earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-C
Funcionalidades: Hardware
Versión del producto: 2023, 2024
13/02/2024

Wire Sizes and Lengths for the RP-C 24 V Controller Models

This section provides recommendations on wire sizes and lengths for the RP-C 24 V controller models.

Para obtener más información, consulte RP-C Models .

The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

Tabla: Wire Sizes and Lengths for the RP-C 24 V Controller Models

Terminals

Minimum Cross-sectional Area

Maximum Cable Length

Power input terminals (1, 2)

0.75 mm² (18 AWG) a

According to local wiring rules

Earth ground terminal (3)

0.75 mm² (18 AWG) a

According to local wiring rules

Return (RET) terminals (4, 5), connected to ground rail

1.3 mm² (16 AWG)

As short as possible within the same panel, maximum 1.5 m (4.8 ft).

Universal inputs/outputs as digital b inputs

0.34 mm² (22 AWG)

200 m (650 ft)

RS-485 terminals (6, 7, 8) c

Para obtener más información, consulte RS-485 Communications .

Para obtener más información, consulte RS-485 Communications .

Universal inputs/outputs as analog d inputs

0.34 mm² (22 AWG)

100 m (330 ft)

Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F)

0.75 mm² (18 AWG)

75 m (250 ft)

Universal inputs/outputs as temperature (thermistor) inputs, up to 75 °C (167 °F)

1.5 mm² (15 AWG)

150 m (500 ft)

Universal inputs/outputs as temperature (thermistor) inputs, up to 150 °C (302 °F)

1.5 mm² (15 AWG)

75 m (250 ft)

Universal inputs/outputs, for actuators and transmitters powered from the same transformer as the RP-C

0.75 mm² (18 AWG)

20 m (65 ft)

Universal inputs/outputs, for actuators and transmitters powered from their own transformer (external or internal)

0.34 mm² (22 AWG)

200 m (650 ft)

Universal inputs/outputs as voltage outputs, for actuators powered from their own transformer (external or internal) or when the outputs have isolated converters

0.34 mm² (22 AWG)

200 m (650 ft)

Relay outputs

According to local wiring rules e

According to local wiring rules e

High power relay output

According to local wiring rules e

According to local wiring rules e

Solid-state relay (SSR) outputs

0.5 mm² (20 AWG) e

According to local wiring rules e

  1. Use wires rated for at least 90 °C (194 °F).
  2. Digital or counter inputs.
  3. Only available on RP-C 24 V controller models with “-M” in the product name.
  4. Supervised, voltage, current, resistive, or 2-wire RTD temperature inputs. Models with “-M” in the product name do not support RTDs.
  5. Confirm the voltage drop from the external load current and the wire resistance (the product of the wire size and length) to obtain the appropriate voltage arriving at the controlled field device (load), to reliably energize and maintain the control action.
  • I/O Wiring
  • Wire Sizes and Lengths
  • Wire Sizes and Lengths for the RP-C 230 V Controller Models
  • RP-C Controllers
  • RP-C Models
  • RP-C Screw Terminals
  • Wiring
  • RS-485 Communications