SmartX AS-B servers with 24 I/O points use nine pluggable terminal blocks and one fixed terminal block.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
The terminal blocks are used as follows:
One 3-position pluggable terminal block for the power input
One 2-position fixed terminal block for the two return (RET) terminals 4 and 5
One 4-position pluggable terminal block for RS-485 communication
One 6-position pluggable terminal block for the four universal inputs/outputs of type Ub
One 6-position pluggable terminal block for the four digital inputs
One 8-position pluggable terminal block for the four relay outputs
Four 6-position pluggable terminal blocks for the 12 universal inputs/outputs of type Ua
Terminal number |
Designation |
Usage |
Power input |
|
|
1 |
L/+ |
Line (L) lead when operating the device from 24 VAC, 50/60 Hz, 15 VA Positive (+) lead when operating the device from 24-30 VDC, 10 W |
2 |
N/– |
Neutral (N) lead when operating the device from 24 VAC, 50/60 Hz, 15 VA Negative (–) lead when operating the device from 24-30 VDC, 10 W |
3 |
|
Earth ground |
Return terminals |
|
|
4 |
RET |
Internally connected to terminal 3 (earth ground) |
5 |
RET |
Internally connected to terminal 3 (earth ground) |
RS-485 |
|
|
6 |
Bias + |
5.0 VDC, RS-485 bias supply, current limited 40 mA |
7 |
TX/RX + |
RS-485 communication |
8 |
TX/RX – |
RS-485 communication |
9 |
RET |
Internally connected to terminal 3 (earth ground) |
Universal inputs/outputs |
|
|
10 |
Ub1 |
Universal input/output, type Ub |
11 |
RET |
Internally connected to terminal 3 (earth ground) |
12 |
Ub2 |
Universal input/output, type Ub |
13 |
Ub3 |
Universal input/output, type Ub |
14 |
RET |
Internally connected to terminal 3 (earth ground) |
15 |
Ub4 |
Universal input/output, type Ub |
Digital inputs |
|
|
16 |
DI1 |
Digital input |
17 |
RET |
Internally connected to terminal 3 (earth ground) |
18 |
DI2 |
Digital input |
19 |
DI3 |
Digital input |
20 |
RET |
Internally connected to terminal 3 (earth ground) |
21 |
DI4 |
Digital input |
Relay outputs |
|
|
22 |
DO1 |
Relay output, type Form A |
23 |
DO1 |
Relay output, type Form A |
24 |
DO2 |
Relay output, type Form A |
25 |
DO2 |
Relay output, type Form A |
26 |
DO3 |
Relay output, type Form A |
27 |
DO3 |
Relay output, type Form A |
28 |
DO4 |
Relay output, type Form A |
29 |
DO4 |
Relay output, type Form A |
Universal inputs/outputs, type Ua |
|
|
30 |
RET |
Internally connected to terminal 3 (earth ground) |
31 |
Ua1 |
Universal input/output, type Ua |
32 |
RET |
Internally connected to terminal 3 (earth ground) |
33 |
Ua2 |
Universal input/output, type Ua |
34 |
RET |
Internally connected to terminal 3 (earth ground) |
35 |
Ua3 |
Universal input/output, type Ua |
36 |
RET |
Internally connected to terminal 3 (earth ground) |
37 |
Ua4 |
Universal input/output, type Ua |
38 |
RET |
Internally connected to terminal 3 (earth ground) |
39 |
Ua5 |
Universal input/output, type Ua |
40 |
RET |
Internally connected to terminal 3 (earth ground) |
41 |
Ua6 |
Universal input/output, type Ua |
42 |
RET |
Internally connected to terminal 3 (earth ground) |
43 |
Ua7 |
Universal input/output, type Ua |
44 |
RET |
Internally connected to terminal 3 (earth ground) |
45 |
Ua8 |
Universal input/output, type Ua |
46 |
RET |
Internally connected to terminal 3 (earth ground) |
47 |
Ua9 |
Universal input/output, type Ua |
48 |
RET |
Internally connected to terminal 3 (earth ground) |
49 |
Ua10 |
Universal input/output, type Ua |
50 |
RET |
Internally connected to terminal 3 (earth ground) |
51 |
Ua11 |
Universal input/output, type Ua |
52 |
RET |
Internally connected to terminal 3 (earth ground) |
53 |
Ua12 |
Universal input/output, type Ua |
The screw terminals 6 to 9, intended for RS-485 communication, act as connectors to the SmartX AS-B server and are easily inserted/removed without disrupting the network. Doing so may help in isolating possible RS-485 communication problems.