earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: IP-IO
Functionalities: Hardware
Product version: 2024, 7.0
6/30/2025

IP-IO Modules

The IP-IO module provides I/O expansion to your HVAC application over BACnet/IP and can share their I/O resources across applications running in automation servers, BACnet/IP controllers, or third-party systems. The IP-IO module can be installed near facilities in the field, away from the automation server or the BACnet/IP controller.

The IP-IO module allows for flexible control options due to the dual Ethernet ports and the versatile mix of digital inputs, universal inputs/outputs, relay outputs, and high power relay outputs.

When IP-IO modules are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

The IP-IO module device can be installed on a DIN rail or other flat surface inside a cabinet.

All IP-IO models can be equipped with MP-C Display, which is an optional add-on module for output override. The MP-C Display can also be used to view and locally configure inputs and outputs.

 
action_zoom_plus_stroke IP-IO module
Figure: IP-IO module

IP-IO Module Models and I/O Point Types

The IP-IO module comes in three models with different I/O point count and different I/O point types.

For more information, see IP-IO Module Models and I/O Point Types .

Output Override Function (Optional)

The output override function allows you to manually override outputs. This function can be used for testing, commissioning, and maintenance of equipment.

For more information, see Output Override Function .

IP-IO Module Built-in Power Supply

The IP-IO module has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

For more information, see IP-IO Module Built-in Power Supply .

Memory in RP and MP Controllers and I/O Modules

BACnet/IP devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

For more information, see Memory in RP and MP Controllers and I/O Modules .

IP-IO Module Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the IP-IO module complies with the BACnet open standard, one of the most popular standards for buildings.

For more information, see IP-IO Module Supported Building Standards .

IP-IO Module Communication Ports

The IP-IO module contains a combination of Ethernet and USB communication ports.

For more information, see IP-IO Module Communication Ports .

IP-IO Module Screw Terminals

The IP-IO module is delivered with terminal blocks installed on the device. The IP-IO module uses pluggable terminal blocks, which are easy to install and remove from the device.

For more information, see IP-IO Module Screw Terminals .

IP-IO Module LEDs

There are three LEDs on the front panel of the IP-IO module.

For more information, see IP-IO Module LEDs .

IP-IO Module Reset Modes

You can reset and restart the IP-IO modules in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

For more information, see IP-IO and RP-IO Module Reset Modes .

IP-IO Module Device Installation

The IP-IO module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

For more information, see IP-IO Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

For more information, see Wiring .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Tip:

SpaceLogic Sensor devices are supported by the BACnet/IP controllers - MP and RP controllers.

For more information, see BACnet/IP Device Firmware Management .

Specifications

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum power consumption
17 VA
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
9 W
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation a
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only a
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5V
Ingress protection rating
IP 20
Mechanical
Dimensions
153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, IP-IO-DI10
Including terminal blocks
0.337 kg (0.742 lb)
Weight, IP-IO-UIO10
Including terminal blocks
0.336 kg (0.740 lb)
Weight, IP-IO-UIO5DOFA4
Including terminal blocks
0.357 kg (0.787 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Removable
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45), IEEE 802.3 compliant
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BTL B-ASC (BACnet Application Specific Controller) a
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
MP-C Display (Optional)
Removable
No
Display size
36 W x 17 H mm (1.4 W x 0.7 H in.)
Display resolution
128 x 64 pixels
Display type
FSTN monochrome LCD, white color transflective backlight
Power consumption
max. 0.15 W (45 mA at 3.3 V)
Ambient temperature, operating
-30 to +60 °C (-22 to +140 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Weight
0.035 kg (0.077 lb)

Internal Configuration

The IP-IO module internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke IP-IO module internal configuration
Figure: IP-IO module internal configuration
  • Hardware Overview
  • IP-IO Module Models and I/O Point Types
  • Output Override Function
  • IP-IO Module Built-in Power Supply
  • Memory in RP and MP Controllers and I/O Modules
  • IP-IO Module Supported Building Standards
  • IP-IO Module Communication Ports
  • IP-IO Module Screw Terminals
  • IP-IO Module LEDs
  • IP-IO and RP-IO Module Reset Modes
  • IP-IO Module Device Installation
  • Wiring
  • BACnet/IP Device Firmware Management