earth_america
user_standard Logga in
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Koncept

Koncept


Produkter: RP-C, RP-C-EXT-REL-4
Funktionaliteter: Maskinvara
Produktversion: 3.3, 2022, 2023, 2024, 7.0
2021-07-22

Relay Outputs on RP-C-EXT-REL-4

arrow1_rotationSpecifikationer

The RP-C-EXT-REL-4 relay module has four Relay outputs, which are designed for power supply and control of lights.

When a relay module is moved from one installation and reused in another installation, the module's “Cold start” and “System failure” values will be unknown. These values are stored in the module's persistent memory. The values control whether the relays will be on/active (energized) or off/inactive (de-energized) when the module is powered on (during a cold start) or powered off (due to a power outage). Connecting equipment to a relay module with unknown values on these properties entails a risk that the equipment will be damaged. To prevent this risk, the module's relay outputs need to be configured in EcoStruxure Building Operation WorkStation before connecting the equipment. This configuration means that the “Cold start” and “System failure” values for the module's Relay objects are configured to match the equipment to be connected. Mer information finns i Configuring Relays in the RP Controller Expansion Relay Module .

Obs!

EQUIPMENT DAMAGE

Before reusing a relay module from one installation to another and connecting equipment to the module, configure the module's relay outputs in EcoStruxure Building Operation WorkStation to match the equipment in the new installation.

Failure to follow these instructions can result in equipment damage.

The relay module distributes the AC mains voltage (100 to 277 VAC) from the Power Input to the light control gear connected to the four Relay outputs.

The Relay output connector has three terminals for power distribution:

  • N (Neutral)

  • PE (Protective earth ground)

  • L (Line)

 
action_zoom_plus_stroke Relay outputs
Figur: Relay outputs

The four outputs are independently controlled. The relay module uses a relay to control the power distribution to each output, by connecting or disconnecting the AC mains voltage to the output (L terminal). In the figure above, the relay is named K1 for the Relay 1 output, K2 for the Relay 2 output, and so on.

The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.

The maximum number of connected light control gear devices per module and per output is determined by the module's power distribution limitations. For more information, see section “Specifications”.

You can configure the module's “Cold start” and “System failure” values, which control whether the relays should be on/active (energized) or off/inactive (de-energized) under non-normal operating conditions such as when the module cold starts or loses communication with the RP-C controller. Mer information finns i Configuring Relays in the RP Controller Expansion Relay Module .

In the event of a power outage, the relays are set to the “System failure value”. When the power supply returns, the relays are temporarily set to the “Cold start value” before the relay module has all its properties reinforced by the parent RP-C controller. Mer information finns i RP Controller Expansion Relay Module Relay Properties - Basic Tab .

The module also has energy metering circuitry that supports the measurement of the energy consumption for the total load connected to the module. Mer information finns i RP Controller Expansion Module Energy Metering .

Specifikationer

Outputs
4, Relay 1 to Relay 4
Output terminals
N, PE, and L
Power distribution
100 to 277 VAC (same voltage as power supply)
  
Maximum 5 A load per output
  
Maximum 10 A total load for the 4 outputs
  
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
  • RP Controller Expansion Modules
  • Light Modules
  • RP-C-EXT-REL-4
  • RP Controller Expansion Module Pluggable Connectors
  • RP Controller Expansion Module Energy Metering
  • Configuring Relays in the RP Controller Expansion Relay Module
  • RP Controller Expansion Relay Module Relay Properties - Basic Tab