SpaceLogic* RP-C-EXT-DALI light module connects to the SpaceLogic RP room controllers and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).
The DALI light module enables control of lights equipped with DALI ballasts (DALI control gear).
The DALI light module is a DALI-2 certified control device (application controller). DALI-2 compliance means benefits such as improved interoperability and easier installation and maintenance. The DALI light module can be used with DALI version-1 products because DALI-2 is designed to be backward compatible with DALI version-1.
Lighting can be controlled by the RP-C through motion detection and light intensity measurement provided by the Multi-sensor or by SpaceLogic Sensors connected to the RP-C.
The DALI light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.
* Formerly known as SmartX.
The DALI light module has the following features:
Power and communications through the room bus
DALI-2 certified control device (application controller)
Group and individual addressing of DALI devices
One DALI channel, which is split into four outputs, for DALI bus power supply and control of up to 32 lights
Up to 16 DALI groups for common control of lights
Four digital inputs for connection of light switches and window contacts. The digital inputs are SELV (Safety Extra-Low Voltage).
Suitable for mounting in ceilings
Wieland connectors for quick and easy installation
Engage mobile application for room comfort settings
Status LED for the device
Rotary switch for address configuration
The DALI-2 interface has the following features:
DALI groups can combine lights regardless of which outputs the lights belong to.
Lights that belong to the same DALI group are controlled simultaneously for switching on/off, dimming, and color temperature (tunable white) adjustment
Management of ballast and lamp alarms
Automatic addressing of lights
The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.
The RP-C room bus supports up to six connected RP controller expansion modules with the following restrictions:
Maximum of two DALI light modules
Maximum of two SMI blind modules
Maximum of four multi-sensors
Maximum total length of the room bus is 72 m (236 ft).
The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP-C controller.
The Engage mobile application is free and available for download from Google Play and Apple App Store.
For more information, see the Engage Specification Sheet.
Product |
Part number |
RP-C-EXT-DALI
|
SXWREDALI110001
|
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
|
SXWDINEND10001
|
Electrical | |||||||||||||
Nominal voltage
|
100 to 277 VAC
|
||||||||||||
Operating voltage range
|
+/-10 %
|
||||||||||||
Frequency
|
50/60 Hz
|
||||||||||||
Power consumption
|
10 VA
|
||||||||||||
Room bus power consumption
|
0.3 W (24 VDC)
|
||||||||||||
Overvoltage category
|
III
|
||||||||||||
Environment | |||||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
||||||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
||||||||||||
Humidity
|
20 to 90 % RH non-condensing
|
||||||||||||
Pollution degree
|
2
|
||||||||||||
Material | |||||||||||||
Plastic flame rating
|
UL94 V-0
|
||||||||||||
Ingress protection rating
|
IP 20
|
||||||||||||
Mechanical | |||||||||||||
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
||||||||||||
|
|||||||||||||
Weight
|
0.352 kg (0.776 lb)
|
||||||||||||
Installation
|
DIN rail or flat surface
|
||||||||||||
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
||||||||||||
Light outputs: 4 x 2-pin Wieland GST15i2 connector
|
|||||||||||||
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
|||||||||||||
Software compatibility | |||||||||||||
EcoStruxure Building Operation software
|
version 3.2 and later
|
||||||||||||
Agency compliances | |||||||||||||
Emission
|
RCM; BS/EN 61000-6-3; BS/EN 50491-5-2; FCC Part 15, Sub-part B, Class B
|
||||||||||||
Immunity
|
BS/EN 61000-6-2; BS/EN 50491-5-3
|
||||||||||||
Safety standards
|
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN 50491-3; UL 916 C-UL US Listed
|
||||||||||||
Fire performance in air-handling spaces
a
|
UL 2043
|
||||||||||||
a) The RP-C-EXT-DALI light module is approved for plenum applications. | |||||||||||||
Digital addressable lighting interface
|
IEC 62386-101; IEC 62386-103
|
||||||||||||
Communication ports | |||||||||||||
Room bus
|
RS-485
|
||||||||||||
Dual RJ45 ports for daisy-chain configurations
|
|||||||||||||
Use a Cat 5 (or higher) cable
|
|||||||||||||
Maximum total length of the room bus: 72 m (236 ft)
|
|||||||||||||
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
||||||||||||
Hardware | |||||||||||||
Main microcontroller | |||||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||||||||
Frequency
|
80 MHz
|
||||||||||||
SRAM (embedded)
|
320 KB
|
||||||||||||
Flash memory (embedded)
|
1024 KB
|
||||||||||||
Memory | |||||||||||||
NOR flash memory
|
16 MB
|
||||||||||||
DALI microcontroller | |||||||||||||
CPU type
|
ARM Cortex-M0 single-core
|
||||||||||||
Frequency
|
32 MHz
|
||||||||||||
SRAM (embedded)
|
8 KB
|
||||||||||||
Flash memory (embedded)
|
64 KB
|
||||||||||||
Additional hardware | |||||||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
||||||||||||
Address switch
|
Rotary switch 0 to 9
|
||||||||||||
Set button
|
Push-button switch
|
||||||||||||
DALI light outputs | |||||||||||||
Outputs
|
4, Light 1 to Light 4
|
||||||||||||
The four outputs share one DALI channel. | |||||||||||||
Output terminals
|
DA+ and DA-
|
||||||||||||
DALI bus voltage
|
18 VDC
|
||||||||||||
Maximum supply current
|
250 mA
|
||||||||||||
Guaranteed supply current
|
64 mA
|
||||||||||||
Maximum cable length
|
See the SpaceLogic Hardware Reference Guide
|
||||||||||||
DALI devices | |||||||||||||
Supported control gear
|
See table below.
|
||||||||||||
|
|||||||||||||
a) Color type Tc (Color temperature) of Part 209 of the IEC 62386 standard is supported. | |||||||||||||
Digital inputs | |||||||||||||
Inputs
|
4, DI1 to DI4
|
||||||||||||
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
Follow proper installation wiring diagrams and instructions. For more information on wiring, see the SpaceLogic Hardware Reference Guide.
Use |
Part number |
Reference |
Connector type |
Suitable for cable diameters mm (inches) |
Marking |
Color of coding / housing |
Minimum order quantity |
Power supply input |
SXWRPCCONWWPOW |
91.931.4053.1 |
Female |
5.6–11 (0.22–0.43) |
L, PE, N |
Black /Black |
100 |
DALI outputs |
SXWRPCCONWWLIGHT |
91.922.3453.0 |
Male |
6–7.7 (0.24–0.30) |
D2, D1 D2: DA+ D1: DA- |
Pastel blue /White |
100 |
Digital inputs |
SXWRPCCONWDI |
91.921.2353.0 |
Female |
3.4–5.5 (0.14–0.21) |
1, 2 1: DI1..4 2: RET |
Light blue /White |
100 |
The external connectors need to be ordered separately. The connectors can be ordered in quantities of 50 or 100 from Schneider Electric using the above part numbers. The connectors can also be ordered directly from Wieland using the above reference numbers. For more information, see the Wieland Electric web site.