earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: Commission, IP-IO , MP-C, MP-V, RP-C
Functionalities: Engineering, BACnet/IP devices
Product version: 2023, 2024
8/7/2024

I/O Checkout Overview

arrow1_rotationI/O Checkout Status arrow1_rotationI/O Checkout Report arrow1_rotationCommissioning Log

After you have wired the physical inputs and outputs of the controller, you perform I/O checkout to verify that the wiring was done correctly and that the physical inputs and outputs are working properly.

For more information, see Performing I/O Checkout .

I/O Checkout Status

The I/O checkout status of each input and output can be found in the Inputs and Outputs view. Prior to the first I/O checkout, Status is New . The checkout statuses of all the inputs and outputs in a BACnet/IP device are displayed as the Checkout status of the controller, in the Device List view.

I/O Checkout Report

When you perform I/O checkout and select Save , an I/O checkout report is generated within the BACnet/IP controller. This report is saved to the Diagnostic Files in the BACnet/IP controller and can be viewed from WorkStation once the device is hosted.

Commissioning Log

During I/O checkout, the Commission mobile application creates a commissioning log file in which the steps performed are automatically saved. This log file is created in the VAV controller and can be viewed from WorkStation.

  • Commission Mobile Application Overview
  • Performing I/O Checkout