Internally connected to all earth ground and RET terminals

9

Uc4

Universal input/output, type Uc

Relay outputs

16

DO1

Relay output, type Form A

17

DO1

Relay output, type Form A

18

DO2

Relay output, type Form A

19

DO2

Relay output, type Form A

20

DO3

Relay output, type Form A

21

DO3

Relay output, type Form A

22

DO4

Relay output, type Form A

23

DO4

Relay output, type Form A

Universal inputs/outputs

32

Ub1

Universal input/output, type Ub

33

RET

Internally connected to all earth ground and RET terminals

34

Ub2

Universal input/output, type Ub

35

Ub3

Universal input/output, type Ub

36

RET

Internally connected to all earth ground and RET terminals

37

Ub4

Universal input/output, type Ub

38

Ub5

Universal input/output, type Ub

39

RET

Internally connected to all earth ground and RET terminals

40

Ub6

Universal input/output, type Ub

41

Ub7

Universal input/output, type Ub

42

RET

Internally connected to all earth ground and RET terminals

43

Ub8

Universal input/output, type Ub

44

Ub9

Universal input/output, type Ub

45

RET

Internally connected to all earth ground and RET terminals

46

Ub10

Universal input/output, type Ub

47

Ub11

Universal input/output, type Ub

48

RET

Internally connected to all earth ground and RET terminals

49

Ub12

Universal input/output, type Ub

50

Ub13

Universal input/output, type Ub

51

RET

Internally connected to all earth ground and RET terminals

52

Ub14

Universal input/output, type Ub

53

Ub15

Universal input/output, type Ub

54

RET

Internally connected to all earth ground and RET terminals

55

Ub16

Universal input/output, type Ub

  • MP-C Controllers
  • MP-C Screw Terminals
  • Wiring