Specifikationer

Specifikationer


Produkter: RP-C-EXT-KNX
Funktionaliteter: Maskinteknik, Maskinvara
Produktversion: 3.3, 2022, 2023, 2024, 7.0
2025-07-29

Spacelogic RP-C-EXT-KNX

arrow1_rotationInledning arrow1_rotationFunktioner arrow1_rotationSpecifikationer arrow1_rotationAnslutningar, lysdioder och knappar arrow1_rotationKNX-datapunktstyper som stöds
 
action_zoom_plus_stroke RP-C-EXT-KNX (KNX Modbus-gateway)
Figur: RP-C-EXT-KNX (KNX Modbus-gateway)

Inledning

SpaceLogic™ RP-C-EXT-KNX KNX Modbus gateway connects to the SpaceLogic RP controllers and provides an interface between the controller and KNX devices such as push-buttons, sensors, and control units for lights, blinds, and room temperature.

KNX Modbus-gateway kan användas för dubbelriktad styrning och övervakning av alla parametrar och funktioner i anslutna KNX-enheter, vilka kan användas för att reglera belysning och persienner i ett rum.

KNX Modbus-gateway är ett gränssnitt mellan Modbus och KNX som ansluter till en av RP-regulatorns konfigurerbara RS-485-portar. KNX Modbus-gateway säkerställer galvanisk isolering mellan KNX-buss och RP-regulatorns Modbus-nätverk (RS-485).

KNX Modbus-gateway kan programmeras via ETS©-programvara för installation, konfiguration och idrifttagning av KNX-enheter. Tilldelning av KNX-objekt till Modbus-register konfigureras genom parametrar i produktdatabasen ETS.

KNX Modbus-gateway stöder långa KNX-ramar.

KNX Modbus-gateway är avsedd att installeras på DIN-skena med en enhets bredd (18 mm eller 0,7 tum).

KNX Modbus-gateway har två tryckknappar och tre lysdioder på fronten för aktivering av lokal drift av enhet samt för statusindikering.

KNX Modbus-gateway kan användas tillsammans med standard Schneider Electric KNX strömförsörjning för att strömförsörja KNX-enheter på KNX-bussen.

Funktioner

KNX Modbus-gateway har följande funktioner:

  • Upp till 250 KNX-datapunkter (10 KNX-enheter) kan anslutas till KNX Modbus-gateway

  • Strömförsörjning och datakommunikation via RP-regulatorns Modbus-nätverk (RS-485)

  • Konfiguration via programvaran EcoStruxure Building Operation

  • Programmering via programvaran ETS©

  • Långa KNX-ramar stöds

  • Avsedd för installation på DIN-skena

  • Tryckknappar för synkronisering (redigering) och läsning av alla objekt i KNX-grupp

  • Statuslysdioder för enhetsläge, KNX-buss och Modbus-kommunikation

Modbus-nätverk

RP-regulatorn har två RS-485-portar, vilka kan konfigureras för olika typer av nätverk. När den är konfigurerad för Modbus-kommunikation levererar RP-regulatorn också strömförsörjning (24 VDC) till KNX Modbus-gateway via RS-485-gränssnittet.

Modbus RTU-protokollet används för RP-regulatorns Modbus-nätverk. RS-485 är gränssnittet för eletricitet.

The KNX Modbus gateway has two 3-position pluggable screw terminal blocks for connection to the RP controller Modbus (RS-485) network. The RP controller's RS-485 ports are RJ45 ports.

Max. en KNX Modbus-gateway kan anslutas till varje RP-regulator.

Tabell: Artikelnummer

Produkt

Artikelnummer

RP-C-EXT-KNX
SXWREKNX10001

Specifikationer

Electrical
DC input supply voltage
24 VDC
  
Drivs av RP-regulatorn
Maximum power consumption
<0.24 W from the KNX bus
  
<0.24 W from the RP controller
Environment
Ambient temperature, operating
-5 °C to +45 °C (23 °F to +113 °F)
Ambient temperature, storage
-25 to +70 °C (-13 to +158 °F)
Humidity
5 to 93 % RH non-condensing
Material
Ingress protection rating
IP 20
Mechanical
Dimensions
18 W x 90 H x 60 D mm (0.7 W x 3.5 H x 2.4 D in.)
 
action_zoom_plus_stroke
Weight
50 g (1.76 oz)
Installation
DIN rail
Software requirements
EcoStruxure Building Operation software
version 3.2 and later
ETS® software 
version 5 and later
RP controller firmware
version 3.02 och senare
Agency compliances
Emission
BS/EN 61000-6-3:2007 + A1:2011; BS/EN 50491-5-2:2010
Immunity
BS/EN 61000-6-2:2005; BS/EN 50491-5-3:2010
Safety standards
IEC/BS/EN 63044-3:2018
Modbus-kommunikation med RP-regulator
Communication protocol (configurable)
Modbus RTU
Elektriskt gränssnitt
RS-485
  
Maximum total length of the RP controller Modbus (RS-485) network: 72 m (236 ft)
KNX bus communications
Transmission media
Twisted pair (TP)
Maximum APDU length
55
Device model
System B
Hardware
CPU type
ARM Cortex-M0+ single-core
Frequency
14.7456 MHz
SRAM (embedded)
32 KB
Flash memory (embedded)
256 KB
Status indicator
LED (green and red) that shows the KNX communication status
  
LED (green and red) that shows the Modbus RTU communication status
  
LED (green and red) that shows the device mode (operating or programming mode)
  
One LED (red) for programming mode
Buttons
One push-button for synchronization of KNX objects (writing all KNX group objects)
  
One push-button for reading all KNX group objects
  
One button for programming mode
Connectors
4-conductor KNX connectors with PUSH WIRE® connection, 2-pole, dark gray/red
Terminal blocks
3-position pluggable screw terminal block for power supply from the RP controller
  
3-position pluggable screw terminal block for Modbus communication with the RP controller
  
Wire cross-sectional area: 0.34 to 2.5 mm 2 (22 to 14 AWG)

Anslutningar, lysdioder och knappar

 
action_zoom_plus_stroke RP-C-EXT-KNX-anslutningar, lysdioder och knappar
Figur: RP-C-EXT-KNX-anslutningar, lysdioder och knappar

KNX-datapunktstyper som stöds

The KNX Modbus gateway supports a limited set of KNX datapoint types. Details can be found in the information below.

  • SpaceLogic RP-C Advanced
  • ETS Database for the KNX Modbus Gateway
  • ETS and the KNX Modbus Gateway
  • KNX Modbus Gateway RP-C-EXT-KNX