The RP-C-EXT-0-10V-4-PD light module connects to the RP-C room controllers and provides I/O expansion for 0-10V lighting control.
The 0-10V light module enables control of lights equipped with electronic ballasts, LED drivers, and other 0-10V compatible control gear.
The power distribution capability means that the 0-10V light module can supply the connected control gear with AC mains voltage (230 VAC) from the module's power input.
The 0-10V light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.
The 0-10V light modules have four Light outputs, which are designed for control (dimming) and power supply of lights with electronic ballasts, LED drivers, and other 0-10V compatible control gear.
有关更多信息,请参阅 0-10V Light Outputs with Power Distribution .
The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.
The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.
有关更多信息,请参阅 RP Controller Expansion Module Digital Inputs .
The RP controller expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.
有关更多信息,请参阅 RP Controller Expansion Module Built-in Power Supply .
RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.
有关更多信息,请参阅 RP Controller Expansion Module Energy Metering .
RP controller expansion modules have two types of memory, flash memory and RAM.
有关更多信息,请参阅 RP Controller Expansion Module Memory .
The 0-10V light module supports 0-10 V lighting control according to both the current sourcing and current sinking standards.
The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.
有关更多信息,请参阅 RP-C Room Bus .
Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.
有关更多信息,请参阅 RP-C Room Bus .
The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.
有关更多信息,请参阅 RP-C Room Bus .
The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.
The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.
有关更多信息,请参阅 RP Controller Expansion Module Pluggable Connectors .
There is one or more LEDs on the front panel of the RP controller expansion modules.
有关更多信息,请参阅 RP Controller Expansion Module LEDs .
All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.
有关更多信息,请参阅 RP Controller Expansion Module Set Button .
The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.
有关更多信息,请参阅 RP Controller Expansion Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
有关更多信息,请参阅 Wiring .
The RP controller expansion modules support different modes that can be used for maintenance purposes.
有关更多信息,请参阅 RP Controller Expansion Module Maintenance Modes .
This section provides information on regulatory compliance and approvals for the RP controller expansion modules with power distribution capability.
有关更多信息,请参阅 BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion modules with power distribution capability.
有关更多信息,请参阅 RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals .
Electrical | |
Nominal voltage
|
230 VAC
|
Operating voltage range
|
+/-10 %
|
Frequency
|
50/60 Hz
|
Maximum current consumption
|
10 A
|
Room bus power consumption
|
0.3 W (24 VDC)
|
Protection
|
Maximum 16 A external fuse (circuit breaker) is needed
|
Overvoltage category
|
III
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
![]() |
|
Weight
|
0.418 kg (0.922 lb)
|
Recommended installation
|
DIN rail or flat surface in a cabinet
a
|
a) It is recommended to install the device in an enclosure (cabinet), unless local regulations allow an exception. | |
Connectors
|
Power input: 1 x 3-pin Wieland GST15i3 connector
|
Light outputs: 4 x 5-pin Wieland GST15i5 connector
|
|
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
|
|
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Light status indicator
|
One status LED (green) for each output
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
Energy metering | |
Energy consumption measurement | |
The energy consumption is measured in Wh, shared by the four outputs. | |
Accuracy class (according to IEC 61557-12)
|
Active energy measurement: Class 1
|
Typical measurement accuracy at room temperature
|
20 to 100 W: 5%
|
100 to 3000 W: 1%
|
|
0-10V light outputs | |
Outputs
|
4, Light 1 to Light 4
|
Output terminals
|
N, PE, L, AOn (n: 1 to 4), and COM
|
Analog output voltage
|
0 to 10 VDC
|
Maximum source/sink current
|
10 mA per output
|
Power distribution
|
230 VAC (same voltage as power supply)
|
Maximum 5 A load per output
|
|
Maximum 10 A total load for the 4 outputs
|
|
Maximum 165 A inrush current (<20 ms) per output
|
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
4, DI1 to DI4
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
The RP-C-EXT-0-10V-4-PD internal configuration with regards to the signal ground is shown in the following figure.