The Zigbee 0-10V module is equipped with eight fixed screw terminals.
Recommended terminal screw tightening torque: 0.50 Nm (4.4 lbf.in)
The Zigbee modules are equipped with screw terminal covers (doors) to reduce access to the screw terminals and wires. To access the screw terminals and wires, you need to loosen the two screws that hold each door in place and then open the door. These two screws are also used to fasten the cable to device, using an upper clamping bar and two lower (removable) clamping bars located under the door.
Recommended clamping screw tightening torque: 0.59 Nm (5.2 lbf.in)
The eight screw terminals are used as follows:
Three screw terminals for the power input
Three screw terminals for the power output
Two screw terminals for the 0-10V light output
An external power supply (220–240 VAC VAC) is connected to the power input. The power output is used for power distribution to the 0-10V control gear.
Terminal designation |
Usage |
Power input |
|
L (in) |
Line (L) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
N (in) |
Neutral (N) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
|
Protective earth ground |
Power output |
|
|
Protective earth ground |
N (out) |
Neutral (N) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
L (out) |
Line (L) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
0-10V light output |
|
0-10V AO |
0-10 V analog output |
COM |
Common terminal for the analog output |