The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.
The Power Output terminals are marked:
N (out) – Neutral
L (out) – Line
The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.
The module has energy metering circuitry to measure the energy consumption for the total load connected to the module. Für weitere Informationen siehe Zigbee Modules Power Consumption Monitoring .
Power input | |
Nominal voltage
|
230 VAC
|
Rated voltage range
|
220 to 240 VAC
|
Frequency
|
50/60 Hz
|
Maximum load current
|
5 A
|
Maximum power consumption
|
<1 W
|
Power input protection
|
MOV suppression and internal fuse
|
Power output | |
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
Maximum load current
|
5 A
|
Maximum inrush current
|
30 A (<5 ms)
|