earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-C
Funcionalidades: Hardware
Versión del producto: 2023, 2024, 7.0
30/03/2023

RP-C Built-in Power Supply

The RP-C 24 V controller models have a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power. The RP-C 230 V controller models' power supply is designed for a nominal operating voltage of 230 VAC at 50/60 Hz.

Para obtener más información, consulte RP-C Models .

RP-C 24 V Controller Models

The design of the built-in power supply differs between the RP-C 24 V controller models, which in that respect can be divided into the following two categories:

  • Models with an “-F” in the product name:

    RP-C-12A-F-24V, RP-C-12B-F-24V, RP-C-12C-F-24V, and RP-C-16B-F-24V

  • Models with an “-M” in the product name:

    RP-C-12A-M-24V, RP-C-12B-M-24V, and RP-C-16A-M-24V

RP-C-12A-F-24V, RP-C-12B-F-24V, RP-C-12C-F-24V, and RP-C-16B-F-24V

The built-in power supply is based on a half-wave rectified, non-isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

To power the controller, you can use a transformer or a DC power supply:

  • Class 2 (EN 60742) transformer supplying a nominal 24 VAC at 50/60 Hz

  • DC power supply supplying a nominal 24 to 30 VDC with the required output power

Para obtener más información, consulte RP-C Controllers .

Aviso

CONTROLLER DEVICE DAMAGE

Do not power the SpaceLogic device with a 24 VAC transformer that is used to power devices that contain non-isolated full-wave rectifier power supplies.

Failure to follow these instructions can result in equipment damage.

RP-C-12A-M-24V, RP-C-12B-M-24V, and RP-C-16A-M-24V

The built-in power supply is based on a full-wave rectified, isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

To power the controller, you can use a transformer or a DC power supply:

  • Class 2 (EN 60742) transformer supplying a nominal 24 VAC at 50/60 Hz

  • DC power supply supplying a nominal 24 to 30 VDC with the required output power

The 24 VAC/VDC power input is galvanically isolated from the electronics. This minimizes the risk of damage due to earth currents and permits the input power to be wired without concern for polarity matching.

RP-C 230 V Controller Models

RP-C-16A-F-230V, RP-C-16B-F-230V, and RP-C-16C-F-230V

The built-in power supply is based on a full-wave rectified, isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

With the 230 VAC input (L and N) electronically isolated from the electronics, the risk of damage due to earth ground currents is reduced and allows the input power to be wired without concern for polarity matching.

  • Hardware Overview
  • RP-C Controllers
  • RP-C Models