The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.
The RP-C-16C-F-230V model has SSR outputs that differs from other RP-C models. Более подробную информацию см. Solid-state Relay (SSR) Outputs with Power Distribution on RP-C-16C-F-230V .
The outputs can be configured as one of the following types:
Digital output
Digital pulsed output
Pulse width modulated output
Tristate output
Tristate pulsed output
The DO SSR outputs are Form A digital outputs, which means the outputs are normally open contacts with one common terminal and one normally open terminal. Each pair of SSR outputs share a common terminal but the outputs can be controlled independently.
Channels, RP-C-12A-F-24V
|
4, DO1 to DO4
|
Channels, RP-C-12B-F-24V
|
0
|
Channels, RP-C-12C-F-24V
|
4, DO1 to DO4
|
Channels, RP-C-16B-F-24V
|
4, DO1 to DO4
|
Channels, RP-C-16A-F-230V
|
4, DO1 to DO4
|
Channels, RP-C-16B-F-230V
|
4, DO1 to DO4
|
Channels, RP-C-16C-F-230V
|
0
|
Channels, RP-C-12A-M-24V
|
4, DO1 to DO4
|
Channels, RP-C-12B-M-24V
|
0
|
Channels, RP-C-16A-M-24V
|
4, DO1 to DO4
|
Output rating
|
Maximum 2 A load per output
|
Maximum 4 A total load for the 4 outputs
|
|
AC voltage range
|
Maximum 30 VAC
|
DC voltage range
|
Maximum 30 VDC
|
Commons
|
COM1 for DO1 and DO2
|
COM2 for DO3 and DO4
|
|
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC. | |
Common voltage range (AC)
|
0 to 30 VAC
|
Common voltage range (DC)
|
-30 to +30 VDC
|
Minimum pulse width
|
100 ms
|
Solid-state relay output protection
|
Transient voltage suppressor across each solid-state relay (SSR) output
|