earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : AO-8, AO-V-8, AS-B, CRS-HH-REL-10, DI-16, DO-FA-12, DO-FC-8, IP-IO , MP-C, MP-V, RP-C, RP-C-EXT-0-10V-4, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-2-LV-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-BL-SMI-2-LV-PD, RP-C-EXT-BL-SMI-4-HV-PD, RP-C-EXT-DALI, RP-C-EXT-DALI-M-PD, RP-C-EXT-KNX, RP-C-EXT-REL-4, RP-IO , RP-V, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
25/06/2025

Wire Sizes and Lengths

arrow1_rotationWire Sizes and Lengths for the Central IO Modules arrow1_rotationWire Sizes and Lengths for the AS-B Servers arrow1_rotationWire Sizes and Lengths for the RP-C 24 V Controller Models arrow1_rotationWire Sizes and Lengths for the RP-C 230 V Controller Models arrow1_rotationWire Sizes and Lengths for the RP-V Controllers arrow1_rotationWire Sizes and Lengths for the MP-C Controllers arrow1_rotationWire Sizes and Lengths for the MP-V Controllers arrow1_rotationWire Sizes and Lengths for the IP-IO Modules arrow1_rotationWire Sizes and Lengths for the RP-IO Modules arrow1_rotationWire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules arrow1_rotationWire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules arrow1_rotationWire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules arrow1_rotationWire Sizes and Lengths for the SMI Interface of the RP Controller Expansion SMI Blind Modules arrow1_rotationWire Sizes and Lengths for the Low-Voltage (24 VDC) Blind Outputs of the RP Controller Expansion Blind Modules arrow1_rotationWire Sizes and Lengths for the 0-10V Light Outputs of the RP Controller Expansion Light Modules arrow1_rotationWire Sizes and Lengths for the RP Controller Expansion Zigbee Modules arrow1_rotationWire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module arrow1_rotationWire Sizes and Lengths for the CRS-HH-REL-10 Relay Module arrow1_rotationWire Sizes and Lengths for the KNX Modbus Gateway

This section provides recommendations on minimum wire sizes (cross-sectional areas) and maximum wire lengths for the wires connected to the screw terminals of Central IO modules, AS-B servers, RP and MP controllers, and IP-IO and RP-IO I/O modules. Recommendations on minimum wire sizes and maximum cable lengths for the various inputs and outputs of the different RP controller expansion modules and the KNX Modbus gateway are also provided. The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

Wire Sizes and Lengths for the Central IO Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the Central IO modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the Central IO Modules .

Wire Sizes and Lengths for the AS-B Servers

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the AS-B servers.

Pour plus d'informations, voir Wire Sizes and Lengths for the AS-B Servers .

Wire Sizes and Lengths for the RP-C 24 V Controller Models

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the RP-C 24 V controller models.

Pour plus d'informations, voir Wire Sizes and Lengths for the RP-C 24 V Controller Models .

Wire Sizes and Lengths for the RP-C 230 V Controller Models

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the RP-C 230 V controller models.

Pour plus d'informations, voir Wire Sizes and Lengths for the RP-C 230 V Controller Models .

Wire Sizes and Lengths for the RP-V Controllers

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the RP-V controllers.

Pour plus d'informations, voir Wire Sizes and Lengths for the RP-V Controllers .

Wire Sizes and Lengths for the MP-C Controllers

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the MP-C controllers.

Pour plus d'informations, voir Wire Sizes and Lengths for the MP-C Controllers .

Wire Sizes and Lengths for the MP-V Controllers

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the MP-V controllers.

Pour plus d'informations, voir Wire Sizes and Lengths for the MP-V Controllers .

Wire Sizes and Lengths for the IP-IO Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the IP-IO modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the IP-IO Modules .

Wire Sizes and Lengths for the RP-IO Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the RP-IO modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the RP-IO Modules .

Wire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the power input and power output (power distribution) of the RP controller expansion modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules .

Wire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the digital inputs of the RP controller expansion modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules .

Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the DALI bus of the RP controller expansion DALI light modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules .

Wire Sizes and Lengths for the SMI Interface of the RP Controller Expansion SMI Blind Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the SMI interface of the RP controller expansion SMI blind modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the SMI Interface of the RP Controller Expansion SMI Blind Modules .

Wire Sizes and Lengths for the Low-Voltage (24 VDC) Blind Outputs of the RP Controller Expansion Blind Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the low-voltage (24 VDC) Blind outputs of the RP controller expansion blind modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the Low-Voltage (24 VDC) Blind Outputs of the RP Controller Expansion Blind Modules .

Wire Sizes and Lengths for the 0-10V Light Outputs of the RP Controller Expansion Light Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the 0-10V Light outputs of the RP controller expansion light modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the 0-10V Light Outputs of the RP Controller Expansion Light Modules .

Wire Sizes and Lengths for the RP Controller Expansion Zigbee Modules

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the RP controller expansion Zigbee DALI and 0-10V modules.

Pour plus d'informations, voir Wire Sizes and Lengths for the RP Controller Expansion Zigbee Modules .

Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the DALI bus of the Zigbee DALI module (RP-C-EXT-ZB-DALI).

Pour plus d'informations, voir Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module .

Wire Sizes and Lengths for the CRS-HH-REL-10 Relay Module

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the CRS-HH-REL-10 relay module.

Pour plus d'informations, voir Wire Sizes and Lengths for the CRS-HH-REL-10 Relay Module .

Wire Sizes and Lengths for the KNX Modbus Gateway

This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the KNX Modbus gateway (RP-C-EXT-KNX).

Pour plus d'informations, voir Wire Sizes and Lengths for the KNX Modbus Gateway .

  • I/O Wiring
  • Wire Sizes and Lengths for the Central IO Modules
  • Wire Sizes and Lengths for the AS-B Servers
  • Wire Sizes and Lengths for the RP-C 24 V Controller Models
  • Wire Sizes and Lengths for the RP-C 230 V Controller Models
  • Wire Sizes and Lengths for the RP-V Controllers
  • Wire Sizes and Lengths for the MP-C Controllers
  • Wire Sizes and Lengths for the MP-V Controllers
  • Wire Sizes and Lengths for the IP-IO Modules
  • Wire Sizes and Lengths for the RP-IO Modules
  • Wire Sizes and Lengths for the Power Input and Power Output of the RP Controller Expansion Modules
  • Wire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules
  • Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules
  • Wire Sizes and Lengths for the SMI Interface of the RP Controller Expansion SMI Blind Modules
  • Wire Sizes and Lengths for the Low-Voltage (24 VDC) Blind Outputs of the RP Controller Expansion Blind Modules
  • Wire Sizes and Lengths for the 0-10V Light Outputs of the RP Controller Expansion Light Modules
  • Wire Sizes and Lengths for the RP Controller Expansion Zigbee Modules
  • Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module
  • Wire Sizes and Lengths for the CRS-HH-REL-10 Relay Module
  • Wire Sizes and Lengths for the KNX Modbus Gateway
  • RP-C Models
  • RP-V Models