RP-C-EXT-DALI

The RP-C-EXT-DALI light module connects to the RP-C room controllers and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).

The DALI light module enables control of lights equipped with electronic ballasts, LED drivers, and other control gear with DALI interface as well as connection of DALI input devices such as sensors and push-buttons.

The DALI light module is a DALI-2 certified control device (application controller) with multi-master capability. DALI-2 compliance means benefits such as improved interoperability and easier installation and maintenance. The DALI light module can be used with DALI version-1 products because DALI-2 is designed to be backward compatible with DALI version-1. The multi-master capability of the DALI light module allows the module to function as a DALI master in a DALI network and can thus work together with DALI-2 sensors and push-buttons.

The DALI light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

 
action_zoom_plus_stroke RP-C-EXT-DALI – DALI light module without power distribution capability
Figure : RP-C-EXT-DALI – DALI light module without power distribution capability

DALI Inputs/Outputs without Power Distribution

The DALI light modules have four DALI inputs/outputs, which are designed for control of DALI light control gear such as lights with electronic ballasts, LED drivers, and other control gear with DALI interface as well as connection of DALI input devices such as sensors and push-buttons.

Pour plus d'informations, voir DALI Inputs/Outputs without Power Distribution .

RP Controller Expansion Module Digital Inputs

The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.

  • The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.

Pour plus d'informations, voir RP Controller Expansion Module Digital Inputs .

RP Controller Expansion Module Built-in Power Supply

The RP controller expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.

Pour plus d'informations, voir RP Controller Expansion Module Built-in Power Supply .

RP Controller Expansion Module Memory

RP controller expansion modules have two types of memory, flash memory and RAM.

Pour plus d'informations, voir RP Controller Expansion Module Memory .

DALI Light Module Supported Building Standards

The DALI light module complies to version 2 of the IEC 62386 standard (DALI-2).

Pour plus d'informations, voir DALI Light Module Supported Building Standards .

RP Controller Expansion Module Communication Ports

The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.

Pour plus d'informations, voir RP-C Room Bus .

RP Controller Expansion Module Address Switch

Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.

Pour plus d'informations, voir RP-C Room Bus .

RP-C Room Bus

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

Pour plus d'informations, voir RP-C Room Bus .

RP Controller Expansion Module Pluggable Connectors

The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.

  • The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.

Pour plus d'informations, voir RP Controller Expansion Module Pluggable Connectors .

RP Controller Expansion Module LEDs

There is one or more LEDs on the front panel of the RP controller expansion modules.

Pour plus d'informations, voir RP Controller Expansion Module LEDs .

RP Controller Expansion Module Set Button

All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.

Pour plus d'informations, voir RP Controller Expansion Module Set Button .

RP Controller Expansion Module Device Installation

The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

Pour plus d'informations, voir RP Controller Expansion Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Pour plus d'informations, voir Wiring .

RP Controller Expansion Module Maintenance Modes

The RP controller expansion modules support different modes that can be used for maintenance purposes.

Pour plus d'informations, voir RP Controller Expansion Module Maintenance Modes .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Déclaration

SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.

Pour plus d'informations, voir BACnet/IP Device Firmware Management .

RP Controller Expansion Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion modules.

Pour plus d'informations, voir RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals .

Spécifications

Electrical
Nominal voltage
100 to 277 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Power consumption
10 VA
Room bus power consumption
0.3 W (24 VDC)
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.352 kg (0.776 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
DALI inputs/outputs: 4 x 2-pin Wieland GST15i2 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
Main microcontroller
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
1024 KB
Memory
NOR flash memory
16 MB
DALI microcontroller
CPU type
ARM Cortex-M0 single-core
Frequency
32 MHz
SRAM (embedded)
8 KB
Flash memory (embedded)
64 KB
Additional hardware
Status indicator
LED (green and red) that shows the status of the device
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
DALI inputs/outputs
Inputs/outputs
4, Light 1 to Light 4
The four inputs/outputs share one DALI channel.
Input/output terminals
DA+ and DA-
DALI bus voltage
18 VDC
Maximum supply current
250 mA
Guaranteed supply current
64 mA
Maximum cable length
See chapter Wiring.
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Internal Configuration

The RP-C-EXT-DALI internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke RP-C-EXT-DALI internal configuration
Figure : RP-C-EXT-DALI internal configuration
  • Hardware Overview
  • RP Controller Expansion Modules
  • Light Modules
  • DALI Inputs/Outputs without Power Distribution
  • RP Controller Expansion Module Digital Inputs
  • RP Controller Expansion Module Built-in Power Supply
  • RP Controller Expansion Module Memory
  • DALI Light Module Supported Building Standards
  • RP-C Room Bus
  • RP Controller Expansion Module Pluggable Connectors
  • RP Controller Expansion Module LEDs
  • RP Controller Expansion Module Set Button
  • RP Controller Expansion Module Device Installation
  • Wiring
  • RP Controller Expansion Module Maintenance Modes
  • BACnet/IP Device Firmware Management
  • RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals