You configure RP controller expansion blind and light power modules to enable supply and control of both motorized blinds and shutters and lights equipped with electrical ballasts.
You configure the RP controller expansion multi-sensors to detect infrared motion and measure luminosity levels and RP controller expansion relay modules to use with lighting control modules that do not support power distribution.
To configure RPcontroller expansion modules
In WorkStation, in the
System Tree
pane, expand the RP controller and then click
Room Bus
.
In the
List View
, select the RP controller expansion module you want.
On the
File
menu, click
Properties
.
Click the
Basic
tab.
Edit the Basic properties.
Property
|
Description
|
Modbus address
|
Displays the Modbus address of the module on the room bus.
|
Status
|
Displays Offline when communication is disrupted between the RP controller and RP controller expansion modules.
|
Diagnostic flags
|
Displays a diagnostic flag when a Module type mismatch, Firmware upgrade failure, or crash report has been detected.
For more information, see RP Controller Expansion Module Diagnostics
.
|
Model name
|
Displays the model name of the RP controller expansion module.
|
Firmware version
|
Displays the firmware version of the RP controller expansion module.
|
Hardware version
|
Displays the hardware version of the RP controller expansion module.
|
Serial number
|
Displays the serial number of the RP controller expansion module.
|
Firmware upgrade
|
Displays Failed when the RP controller expansion module upgrade is unsuccessful.
|
Uptimes (s)
|
Displays the amount of time the module has been up and running.
|
Run level
|
Displays the current module run level.
|
Edit the Advanced properties.
Property
|
Description
|
Object ID
|
Displays the BACnet object type and the instance number of the module.
|
BACnet name
|
View the name of the BACnet object or type a new name to change the name.
If you plan on using the Commission mobile application to commission RP controller expansion modules, it is recommended that you use short names for the module and the point. The Commission mobile application reads the BACnet name, which is ModuleName_PointName by default. If module and object names combined exceed 32 characters, then the BACnet name may be difficult to read from the Commission mobile application unless you manually change the BACnet name.
|
BACnet type
|
Displays the type: structured view.
|
Profile name
|
Displays the unique name of the profile that describes the characteristics of the object, such as additional properties, behaviors, or requirements.
|
Log level
|
Select the trace logging level for the module.
|
Status LED mode
|
Select
Status LED mode
to display LED status including the following states:
Steady green: normal
Green with 2 second red flicker: normal but past error logged
Green flashing: normal.
For more information, see RP Controller Expansion Module LEDs
.
Red flashing or constant: not operational
Select
Off
should you not want to display LED status.
|