The RP-C-12A-F-24V model has 12 I/O points and the controller is equipped with 23 fixed screw terminals.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
The 23 screw terminals are used as follows:
Two screw terminals for the power input
One screw terminal for ground input
Two screw terminals for the return (RET) terminals 4 and 5
Six screw terminals for the four solid-state relay (SSR) outputs
12 screw terminals for the eight universal inputs/outputs of type Ub
Terminal number |
Designation |
Usage |
Power input |
|
|
1 |
![]() |
G – 24 VAC, 50/60 Hz, 23 VA Positive lead (+) when operating the device from 24-30 VDC, 14 W |
2 |
![]() |
G0 – The other output from the 24 VAC transformer connects to terminal 2. Terminals 2 and 3 are internally connected. Negative (–) lead when operating the device from 24-30 VDC, 14 W |
3 |
RET ![]() |
Terminal 3 is provided for convenience to connect to protective earth ground (optional). Terminals 2 and 3 are internally connected. |
Return terminals |
|
|
4 |
RET |
Internally connected to all earth ground and RET terminals |
5 |
RET |
Internally connected to all earth ground and RET terminals |
Solid-state relay (SSR) outputs |
|
|
6 |
DO1 |
SSR output |
7 |
COM1 |
Common connection for DO1 and DO2 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
8 |
DO2 |
SSR output |
9 |
DO3 |
SSR output |
10 |
COM2 |
Common connection for DO3 and DO4 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
11 |
DO4 |
SSR output |
Universal inputs/outputs |
|
|
19 |
Ub1 |
Universal input/output, type Ub |
20 |
RET |
Internally connected to all earth ground and RET terminals |
21 |
Ub2 |
Universal input/output, type Ub |
22 |
Ub3 |
Universal input/output, type Ub |
23 |
RET |
Internally connected to all earth ground and RET terminals |
24 |
Ub4 |
Universal input/output, type Ub |
25 |
Ub5 |
Universal input/output, type Ub |
26 |
RET |
Internally connected to all earth ground and RET terminals |
27 |
Ub6 |
Universal input/output, type Ub |
28 |
Ub7 |
Universal input/output, type Ub |
29 |
RET |
Internally connected to all earth ground and RET terminals |
30 |
Ub8 |
Universal input/output, type Ub |