SpaceLogic* RP-C-EXT-ZB-DALI Zigbee DALI module communicates with the SpaceLogic RP room controller over the Zigbee TM wireless protocol and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).
The Zigbee DALI module enables control of different types of lights equipped with DALI electrical ballasts for 220–240 VAC line voltage. The Zigbee DALI module can distribute power (220–240 VAC) from an external power supply to the lights (DALI control gear).
The Zigbee DALI module supports LED lamp control gear (LED drivers) of Device Type 6 (DT6) and fluorescent lamp control gear of Device Type 0 (DT0).
Lighting can be controlled by the RP-C through motion detection and light intensity measurement provided by the Multi-sensor or by SpaceLogic Sensors connected to the RP-C.
* Formerly known as SmartX.
The Zigbee DALI module has the following features:
Wireless communication with the RP-C room controller
Broadcast addressing of DALI devices
One DALI channel for power and control of 230 VAC powered lights (see output specification for limitations on inrush current)
Power consumption monitoring per module
Suitable for mounting in ceilings
Integrated 2.4 GHz antenna
Configuration through EcoStruxure Building Operation software
Status LED for the device
The light output is connected to the power supply network via the Zigbee DALI module. For the DALI bus wires, you may use the standard installation equipment permitted for ELV (Extra-Low Voltage) installations. The DALI bus meets SELV (Safety Extra-Low Voltage) requirements.
The DALI interface has the following features:
Using the DALI broadcast command, all lights connected to the output are controlled simultaneously for switching on/off and dimming.
Management of ballast and lamp alarms
Automatic addressing of lights
Product |
Part number |
RP-C-EXT-ZB-DALI
|
SXWREZBDALI110001
|
AC input | ||||||||||
Nominal voltage
|
230 VAC
|
|||||||||
Rated voltage range
|
220 to 240 VAC
|
|||||||||
Frequency
|
50/60 Hz
|
|||||||||
Maximum load current
|
5 A
|
|||||||||
Maximum power consumption
|
<1 W
|
|||||||||
Power input protection
|
MOV suppression and internal fuse
|
|||||||||
AC output | ||||||||||
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
|||||||||
Maximum load current
|
5 A
|
|||||||||
Maximum inrush current
|
30 A (<5 ms)
|
|||||||||
Wireless connectivity | ||||||||||
Communication protocol
|
Zigbee 3.0
|
|||||||||
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
|||||||||
Maximum output power
|
7 dBm
|
|||||||||
Effective indoor radio signal range
|
30 m (98 ft)
|
|||||||||
Antenna
|
Integrated antenna
|
|||||||||
Environment | ||||||||||
Ambient temperature, operating
|
-20 °C to +50 °C (-4 °F to +122 °F)
|
|||||||||
Case temperature, maximum
|
75 °C (167 °F)
|
|||||||||
Ambient temperature, storage
|
-30 to +65 °C (-22 to +149 °F)
|
|||||||||
Humidity
|
Maximum 85 % RH non-condensing
|
|||||||||
Material | ||||||||||
Plastic flame rating
|
UL94 V-0
|
|||||||||
Ingress protection rating
|
IP 20
|
|||||||||
Mechanical | ||||||||||
Dimensions
|
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
|
|||||||||
Weight
|
0.126 kg (0.278 lb)
|
|||||||||
Installation
|
Ceiling
|
|||||||||
Indoor use only
|
||||||||||
Output terminals
|
Fixed
|
|||||||||
Left side: 1 x 6-pin terminal block
|
||||||||||
Right side: 1 x 2-pin terminal block
|
||||||||||
Compatibility | ||||||||||
EcoStruxure Building Operation
|
version 4.0.1 and later
|
|||||||||
Agency compliances | ||||||||||
EMC
|
ETSI EN 301 489-1 V2.1.1 (2017); ETSI EN 301 489-17 V3.1.1 (2017); BS/EN 61000-3-2:2014; BS/EN 61000-3-3:2013; BS/EN 55015:2013; BS/EN 61547:2009
|
|||||||||
Radio
|
ETSI EN 300 328 V2.1.1 (2016)
|
|||||||||
Safety standards
|
BS/EN 62493:2015; BS/EN 62479:2010; BS/EN 61347-1:2015; BS/EN 61347-2-11:2001
|
|||||||||
Power consumption monitoring
|
BS/EN 61010-1:2010
|
|||||||||
Hardware | ||||||||||
Main microcontroller | ||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
|||||||||
Frequency
|
40 MHz
|
|||||||||
SRAM (embedded)
|
64 KB
|
|||||||||
Flash memory (embedded)
|
512 KB
|
|||||||||
Memory | ||||||||||
NOR flash memory
|
1 MB
|
|||||||||
DALI microcontroller | ||||||||||
CPU type
|
ARM Cortex-M0 single-core
|
|||||||||
Frequency
|
32 MHz
|
|||||||||
SRAM (embedded)
|
16 KB
|
|||||||||
Flash memory (embedded)
|
32 KB
|
|||||||||
Additional hardware | ||||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
|||||||||
Reset button
|
Push-button switch
|
|||||||||
Energy metering | ||||||||||
Measurement accuracy
|
See table below.
|
|||||||||
|
||||||||||
DALI light output | ||||||||||
Outputs
|
1 (1 DALI channel), terminals DA+ and DA-
|
|||||||||
DALI bus voltage
|
17 VDC
|
|||||||||
Maximum supply current
|
250 mA
|
|||||||||
Guaranteed supply current
|
90 mA
|
|||||||||
Maximum cable length
|
See the SpaceLogic Hardware Reference Guide
|
|||||||||
DALI devices | ||||||||||
Supported control gear
|
See table below.
|
|||||||||
|