Poradnik

Poradnik


Produkty: AS-B, AS-P, RP-C, Adapter SmartX Zigbee
Funkcje: Sprzęt
Wersja produktu: 3.3, 2022, 2023, 2024, 7.0
2022-06-10

Installing Wireless Adapter - Advanced in a Dropped Ceiling

You install Wireless Adapter - Advanced in a dropped ceiling and connect the adapter to an RP-C controller, AS-P server, or AS-B server to add Zigbee wireless connectivity to the controller or server.

Pokaż więcej
action_close

Wireless Adapter - Advanced is a USB-based wireless adapter that enables Zigbee TM wireless connectivity with an RP controller, AS-P server, or AS-B server, extending the controller's or server's point count and bringing flexibility in retrofit applications.

The adapter is a Zigbee Certified Product when it is used with RP controllers and automation servers. The adapter is compliant with Zigbee 3.0.

An automation server equipped with the adapter can communicate over the Zigbee wireless protocol with up to 164 wireless devices, depending on the type of Zigbee device and the radio bandwidth usage of the device. An RP controller equipped with the adapter can communicate with up to 30 wireless devices.

Więcej informacji zawiera Supported Wireless Devices .

The adapter works seamlessly within EcoStruxure Building Management systems so that Zigbee objects become easily available to the user.

The adapter’s compact design allows it to plug in to RP controllers or automation servers in tight spaces and the optional mounting cradle, wall plate, and USB cable extension allow for the choice of a wall, ceiling, or exterior of the enclosure mount to maximize the transmission and reception of signals from distributed Zigbee devices.

 
action_zoom_plus_stroke  Adapter with mounting cradle and wall plate
Rysunek: Adapter with mounting cradle and wall plate

The adapter is plugged into the USB host port on the RP controller, AS-P server, or AS-B server. The adapter is powered by the RP controller or automation server, which also provides transient protection to the adapter.

 
action_zoom_plus_stroke  Adapter installed on an enclosure exterior and connected to the USB host port of an RP controller
Rysunek: Adapter installed on an enclosure exterior and connected to the USB host port of an RP controller

The adapter must be professionally installed to avoid harmful interference to radio communications and to maintain the regulatory compliance and approvals for the device. Więcej informacji zawiera Wireless Adapter - Advanced Regulatory Compliance and Approvals .

In WorkStation, the firmware of the adapter will be automatically updated when you update the RP controller or automation server to which it is connected.

Dane techniczne

Electrical
DC input supply voltage
5 VDC (USB) a
Maximum power consumption
0.3 W
Wireless connectivity
Communication protocol
Zigbee 3.0
Frequency band
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
Maximum output power
+10 dBm
Maximum communication distance
Line-of-sight: 50 m (164 ft)
Antenna
Integrated antenna
Maximum total number of hops allowed in the wireless network
5
Wireless device limits for an RP controller
Maximum total number of wireless devices connected to the wireless network
Up to 30 a
Maximum total number of SE8000 and VT8000 room controllers
4
Maximum total number of Zigbee end devices paired with an RP controller
20
Maximum total number of ASSA ABLOY VingCard electronic locks
1
Wireless device limits for an automation server
Maximum total number of wireless devices connected to the wireless network
Up to 164 a
Maximum total number of Zigbee routers and Zigbee end devices
64
Maximum total number of Zigbee Green Power devices
100
Maximum total number of Zigbee end devices paired with an automation server
20
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Humidity
Maximum 95 % RH non-condensing
Material
Plastic flame rating
UL94 HB
Plenum rating
UL 2043
Ingress protection rating
IP 20
Mechanical
Dimensions, adapter
See drawing below
 
action_zoom_plus_stroke
Dimensions, mounting cradle and wall plate
See drawing below
 
action_zoom_plus_stroke
Weight
Adapter: 7.57 g (0.267 oz)
  
Cradle and nut: 21.35 g (0.753 oz)
  
Cradle, nut, and wall plate: 33.40 g (1.178 oz)
Installation
Connection to USB host port on RP controller or automation server
  
Indoor use only
Installation options
Enclosure exterior
  
Drop ceiling with mounting cradle (optional)
  
Wall with wall plate (optional)
Maximum USB 2.0 cable length
3 m (10 ft)
Hardware
CPU type
ARM Cortex-M4 with Floating Point Unit (FPU)
Frequency
38.4 MHz
SRAM (embedded)
64 KB
Flash memory (embedded)
512 KB
Connectors
USB 2.0, type-A connector

To install Wireless Adapter - Advanced in a dropped ceiling
  1. Refer to the dimensional drawings before installing the adapter.

     
    action_zoom_plus_stroke
  2. Ensure that you have the proper mounting hardware.

  3. Find a suitable location on the ceiling for mounting the adapter.

  4. Mark the place where the hole should be in the ceiling tile.

     
    action_zoom_plus_stroke
  5. Remove the ceiling tile.

  6. Create a 32 mm (1.250 inches) diameter mounting hole in the ceiling tile.

     
    action_zoom_plus_stroke
    Uwaga

    Use a hole saw or ceiling tile hole cutter to create the hole in the ceiling tile.

  7. Mount the cradle and fasten it using the thumb nut.

     
    action_zoom_plus_stroke
  8. Install the adapter in the cradle.

     
    action_zoom_plus_stroke
  9. Connect the USB extension cable to the adapter.

     
    action_zoom_plus_stroke
    Uwaga

    Use the following USB cable ordered from Schneider Electric:

    • Plenum rated USB extension cable of length 3 m (10 ft) (part number SXWUSBCBL10002)

  10. Connect the USB extension cable to the USB host port on the RP-C controller or automation server.

     
    action_zoom_plus_stroke
  11. Reinstall the ceiling tile.

You can now use the adapter.

  • Wireless Adapter - Advanced
  • Installing Wireless Adapter - Advanced on an Enclosure Exterior
  • Installing Wireless Adapter - Advanced on a Wall