Viewing an I/O Checkout Report

You view an I/O checkout report when checkout of all objects in the controller is complete. The report is created when you are performing I/O checkout and select the Save button. The report is saved in the BACnet/IP controller within diagnostic files.

Visa mer
action_close

After you have wired the physical inputs and outputs of the controller, you perform I/O checkout to verify that the wiring was done correctly and that the physical inputs and outputs are working properly.

Mer information finns i Performing I/O Checkout .

I/O Checkout Status

The I/O checkout status of each input and output can be found in the Inputs and Outputs view. Prior to the first I/O checkout, Status is New . The checkout statuses of all the inputs and outputs in a BACnet/IP device are displayed as the Checkout status of the controller, in the Device List view.

I/O Checkout Report

When you perform I/O checkout and click Done , an I/O checkout report is generated within the BACnet/IP controller. This report is saved to the Diagnostic Files folder in the BACnet/IP controller and can be viewed from WorkStation once the device is hosted.

Commissioning Log

During I/O checkout, the Commission mobile application creates a commissioning log file in which the steps performed are automatically saved. This log file is created in the VAV controller and can be viewed from WorkStation.

To view an I/O checkout report
  1. In the Inputs and Outputs page, click the Report icon.

  2. Use the share options available on your device to send the report to the target location of your choice. Each report is a text file which can be opened with any text editor.

  3. Close the Share dialog to view the contents of the report.

    Obs!

    To clear the I/O checkout report, click the Clear Report icon (top).

  • I/O Checkout Overview