IP-IO-UIO5DOFA4 Screw Terminals

IP-IO-UIO5DOFA4 has 9 I/O points and the IP-IO module is equipped with four pluggable terminal blocks and one fixed terminal block.

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, IP-IO-UIO5DOFA4
Figure : Screw terminals and other connectors, IP-IO-UIO5DOFA4

The terminal blocks are used as follows:

  • One 3-position pluggable terminal block for the power input

  • One 6-position pluggable terminal block for the three relay outputs

  • One 2-position fixed terminal block for the high power relay output

  • One 6-position plus one 2-position pluggable terminal blocks for the five universal inputs/outputs of type Ub

Table : Screw Terminals, IP-IO-UIO5DOFA4

Terminal number

Designation

Usage

Power input

1

24 VAC/DC

24 VAC, 50/60 Hz, 17 VA

Positive lead (+) when operating the device from 24-30 VDC, 9 W

2

 
action_zoom_plus_stroke
/ –

Earth ground lead of 24 VAC transformer connects to terminals 2 or 3.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 9 W

3

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Relay outputs

10

DO1

Relay output, type Form A

11

DO1

Relay output, type Form A

12

DO2

Relay output, type Form A

13

DO2

Relay output, type Form A

14

DO3

Relay output, type Form A

15

DO3

Relay output, type Form A

High power relay outputs

16

DO4

High power relay output, type Form A

17

DO4

High power relay output, type Form A

Universal inputs/outputs

18

Ub1

Universal input/output, type Ub

19

RET

Internally connected to all earth ground and RET terminals

20

Ub2

Universal input/output, type Ub

21

Ub3

Universal input/output, type Ub

22

RET

Internally connected to all earth ground and RET terminals

23

Ub4

Universal input/output, type Ub

24

Ub5

Universal input/output, type Ub

25

RET

Internally connected to all earth ground and RET terminals

  • IP-IO Modules
  • IP-IO Module Screw Terminals
  • Wiring