Use this workflow to perform flow balance on a single MP-V controller, using the eCommission SmartX Controllers mobile application. Related information can be found in the section after the flowchart.
Mer information finns i Flow Balancing .
Start the eCommission application and log in as either a Technician or Flow Balancer.
Mer information finns i Downloading and Starting the eCommission SmartX Controllers Mobile Application .
Discover controllers on the site, and connect to a single MP-V.
Mer information finns i Device Connection .
You configure the MP-V controller setpoints to set up the parameters by which the controller is flow balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional.
Mer information finns i Configuring MP-V Controller Setpoints .
Using the eCommission application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.
Mer information finns i Flow Balancing at Minimum, Intermediate, or Maximum Flow Setpoint .
After flow balancing the MP-V controller, you can perform manual checkout on two components of the MP-V:
Verify direction of rotation to open
You can manually verify the direction of damper rotation to determine whether the actuator rotates clockwise or counterclockwise to open.
Mer information finns i Manually Verifying the Direction of Damper Rotation .
Manual checkouts of air flow
After completing the automated flow balancing process, you can optionally verify and command the air flow values by performing manual checkout.
Mer information finns i Performing Manual Checkout of Air Flow .
After completing flow balancing, you can use the eCommission application to create, append, view, or delete flow balance reports. Mer information finns i Managing Flow Balance Reports .