Commission

arrow1_rotation Introduction arrow1_rotation Features arrow1_rotation Connection options arrow1_rotation Specifications
 
action_zoom_plus_stroke Commission mobile application
Figure: Commission mobile application

Introduction

The EcoStruxure Building Commission mobile application is designed to help airflow balancers, electricians, and technicians carefully and quickly pre-commission and commission SpaceLogic BACnet/IP devices, RP controller expansion modules, and EasyLogic BACnet MS/TP devices. The Commission mobile application allows light weight devices such as smartphones and tablets to be used to commission and test controllers without the need for EcoStruxure BMS servers to be connected, minimizing on-site time and reducing costs. Various checkout reports are available to confirm that the work has been done.

The Commission mobile application can connect to a single BACnet/IP controller via Bluetooth or to a network of BACnet/IP controllers on the local network, using Wi-Fi or an Ethernet cable.

The Commission mobile application does not require a license for activation and is available at no cost to the user. It is designed for use with Android, iOS (Apple), and Microsoft Windows 11 devices, and is available for download from Google Play, Apple App Store, and Microsoft Store.

After installing the Commission mobile application, users launch the mobile application by logging in with their Schneider Electric extranet credentials while connected to the Internet. Once logged in, the mobile application can be used without an Internet connection. In this state, the user remains logged in until an Internet connection is restored. This allows the device running the mobile application to be used at sites without Internet connectivity.

Features

The Commission mobile application provides simple workflows to perform the following for SpaceLogic BACnet/IP devices, RP controller expansion modules, and EasyLogic BACnet MS/TP devices:

  • Use of BACnet to discover and connect

  • Configure network communication settings

  • View status information and diagnostic files

  • Download application image files

  • Download firmware and update control via IP connection (Wi-Fi or wired)

  • Perform a restart

  • Perform checkout of inputs and outputs of a controller or an RP controller expansion module*

  • Perform calibration and testing of devices such as lights and blinds*

  • Perform commissioning of Modbus and Zigbee devices*

  • Quickly configure application setpoints and values with Configuration Menus

  • Air balance terminal boxes controlled by MP-V and RP-V controllers

  • Use the mobile camera device to capture controller specific data from the Data Matrix symbol on the product label and High Security Zigbee QR Codes containing IEEE Address and Install codes.

  • Provide feedback direct from the mobile application

* For applications with SpaceLogic BACnet/IP devices.

Controller list creator

 
action_zoom_plus_stroke
The Commission mobile application allows the user to create a list of BACnet/IP and BACnet MS/TP devices by scanning the Data Matrix symbol on the tear-off product info label on the devices, using the camera on the mobile device. The resulting list shows the model name and unique serial number of each controller. Additionally, unique details entered by the user about the controller's location and associated equipment, as well as any comments, are recorded. This list can be exported as a CSV file for use by other tools.
Device settings

 
action_zoom_plus_stroke
The Commission mobile application allows either the easy discovery of BACnet/IP controllers over an IP network or over a Bluetooth connection. Filters can be applied to the list to display a desired subset of these devices. The discovery view allows the user to easily identify and select a controller to view or make changes to the configuration, including the controller's location, BACnet and network settings, and to set the controller's parent server.
Download image and firmware

 
action_zoom_plus_stroke
With the Commission mobile application, the user can download, to a BACnet/IP or BACnet MS/TP device, an application image file that is file from WorkStation or downloaded from the EcoStruxure BMS Applications site. This feature is especially useful in cases where control applications cannot be downloaded normally, through WorkStation, because the system infrastructure is not yet completed or is otherwise not serviceable.

The user can download firmware to multiple BACnet/IP devices over an IP connection. This is useful when an application image is associated with a newer firmware version than what is currently loaded into the controller.

Flow balance

 
action_zoom_plus_stroke
Using the Commission mobile application, the user has use of an intuitive workflow that allows airflow calibration to be performed without the need for programming. The Commission mobile application automatically guides the user through a five-step flow balance process. Manual Checkout commands provide the flexibility to efficiently verify and command the air flow values. Following flow balancing, a report can be generated in HTML format, for one or more VAV units. The balancing parameters generated during flow balance are stored in the parent server, facilitating controller replacement when necessary. In addition, the Commission mobile application creates a log file in the MP-V or RP-V controller in which the steps performed during flow balancing are automatically saved. This log file can be viewed in WorkStation.
I/O checkout

 
action_zoom_plus_stroke
After wiring the physical inputs and outputs of the BACnet/IP or BACnet MS/TP devices, the user can perform I/O checkout to verify that the wiring was done correctly and that the physical inputs and outputs are working properly.

