The CRS-HH-REL-10 relay module connects to the RP-C room controllers and enables the control of lights and blinds.
It is part of the EcoStruxure™ Connected Room Solutions for Hotels and can be combined with other modules from this product range.
It is designed for hotel guest room applications.
The CRS-HH-REL-10 relay module is an RP controller expansion module. This means that it can also be combined with modules from the Connected Room Solutions for Buildings.
The CRS-HH-REL-10 relay module has 10 relay outputs, which are designed for control of lights and blinds.
Para mais informações, consulte Relay Outputs on CRS-HH-REL-10 .
The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.
The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.
Para mais informações, consulte RP Controller Expansion Module Digital Inputs .
RP controller expansion modules and multi-sensor have two types of memory, flash memory and RAM.
Para mais informações, consulte RP Controller Expansion Module and Multi-sensor Memory .
The RP controller expansion modules and multi-sensors have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules and multi-sensors on the room bus through a daisy-chain configuration.
Para mais informações, consulte RP-C Room Bus .
Each RP controller expansion module and multi-sensor has a rotary switch, which is used to give the device a unique address on the room bus.
Para mais informações, consulte RP-C Room Bus .
The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.
Para mais informações, consulte RP-C Room Bus .
The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:
The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.
The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.
Para mais informações, consulte RP Controller Expansion Module Pluggable Connectors .
There is one or more LEDs on the front panel of the RP controller expansion modules.
Para mais informações, consulte RP Controller Expansion Module LEDs .
All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.
Para mais informações, consulte RP Controller Expansion Module Set Button .
The RP controller expansion module can be installed on a DIN rail or flat surface.
Para mais informações, consulte RP Controller Expansion Module Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Para mais informações, consulte Wiring .
The RP controller expansion modules and multi-sensors support different modes that can be used for maintenance purposes.
Para mais informações, consulte RP Controller Expansion Module and Multi-sensor Maintenance Modes .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
Para mais informações, consulte BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion modules.
Para mais informações, consulte RP Controller Expansion Modules Regulatory Compliance and Approvals .
The CRS-HH-REL-10 relay module supports blind motors with an operating voltage of 120 or 240 VAC, 50/60 Hz.
Para mais informações, consulte Types of Blind Motors Supported by CRS-HH-REL-10 .
Electrical | |
DC input supply voltage
|
24 VDC
|
Powered by the RP-C through the room bus (RJ45)
|
|
Maximum power consumption
|
0.3 W
|
Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
Humidity
|
20 to 90 % RH non-condensing
|
Pollution degree
|
2
|
Material | |
Plastic flame rating
|
UL94 V-0
|
Ingress protection rating
|
IP 20
|
Mechanical | |
Dimensions
|
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
|
|
|
Weight
|
0.476 kg (1.050 lb)
|
Installation
|
DIN rail or flat surface
|
Terminal blocks
|
Relay outputs: 10 x 2-pin screw terminal block
|
Digital inputs: 2 x 9-pin screw terminal block
|
|
Communication ports | |
Room bus
|
RS-485
|
Dual RJ45 ports for daisy-chain configurations
|
|
Use a Cat 5 (or higher) cable
|
|
Maximum total length of the room bus: 72 m (236 ft)
|
|
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
Hardware | |
CPU type
|
ARM Cortex-M4 single-core
|
Frequency
|
80 MHz
|
SRAM (embedded)
|
320 KB
|
Flash memory (embedded)
|
512 KB
|
NOR flash memory
|
16 MB
|
Status indicator
|
LED (green and red) that shows the status of the device
|
Address switch
|
Rotary switch 0 to 9
|
Set button
|
Push-button switch
|
Relay outputs | |
Outputs
|
10, DO1 to DO10
|
Relay output rating
|
24 to 277 VAC, 50/60 Hz, 30 VDC:
|
Resistive and incandescent: 10 A
|
|
Standard magnetic ballast: 5 A
|
|
LED driver: 5 A
|
|
1/2 HP, 240 VAC, 50/60 Hz
|
|
1/4 HP, 120 VAC, 50/60 Hz
|
|
Maximum load current
|
Maximum 50 A total load for the 10 outputs
|
Maximum inrush current
|
Maximum 165 A inrush current (<20 ms) per output
|
Maximum 800 A inrush current (<200 µs) per output
|
|
Digital inputs | |
Inputs
|
12, DI1 to DI12
|
Range
|
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)
|
The CRS-HH-REL-10 internal configuration with regards to the signal ground is shown in the following figure.