earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-C
Funcionalidades: Hardware
Versión del producto: 2022, 2023, 2024, 7.0
25/05/2023

RP-C-16A-F-230V Screw Terminals

The RP-C-16A-F-230V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals.

Peligro Peligro

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Peligro Peligro

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Never connect the 24 VAC supply output terminals 4 and 5 to any other power supply output, regardless of polarity.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, RP-C-16A-F-230V (hardware version 10 and later)
Figura: Screw terminals and other connectors, RP-C-16A-F-230V (hardware version 10 and later)

The 30 screw terminals are used as follows:

  • Two screw terminals for the power input

  • One screw terminal for protective earth ground

  • Two screw terminals for the 24 VAC output terminals 4 and 5

  • Six screw terminals for the four solid-state relay (SSR) outputs

  • Four screw terminals for the three relay outputs

  • Three screw terminals for the high power relay output

  • 12 screw terminals for the eight universal inputs/outputs of type Ub

Tabla: Screw Terminals, RP-C-16A-F-230V

Terminal number

Designation

Usage

Power input

1

L

Line (L) lead, 230 VAC, 50/60 Hz, 65 VA

2

N

Neutral (N) lead, 230 VAC, 50/60 Hz, 65 VA

3

 
action_zoom_plus_stroke

Protective earth ground

This applies to hardware version a 10 and later. Para obtener más información, consulte Differences Between RP-C Hardware Versions .

24 VAC output

4

24 VAC Out

24 VAC, 19 VA, isolated output

Para obtener más información, consulte 24 VAC Output on RP-C 230 V Controller Models .

5

24 VAC Out

24 VAC, 19 VA, isolated output

Para obtener más información, consulte 24 VAC Output on RP-C 230 V Controller Models .

Solid-state relay (SSR) outputs

6

DO1

SSR output

7

COM1

Common connection for DO1 and DO2

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

8

DO2

SSR output

9

DO3

SSR output

10

COM2

Common connection for DO3 and DO4

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

11

DO4

SSR output

Relay outputs

12

COM3

Common connection for DO1, DO2, and DO3

13

DO1

Relay output, type Form A

14

DO2

Relay output, type Form A

15

DO3

Relay output, type Form A

High power relay outputs

16

NC

Normally Closed terminal. High power relay output, type Form C.

17

DO4

Common terminal. High power relay output, type Form C.

18

NO

Normally Open terminal. High power relay output, type Form C.

Universal inputs/outputs

19

Ub1

Universal input/output, type Ub

20

RET

Internally connected to all RET terminals

21

Ub2

Universal input/output, type Ub

22

Ub3

Universal input/output, type Ub

23

RET

Internally connected to all RET terminals

24

Ub4

Universal input/output, type Ub

25

Ub5

Universal input/output, type Ub

26

RET

Internally connected to all RET terminals

27

Ub6

Universal input/output, type Ub

28

Ub7

Universal input/output, type Ub

29

RET

Internally connected to all RET terminals

30

Ub8

Universal input/output, type Ub

  1. The hardware version is shown on the label on the side of the device.
  • RP-C Controllers
  • RP-C Screw Terminals
  • Wiring
  • 24 VAC Output on RP-C 230 V Controller Models
  • Differences Between RP-C Hardware Versions