The RP-C-EXT-BL-4-HV-PD blind module connects to the RP-C room controllers and provides I/O expansion for high-voltage blind control.
The high-voltage blind module enables control and power supply (230 VAC) of motorized window blinds and shutters.
The blind module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.
The high-voltage blind modules have four Blind outputs for control of motorized window blinds that are powered by AC mains voltage (230 VAC).
Para obtener más información, consulte High-Voltage Blind Outputs .
The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.
The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.
Para obtener más información, consulte RP Controller Expansion Module Digital Inputs .
RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.
Para obtener más información, consulte RP Controller Expansion Module Energy Metering .
RP controller expansion modules have two types of memory, flash memory and RAM.
Para obtener más información, consulte RP Controller Expansion Module Memory .
The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.
Para obtener más información, consulte RP-C Room Bus .
Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.
Para obtener más información, consulte RP-C Room Bus .
The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.
Para obtener más información, consulte RP-C Room Bus .
The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.
The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.
Para obtener más información, consulte RP Controller Expansion Module Pluggable Connectors .
There is one or more LEDs on the front panel of the RP controller expansion modules.
Para obtener más información, consulte RP Controller Expansion Module LEDs .
All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.
Para obtener más información, consulte RP Controller Expansion Module Set Button .
The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.
Para obtener más información, consulte RP Controller Expansion Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Para obtener más información, consulte Wiring .
The RP controller expansion modules support different modes that can be used for maintenance purposes.
Para obtener más información, consulte RP Controller Expansion Module Maintenance Modes .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
Para obtener más información, consulte BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion modules with power distribution capability.
Para obtener más información, consulte RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals .
Electrical | |
Nominal voltage
|
230 VAC
|
Operating voltage range
|
+/-10 %
|
Frequency
|
50/60 Hz
|
Maximum current consumption
|
8 A
|
Room bus power consumption
|
0.3 W (24 VDC)
|
Protection
|
Maximum 16 A external fuse (circuit breaker) is needed
|
Overvoltage category
|
III
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
|
|
Weight
|
0.437 kg (0.963 lb)
|
Recommended installation
|
DIN rail or flat surface in a cabinet
a
|
a) It is recommended to install the device in an enclosure (cabinet), unless local regulations allow an exception. | |
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
Blind outputs: 4 x 4-pin Wieland GST15i4 connector
|
|
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
|
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Blind status indicator
|
One status LED (green) for each output
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
Energy metering | |
Energy consumption measurement | |
The energy consumption is measured in Wh, shared by the four outputs. | |
Accuracy class (according to IEC 61557-12)
|
Active energy measurement: Class 1
|
Typical measurement accuracy at room temperature
|
20 to 100 W: 5%
|
100 to 3000 W: 1%
|
|
Blind outputs | |
Motor control outputs for 230 VAC powered blind motors with automatic end stop detection. An end stop at the top position is required. An end stop at the bottom position is recommended. | |
Outputs
|
4, Blind 1 to Blind 4
|
Output terminals
|
N, PE, ↑ (UP), and ↓ (DOWN)
|
Power distribution
|
230 VAC (same voltage as power supply)
|
Maximum 2 A load per output
|
|
Maximum 8 A total load for the 4 outputs
|
|
Digital inputs | |
Inputs
|
4, DI1 to DI4
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
The RP-C-EXT-BL-4-HV-PD internal configuration with regards to the signal ground is shown in the following figure.