SpaceLogic™ RP-C-EXT-ZB-0-10V Zigbee 0-10V module communicates with the SpaceLogic RP room controller over the Zigbee TM wireless protocol and provides I/O expansion for 0-10V lighting control.
The Zigbee 0-10V module enables dimming of different types of lights equipped with electrical ballasts for 220–240 VAC line voltage. The Zigbee 0-10V module can distribute power (220–240 VAC) from an external power supply to the lights.
Lighting can be controlled by the RP controller through motion detection and light intensity measurement provided by the Multi-sensor or Insight-Sensor, or by SpaceLogic Sensors connected to the RP controller.
The Zigbee 0-10V module has the following features:
Wireless communication with the RP room controller
0-10V light output for control of 230 VAC powered lights (see output specification for limitations on inrush current)
Power consumption monitoring per module
Suitable for mounting in ceilings
Integrated 2.4 GHz antenna
Configuration through EcoStruxure Building Operation software
Status LED for the device
The light output is connected to the power supply network through the Zigbee 0-10V module. For the 0-10 VDC control signal wires, you may use the standard installation equipment permitted for ELV (Extra-Low Voltage) installations. The 0-10 VDC control signal meets SELV (Safety Extra-Low Voltage) requirements.
The analog interface has the following features:
The lights connected to the output belong to the same group and are thus controlled simultaneously (same ON / OFF / Dimming setpoint).
Power to the ballasts is cut off when the lights are switched off.
Product |
Part number |
RP-C-EXT-ZB-0-10V
|
SXWREZB010110001
|
AC input | |||||||
Nominal voltage
|
230 VAC
|
||||||
Rated voltage range
|
220 to 240 VAC
|
||||||
Frequency
|
50/60 Hz
|
||||||
Maximum load current
|
5 A
|
||||||
Maximum power consumption
|
<1 W
|
||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||
AC output | |||||||
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
||||||
Maximum load current
|
5 A
|
||||||
Maximum inrush current
|
30 A (<5 ms)
|
||||||
Wireless connectivity | |||||||
Communication protocol
|
Zigbee 3.0
|
||||||
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
||||||
Maximum output power
|
7 dBm
|
||||||
Effective indoor radio signal range
|
30 m (98 ft)
|
||||||
Antenna
|
Integrated antenna
|
||||||
Environment | |||||||
Ambient temperature, operating
|
-20 °C to +50 °C (-4 °F to +122 °F)
|
||||||
Case temperature, maximum
|
75 °C (167 °F)
|
||||||
Ambient temperature, storage
|
-30 to +65 °C (-22 to +149 °F)
|
||||||
Humidity
|
Maximum 85 % RH non-condensing
|
||||||
Material | |||||||
Plastic flame rating
|
UL94 V-0
|
||||||
Ingress protection rating
|
IP 20
|
||||||
Mechanical | |||||||
Dimensions
|
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
|
||||||
Weight
|
0.126 kg (0.278 lb)
|
||||||
Installation
|
Ceiling
|
||||||
Indoor use only
|
|||||||
Output terminals
|
Fixed
|
||||||
Left side: 1 x 6-pin terminal block
|
|||||||
Right side: 1 x 2-pin terminal block
|
|||||||
Compatibility | |||||||
EcoStruxure BMS server communication
|
|||||||
EcoStruxure Building Operation
|
version 4.0.1 and later
|
||||||
Power consumption monitoring support
|
|||||||
EcoStruxure Building Operation
|
version 5.0.1 and later
|
||||||
Agency compliances | |||||||
EMC
|
ETSI EN 301 489-1 V2.1.1 (2017); ETSI EN 301 489-17 V3.1.1 (2017); BS/EN 61000-3-2:2014; BS/EN 61000-3-3:2013; BS/EN 55015:2013; BS/EN 61547:2009
|
||||||
Radio
|
ETSI EN 300 328 V2.1.1 (2016)
|
||||||
Safety standards
|
BS/EN 62493:2015; BS/EN 62479:2010; BS/EN 61347-1:2015; BS/EN 61347-2-11:2001
|
||||||
Power consumption monitoring
|
BS/EN 61010-1:2010
|
||||||
Hardware | |||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||
Frequency
|
40 MHz
|
||||||
SRAM (embedded)
|
64 KB
|
||||||
Flash memory (embedded)
|
512 KB
|
||||||
NOR flash memory
|
1 MB
|
||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
||||||
Reset button
|
Push-button switch
|
||||||
Energy metering | |||||||
Measurement accuracy
|
See table below.
|
||||||
|
|||||||
0-10V light output | |||||||
Outputs
|
1, terminals 0-10V AO and COM
|
||||||
Output voltage
|
0 to 10 VDC
|
||||||
Sink current
|
40 mA
|
For more information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.