earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-C
Funcionalidades: Hardware
Versión del producto: 2023, 2024
01/11/2023

RP-C-EXT-ZB-DALI

The RP-C-EXT-ZB-DALI Zigbee DALI module communicates with the RP-C room controller over the Zigbee TM wireless protocol and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).

The Zigbee DALI module enables control of different types of lights equipped with DALI electrical ballasts for 220–240 VAC line voltage. The Zigbee DALI module can distribute power (220–240 VAC) from an external power supply to the lights (DALI control gear).

The Zigbee DALI module supports LED lamp control gear (LED drivers) of Device Type 6 (DT6) and fluorescent lamp control gear of Device Type 0 (DT0).

The Zigbee DALI module supports broadcast addressing of the DALI devices. Using the DALI broadcast command, all lights connected to the output are controlled simultaneously for switching on/off and dimming.

The Zigbee DALI module provides one DALI channel (DALI bus). Up to 20 DALI control gear devices can be connected to the Zigbee DALI module.

 
action_zoom_plus_stroke RP-C-EXT-ZB-DALI – Zigbee DALI module
Figura: RP-C-EXT-ZB-DALI – Zigbee DALI module

Zigbee DALI Light Output and Power Output

The Zigbee DALI module has one DALI light output for control of lights with electronic ballasts, LED drivers, and other control gear with DALI interface and one power output for power distribution to the control gear.

Para obtener más información, consulte Zigbee DALI Light Output and Power Output .

Zigbee Modules Power Distribution

The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.

Para obtener más información, consulte Zigbee Modules Power Distribution .

Zigbee Modules Power Consumption Monitoring

RP controller expansion Zigbee modules can measure and monitor the power consumption for the loads connected to the module.

Para obtener más información, consulte Zigbee Modules Power Consumption Monitoring .

Zigbee Modules Memory

RP controller expansion Zigbee modules have two types of memory, flash memory and RAM.

Para obtener más información, consulte Zigbee Modules Memory .

Zigbee Modules Wireless Connectivity

The RP controller expansion Zigbee modules are Zigbee Certified Products. The Zigbee modules' wireless connectivity option is used for connecting to and communicating with the RP controller.

Para obtener más información, consulte Zigbee Modules Wireless Connectivity .

Zigbee Modules Screw Terminals

The RP controller expansion Zigbee modules have fixed screw terminals for the power input, power output, and light output.

Para obtener más información, consulte Zigbee Modules Screw Terminals .

Zigbee Modules LED

There is one LED on the front panel of the RP controller expansion Zigbee modules.

Para obtener más información, consulte Zigbee Modules LED .

Zigbee Modules Reset Button

The RP controller expansion Zigbee modules have a Reset button on the front.

Para obtener más información, consulte Zigbee Modules Reset Button .

Zigbee Modules Device Installation

The RP controller expansion Zigbee modules are designed to be installed on a flat surface on a ceiling.

Para obtener más información, consulte Zigbee Modules Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Para obtener más información, consulte Wiring .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Aviso

SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.

Para obtener más información, consulte BACnet/IP Device Firmware Management .

Zigbee Modules Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion Zigbee modules.

Para obtener más información, consulte Zigbee Modules Regulatory Compliance and Approvals .

Especificaciones

AC input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
AC output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
Wireless connectivity
Communication protocol
Zigbee 3.0
Frequency band
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
Maximum output power
7 dBm
Effective indoor radio signal range
30 m (98 ft)
Antenna
Integrated antenna
Environment
Ambient temperature, operating
-20 °C to +50 °C (-4 °F to +122 °F)
Case temperature, maximum
75 °C (167 °F)
Ambient temperature, storage
-30 to +65 °C (-22 to +149 °F)
Humidity
Maximum 85 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
Weight
0.126 kg (0.278 lb)
Installation
Ceiling
  
Indoor use only
Output terminals
Fixed
  
Left side: 1 x 6-pin terminal block
  
Right side: 1 x 2-pin terminal block
Hardware
Main microcontroller
CPU type
ARM Cortex-M4 single-core
Frequency
40 MHz
SRAM (embedded)
64 KB
Flash memory (embedded)
512 KB
Memory
NOR flash memory
1 MB
DALI microcontroller
CPU type
ARM Cortex-M0 single-core
Frequency
32 MHz
SRAM (embedded)
16 KB
Flash memory (embedded)
32 KB
Additional hardware
Status indicator
LED (green and red) that shows the status of the device
Reset button
Push-button switch
Energy metering
Measurement accuracy
See table below.

Measurement range

Measurement accuracy

< 50 W

+/-2 W

>= 50 W

+/-2 %

DALI light output
Outputs
1 (1 DALI channel), terminals DA+ and DA-
DALI bus voltage
17 VDC
Maximum supply current
250 mA
Guaranteed supply current
90 mA
Maximum cable length
See chapter Wiring.
DALI devices
Supported control gear
See table below.

Device type number

Type of control gear

Supported

Device Type 0 (DT0)

Fluorescent lamp control gear

Yes

Device Type 6 (DT6)

LED lamp control gear (LED drivers)

Yes

  • Hardware Overview
  • RP Controller Expansion Zigbee Modules
  • Zigbee DALI Light Output and Power Output
  • Zigbee Modules Power Distribution
  • Zigbee Modules Power Consumption Monitoring
  • Zigbee Modules Memory
  • Zigbee Modules Wireless Connectivity
  • Zigbee Modules Screw Terminals
  • Zigbee Modules LED
  • Zigbee Modules Reset Button
  • Zigbee Modules Device Installation
  • Wiring
  • BACnet/IP Device Firmware Management
  • Zigbee Modules Regulatory Compliance and Approvals