Zigbee Modules Power Distribution

arrow1_rotationEspecificaciones

The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.

The Power Output terminals are marked:

  •  
    action_zoom_plus_stroke
    – Protective earth ground

  • N (out) – Neutral

  • L (out) – Line

 
action_zoom_plus_stroke Zigbee module power distribution
Figura: Zigbee module power distribution

The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.

The module has energy metering circuitry to measure the energy consumption for the total load connected to the module. Para obtener más información, consulte Zigbee Modules Power Consumption Monitoring .

Especificaciones

Power input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
Power output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
  • RP Controller Expansion Zigbee Modules
  • RP-C-EXT-ZB-DALI
  • RP-C-EXT-ZB-0-10V
  • Zigbee Modules Power Consumption Monitoring
  • Zigbee DALI Module Screw Terminals
  • Zigbee 0-10V Module Screw Terminals