The RP-C-EXT-DALI-M-PD light module connects to the RP-C room controllers and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).
The DALI light module enables control of lights equipped with electronic ballasts, LED drivers, and other control gear with DALI interface.
The power distribution capability means that the DALI light module can supply the connected control gear with AC mains voltage (230 VAC) from the module's power input.
The DALI light module is a DALI-2 certified application controller. The DALI light module supports all electronic ballasts, LED drivers, and other control gear that are fully compliant with DALI version-1 or DALI-2.
The DALI light module is part of the RP Series expansion modules for connected room solution and can be combined with other modules from this product range.
The DALI light modules have four Light outputs, which are designed for control and power supply of lights with electronic ballasts, LED drivers, and other control gear with DALI interface.
Para obtener más información, consulte DALI Light Outputs with Power Distribution .
The RP Series expansion modules have four digital inputs, which can be used for sensing of dry contact digital inputs in applications such as interfacing with light switches and window contacts.
Para obtener más información, consulte RP Series Expansion Module Digital Inputs .
The RP Series expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.
Para obtener más información, consulte RP Series Expansion Module Built-in Power Supply .
RP Series expansion modules and multi-sensor have two types of memory, flash memory and RAM.
Para obtener más información, consulte RP Series Expansion Module and Multi-sensor Memory .
The DALI light module complies to version 2 of the IEC 62386 standard (DALI-2).
Para obtener más información, consulte DALI Light Module Supported Building Standards .
The RP Series expansion modules and multi-sensors have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules and multi-sensors on the room bus through a daisy-chain configuration.
Para obtener más información, consulte RP-C Room Bus .
Each RP Series expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus.
Para obtener más información, consulte RP-C Room Bus .
The RP-C room bus allows RP Series expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.
Para obtener más información, consulte RP-C Room Bus .
The RP Series expansion modules have PCB mounted connectors for the power input, outputs and digital inputs. The connectors are mechanically keyed and color-coded, which allows the matching external connectors to be plugged in on site quickly and easily.
Para obtener más información, consulte RP Series Expansion Module Pluggable Connectors .
There is one or more LEDs on the front panel of the RP Series expansion modules.
Para obtener más información, consulte RP Series Expansion Module LEDs .
All RP Series expansion modules have a Set button on the front. The Set button is reserved for future use.
Para obtener más información, consulte RP Series Expansion Module Set Button .
The RP Series expansion module can be installed on a DIN rail or flat surface.
Para obtener más información, consulte RP Series Expansion Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, SmartX IP Controller devices, and RP Series expansion modules and multi-sensors.
Para obtener más información, consulte Wiring .
The RP Series expansion modules and multi-sensors support different modes that can be used for maintenance purposes.
Para obtener más información, consulte RP Series Expansion Module and Multi-sensor Maintenance Modes .
Using WorkStation, you can update the firmware of multiple SmartX IP Controller devices and their attached SmartX Sensors, RP Series expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SmartX Sensors, RP Series expansion modules, and multi-sensors are supported by the SmartX IP Controller - RP Series.
Para obtener más información, consulte SmartX IP Controller Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP Series expansion modules with power distribution capability.
Para obtener más información, consulte RP Series Expansion Modules Regulatory Compliance and Approvals .
Electrical | |
Nominal voltage
|
230 VAC
|
Operating voltage range
|
+/-10 %
|
Frequency
|
50/60 Hz
|
Maximum current consumption
|
10 A
|
Room bus power consumption
|
0.3 W (24 VDC)
|
Protection
|
Maximum 16 A external fuse (circuit breaker) is needed
|
Overvoltage category
|
III
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
|
|
Weight
|
0.433 kg (0.955 lb)
|
Installation
|
DIN rail or flat surface
|
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
Light outputs: 4 x 5-pin Wieland GST15i5 connector
|
|
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
|
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
Main microcontroller | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
1024 KB
|
Memory | |
NOR flash memory
|
16 MB
|
DALI microcontroller | |
CPU type
|
ARM Cortex-M0 single-core
|
Frequency
|
32 MHz
|
SRAM (embedded)
|
8 KB
|
Flash memory (embedded)
|
64 KB
|
Additional hardware | |
Status indicator
|
LED (green and red) that shows the status of the device
|
Light status indicator
|
One status LED (green) for each output
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
DALI light outputs | |
Outputs
|
4, Light 1 to Light 4
|
The four outputs share one DALI channel. | |
Output terminals
|
N, PE, L, DA+, and DA-
|
DALI bus voltage
|
18 VDC
|
Maximum supply current
|
250 mA
|
Guaranteed supply current
|
64 mA
|
Maximum cable length
|
See chapter Wiring.
|
Power distribution
|
230 VAC (same voltage as power supply)
|
Maximum 5 A load per output
|
|
Maximum 10 A total load for the 4 outputs
|
|
Maximum 165 A inrush current (<20 ms) per output
|
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
4, DI1 to DI4
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA
|
The RP-C-EXT-DALI-M-PD internal configuration with regards to the signal ground is shown in the following figure.