Produits : MP-C
Fonctionnalités : Matériel
Version produit : 2.0, 2.1, 3.0, 3.1, 3.2
18/03/2021

MP-C-24A Screw Terminals

MP-C-24A has 24 I/O points and the controller is equipped with seven pluggable terminal blocks.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, MP-C-24A
Figure : Screw terminals and other connectors, MP-C-24A

The terminal blocks are used as follows:

  • One 3-position pluggable terminal block for the power input

  • One 6-position pluggable terminal block for the four universal inputs/outputs of type Uc

  • One 8-position pluggable terminal block for the four relay outputs

  • Four 6-position pluggable terminal blocks for the 16 universal inputs/outputs of type Ub

Table : Screw Terminals, MP-C-24A

Terminal number

Designation

Usage

Power input

1

24 VAC/DC

24 VAC, 50/60 Hz, 28 VA

Positive lead (+) when operating the device from 24-30 VDC, 15 W

2

 
action_zoom_plus_stroke
/ –

Earth ground lead of 24 VAC transformer connects to terminals 2 or 3.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 15 W

3

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Universal inputs/outputs

4

Uc1

Universal input/output, type Uc

5

RET

Internally connected to all earth ground and RET terminals

6

Uc2

Universal input/output, type Uc

7

Uc3

Universal input/output, type Uc

8

RET

Internally connected to all earth ground and RET terminals

9

Uc4

Universal input/output, type Uc

Relay outputs

16

DO1

Relay output, type Form A

17

DO1

Relay output, type Form A

18

DO2

Relay output, type Form A

19

DO2

Relay output, type Form A

20

DO3

Relay output, type Form A

21

DO3

Relay output, type Form A

22

DO4

Relay output, type Form A

23

DO4

Relay output, type Form A

Universal inputs/outputs

32

Ub1

Universal input/output, type Ub

33

RET

Internally connected to all earth ground and RET terminals

34

Ub2

Universal input/output, type Ub

35

Ub3

Universal input/output, type Ub

36

RET

Internally connected to all earth ground and RET terminals

37

Ub4

Universal input/output, type Ub

38

Ub5

Universal input/output, type Ub

39

RET

Internally connected to all earth ground and RET terminals

40

Ub6

Universal input/output, type Ub

41

Ub7

Universal input/output, type Ub

42

RET

Internally connected to all earth ground and RET terminals

43

Ub8

Universal input/output, type Ub

44

Ub9

Universal input/output, type Ub

45

RET

Internally connected to all earth ground and RET terminals

46

Ub10

Universal input/output, type Ub

47

Ub11

Universal input/output, type Ub

48

RET

Internally connected to all earth ground and RET terminals

49

Ub12

Universal input/output, type Ub

50

Ub13

Universal input/output, type Ub

51

RET

Internally connected to all earth ground and RET terminals

52

Ub14

Universal input/output, type Ub

53

Ub15

Universal input/output, type Ub

54

RET

Internally connected to all earth ground and RET terminals

55

Ub16

Universal input/output, type Ub

  • MP-Cs