The RP-C sensor bus allows SpaceLogic Sensor devices to be connected to the controller.
Obs!
|
LOSS OF COMMUNICATION
Ensure that the total length of the sensor bus does not exceed 61 m (200 ft).
Use a Cat 5 or higher unshielded twisted pair cable with eight conductors (four twisted pairs), a cross-sectional area of 22 to 26 AWG (0.34 to 0.14 mm
2
), and a rating that meets the requirements of the target environment.
Failure to follow these instructions can result in loss of communication.
|
By default, the RP-C controller's Sensor Bus port (RS-485 Com A) is configured and allocated for the sensor bus.
Mer information finns i RP-C Communication Ports
.
action_zoom_plus_stroke
Figur:
Location of the Sensor Bus port (RS-485 Com A) on the RP-C controllers
Obs!
When connecting SpaceLogic Sensor devices to the sensor bus through a daisy-chain configuration, it does not matter if the incoming and outgoing cables are connected to one or the other sensor bus port on the SpaceLogic Sensor.
Description
|
Model Number
|
Power (mW)
|
Sensor base with temperature sensor
|
SXWSBTXXXSXX
|
90
|
Sensor base with temperature and humidity sensors
|
SXWSBTHXXSXX
|
90
|
Sensor base with temperature and CO
2
sensors
|
SXWSBTXCXSXX
|
490
|
Sensor base with temperature, humidity, and CO
2
sensors
|
SXWSBTHCXSXX
|
490
|
Blank cover
|
SXWSCBXSELXn
|
0
|
Blank cover with occupancy sensor
|
SXWSCBPSELXn
a
|
20
|
3-button cover (buttons for override and setpoint control)
|
SXWSC3XSELXn
a
|
190
|
3-button cover (buttons for override and setpoint control) with occupancy sensor
|
SXWSC3PSELXn
a
|
210
|
Touchscreen display cover
|
SXWSCDXSELXn
a
|
190
|
Touchscreen display cover with occupancy sensor
|
SXWSCDPSELXn
a
|
210
|
Touchscreen display cover with light control buttons
|
SXWSC2XSELXn
a
|
190
|
Touchscreen display cover with light control buttons and occupancy sensor
|
SXWSC2PSELXn
a
|
210
|
Touchscreen display cover with light and blind control buttons
|
SXWSC4XSELXn
a
|
190
|
Touchscreen display cover with light and blind control buttons and occupancy sensor
|
SXWSC4PSELXn
a
|
210
|
Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover
|
SXWSATXXXSLn
a
|
80
|
Complete non-communicating
SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover
|
SLAnXXX
SXWSATXXXRXX
|
0
|
SpaceLogic Bluetooth Adapter
|
SXWBTAECXX10001
|
300
|
To summarize the power conditions, the sensor bus supports the following key SpaceLogic Sensor combinations:
Blank covers: Up to four sensors of any combination of sensor base types
3-button and touchscreen covers:
SpaceLogic LCD temperature sensors: Up to four sensors are supported
action_zoom_plus_stroke
Figur:
Examples with one SpaceLogic Sensor and four SpaceLogic Sensor devices connected to an RP-C controller in a daisy-chain configuration
Each SpaceLogic Sensor has two 2-position DIP switches, which are used to give the sensor a unique address on the sensor bus. An incorrectly configured or improper DIP switch can cause two sensors to have the same address on the sensor bus, which means that both sensors will be offline.
Mer information finns i SpaceLogic Sensors
.
Obs!
|
LOSS OF COMMUNICATION
Ensure that the address DIP switches on the SpaceLogic Sensor are configured to give the sensor a unique address on the sensor bus.
Failure to follow these instructions can result in loss of communication.
|
Obs!
SpaceLogic Sensor devices connected to the sensor bus through a daisy-chain configuration can be assigned addresses regardless of the order in which the sensors appear in the daisy chain. For example, sensor number 1 can have the address 6, sensor number 2 can have the address 4, and so on.