Powering Up an RP Controller Expansion Blind Module

You perform the following steps to power up an RP controller expansion blind module.

Показать больше
action_close

The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

A DIN rail is a common and convenient technique for installing the RP controller expansion module along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the RP controller expansion module rail and adjacent rails or other devices.

The RP controller expansion module is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke RP controller expansion module installed on a horizontal DIN rail
Рисунок: RP controller expansion module installed on a horizontal DIN rail

The restrictions on installing the device in other orientations, as well as the normal operating conditions, differ between different types of RP controller expansion modules.

Примечание

EXPANSION MODULE DAMAGE

Follow the installation orientation restrictions that apply to the specific RP controller expansion module.

Failure to follow these instructions can result in equipment damage.

Таблица: Normal Operating Conditions for Different Types of RP Controller Expansion Modules

Type of Module

Ambient Temperature

Light modules, high-voltage blind modules, and relay modules

0 to 50 °C (32 to 122 °F)

Low-voltage blind modules

0 to 40 °C (32 to 104 °F)

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the light modules and high-voltage blind modules can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

  • Face down from a ceiling. See “d” in the following figure.

  • Rotated 180 degrees from the horizontal position with device label text up and down. See “e” in the following figure.

  • Face up on a horizontal surface. See “f” in the following figure.

 
action_zoom_plus_stroke Installation orientation restrictions for light modules and high-voltage blind modules in normal conditions
Рисунок: Installation orientation restrictions for light modules and high-voltage blind modules in normal conditions

Under normal operating conditions of 0 to 40 °C (32 to 104 °F), the low-voltage blind modules can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

  • Face down from a ceiling. See “d” in the following figure.

  • Rotated 180 degrees from the horizontal position with device label text up and down. See “e” in the following figure.

The only installation orientation that is not supported for the low-voltage blind modules is when the device is installed face up on a horizontal surface. See “f” in the following figure. In the face up position, the low-voltage blind module's thermal specifications may be exceeded, which can damage the module.

 
action_zoom_plus_stroke Installation orientation restrictions for low-voltage blind modules in normal conditions
Рисунок: Installation orientation restrictions for low-voltage blind modules in normal conditions

All RP controller expansion module models are recommended to be installed in a cabinet, unless local regulations allow an exception.

The RP controller expansion modules can be installed in a standard DIN enclosure/cabinet.

Примечание

Local panel regulations should be followed when installing the RP controller expansion modules in a distribution panel.

 
action_zoom_plus_stroke RP controller expansion modules installed on horizontal DIN rails in a cabinet
Рисунок: RP controller expansion modules installed on horizontal DIN rails in a cabinet

When installing RP controller expansion modules in a DIN enclosure or cabinet, it is recommended to provide ample space between the DIN rails and modules for sufficient ventilation.

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

Примечание

EXPANSION MODULE DAMAGE

Use an end clip (part number SXWDINEND10001) when you install the RP controller expansion module on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
Рисунок: End clip for DIN 35 fixed across the DIN rail

The RP controller expansion light, blind, and RP-C-EXT-REL-4 relay modules have connectors that allow the matching, external connectors (and cables) for the power supply, outputs, and digitals input to be plugged in on site quickly and easily. Более подробную информацию см. RP Controller Expansion Module Pluggable Connectors .

 
action_zoom_plus_stroke RP controller expansion module (example) with connectors for outputs, power input, and digital inputs
Рисунок: RP controller expansion module (example) with connectors for outputs, power input, and digital inputs

The RP controller expansion CRS-HH-REL-10 relay module has connectors for pluggable screw terminal blocks, which are delivered in a plastic bag with the device. The terminal blocks are easy to install and remove from the device. Более подробную информацию см. RP Controller Expansion Module Pluggable Connectors .

 
action_zoom_plus_stroke CRS-HH-REL-10 relay module with connectors for pluggable screw terminal blocks
Рисунок: CRS-HH-REL-10 relay module with connectors for pluggable screw terminal blocks

The RP controller expansion module has four anchor points that can be used to fasten cable ties or other accessories for bundling light weight wires.

 
action_zoom_plus_stroke Anchor points for cable ties
Рисунок: Anchor points for cable ties

It is recommended to always anchor excess cabling, in accordance with the local regulations, to alleviate all stresses on connectors and cable assemblies. When excess cabling is coiled and left suspended only from the module’s connectors, damage can occur to connectors and/or cable assemblies.

Примечание

CONNECTOR OR CABLE ASSEMBLY DAMAGE

Anchor the excess cabling to alleviate all stresses on connectors and cable assemblies.

Failure to follow these instructions can result in equipment damage.

Примечание

EXPANSION MODULE DAMAGE

Before powering up the RP controller expansion module, ensure that the input power voltage level meets the specifications of the device.

Failure to follow these instructions can result in equipment damage.

Примечание

BLINDS/AWNINGS DAMAGE

Before turning on or connecting the AC mains power (230 VAC) to the high-voltage blind module, ensure that the module is powered up by the RP-C room bus (24 VDC).

Failure to follow these instructions can result in equipment damage.

To power up an RP controller expansion blind module
  1. Check that all wiring is correct.

  2. Ensure that appropriate cable strain relief is provided, especially for wires that carry 30 VAC or 42.4 VDC or above.

  3. Ensure that the address rotary switch on the device is configured to give the device a unique address on the room bus, within the range supported by the RP-C controller model.

    Более подробную информацию см. Configuring the Room Bus Address for an RP Controller Expansion Module .

  4. Ensure that the RP-C room bus (24 VDC) is connected to the RP controller expansion module.

    Более подробную информацию см. Connecting RP Controller Expansion Modules to an RP Controller .

  5. After powering up the module through the room bus, check that the Status LED changes to a constant green light after a few seconds.

    Более подробную информацию см. RP Controller Expansion Module LEDs .

  6. Ensure that the 230 VAC at 50/60 Hz is supplied to the Power Input of the module.

     