The RP-C-16A-F-230V model has 16 I/O points and the controller is equipped with 30 fixed screw terminals.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
The 30 screw terminals are used as follows:
Two screw terminals for the power input
One screw terminal for protective earth ground
Two screw terminals for the 24 VAC output terminals 4 and 5
Six screw terminals for the four solid-state relay (SSR) outputs
Four screw terminals for the three relay outputs
Three screw terminals for the high power relay output
12 screw terminals for the eight universal inputs/outputs of type Ub
Terminal number |
Designation |
Usage |
Power input |
|
|
1 |
L |
Line (L) lead, 230 VAC, 50/60 Hz, 65 VA |
2 |
N |
Neutral (N) lead, 230 VAC, 50/60 Hz, 65 VA |
3 |
|
Protective earth ground This applies to hardware version a 10 and later. 有关更多信息,请参阅 Differences Between RP-C Hardware Versions . |
24 VAC output |
|
|
4 |
24 VAC Out |
24 VAC, 19 VA, isolated output 有关更多信息,请参阅 24 VAC Output on RP-C 230 V Controller Models . |
5 |
24 VAC Out |
24 VAC, 19 VA, isolated output 有关更多信息,请参阅 24 VAC Output on RP-C 230 V Controller Models . |
Solid-state relay (SSR) outputs |
|
|
6 |
DO1 |
SSR output |
7 |
COM1 |
Common connection for DO1 and DO2 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
8 |
DO2 |
SSR output |
9 |
DO3 |
SSR output |
10 |
COM2 |
Common connection for DO3 and DO4 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
11 |
DO4 |
SSR output |
Relay outputs |
|
|
12 |
COM3 |
Common connection for DO1, DO2, and DO3 |
13 |
DO1 |
Relay output, type Form A |
14 |
DO2 |
Relay output, type Form A |
15 |
DO3 |
Relay output, type Form A |
High power relay outputs |
|
|
16 |
NC |
Normally Closed terminal. High power relay output, type Form C. |
17 |
DO4 |
Common terminal. High power relay output, type Form C. |
18 |
NO |
Normally Open terminal. High power relay output, type Form C. |
Universal inputs/outputs |
|
|
19 |
Ub1 |
Universal input/output, type Ub |
20 |
RET |
Internally connected to all RET terminals |
21 |
Ub2 |
Universal input/output, type Ub |
22 |
Ub3 |
Universal input/output, type Ub |
23 |
RET |
Internally connected to all RET terminals |
24 |
Ub4 |
Universal input/output, type Ub |
25 |
Ub5 |
Universal input/output, type Ub |
26 |
RET |
Internally connected to all RET terminals |
27 |
Ub6 |
Universal input/output, type Ub |
28 |
Ub7 |
Universal input/output, type Ub |
29 |
RET |
Internally connected to all RET terminals |
30 |
Ub8 |
Universal input/output, type Ub |