The Zigbee DALI module is equipped with eight fixed screw terminals.
Recommended terminal screw tightening torque: 0.50 Nm (4.4 lbf.in)
The Zigbee modules are equipped with screw terminal covers (doors) to reduce access to the screw terminals and wires. To access the screw terminals and wires, you need to loosen the two screws that hold each door in place and then open the door. These two screws are also used to fasten the cable to device, using an upper clamping bar and two lower (removable) clamping bars located under the door.
Recommended clamping screw tightening torque: 0.59 Nm (5.2 lbf.in)
The eight screw terminals are used as follows:
Three screw terminals for the power input
Three screw terminals for the power output
Two screw terminals for the DALI light output
An external power supply (220–240 VAC) is connected to the power input. The power output is used for power distribution to the DALI control gear.
Terminal designation |
Usage |
Power input |
|
L (in) |
Line (L) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
N (in) |
Neutral (N) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
![]() |
Protective earth ground |
Power output |
|
![]() |
Protective earth ground |
N (out) |
Neutral (N) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
L (out) |
Line (L) lead, 220–240 VAC, 50/60 Hz, maximum 5 A |
DALI light output |
|
DA+ |
DALI bus line (+) |
DA- |
DALI bus line (-) |