During I/O checkout, a report is generated in the device. This report identifies connections that are not established, so appropriate actions can be taken. When checkout is complete, you can view the report in WorkStation. This report can serve as a record of checkout progress during the installation of a project.

With SpaceLogic RP controllers, the user can perform I/O checkout on the RP controller room bus to verify proper communication over the room bus between the RP controller and the associated RP controller expansion modules. Module type mismatches or address mismatches can then be resolved. After wiring the physical inputs and outputs of the RP controller expansion modules, the user can perform the following tasks on the different modules:

  • DALI light modules: discover, wink, and associate DALI lights and input devices to logical software points, and test individual lights

  • 0-10V light modules: test individual lights

  • Blind modules: calibrate and test blinds

  • Relay module: test outputs

The user can commission Modbus devices and determine their online or offline status.

In applications with SpaceLogic RP controllers, the user can commission Zigbee devices by joining them to a standard security, high security or VingCard network, associating them with controller objects, and determining their online or offline status.

Browse objects

 
action_zoom_plus_stroke
The Commission mobile application can be used to view all the objects within a selected BACnet/IP controller application, allowing the user to view and edit these objects as needed.
Configuration menu

 
action_zoom_plus_stroke
The Commission mobile application enables the user to commission a controller and quickly configure its setpoints and values using the Configuration Menu feature. Multiple configuration menus can be created in WorkStation and each configuration menu contains a set of preconfigured properties. Configuration menus are saved as part of an application image that the user can download to the controller.
Diagnostic files

 
action_zoom_plus_stroke
The Commission mobile application allows the user to view and export the BACnet/IP and BACnet MS/TP device report, error log, or crash report, for use during troubleshooting or when communicating with product support.
Device restart

 
action_zoom_plus_stroke
Using the Device Restart function of the Commission mobile application, the user can perform a warm or cold restart of the BACnet/IP device.

Connection options

You can choose from several different options to connect the Commission mobile application to one or more BACnet/IP devices.

Bluetooth connection by adapter

With SpaceLogic Bluetooth Adapter, the Commission mobile application can connect to a BACnet/IP device through Bluetooth. You plug the adapter into the side of a SpaceLogic Sensor connected to the controller's sensor bus. For more information, see the SpaceLogic Sensors - SXWS Sensors for MP and RP IP Controllers - Specification Sheet.

 
action_zoom_plus_stroke SpaceLogic Bluetooth Adapter
Figure: SpaceLogic Bluetooth Adapter
Bluetooth connection directly to RP controller

With the Commission mobile application, you can connect directly to an RP controller through the controller's onboard Bluetooth connectivity. By default, the controller advertises its name, model name and unique serial number. For more information, see the RP-C and RP-V Specification Sheets.

Wi-Fi connection

The Commission mobile application can also connect to a single BACnet/IP device or to a network of BACnet/IP devices on the local network, using a Wi-Fi router or a wireless access point.

Wired Ethernet Connection

A mobile device running the Commission mobile application can be connected to a single BACnet/IP device or to a network of BACnet/IP devices on the local network using an Ethernet cable.

Specifications

Commission mobile application
Hardware and software requirements
Hardware
Android phones and tablets
  
Apple iPhones and iPads
  
PCs, laptops, and tablets running Microsoft Windows 11
Operating systems
Android 8.1 (Oreo) and later
  
Apple iOS 11.2 and later
  
Microsoft Windows 11
Compatibility
MP controller communication
EcoStruxure Building Operation
version 2.0.1 and later
RP-C communication
EcoStruxure Building Operation
version 3.0.1 and later
Configuration Menu support
EcoStruxure Building Operation
version 3.0.1 and later
Bluetooth connectivity
EcoStruxure Building Operation
version 3.0.2 and later
RP controller expansion module support
EcoStruxure Building Operation
version 3.1.1 and later
RP-V communication
EcoStruxure Building Operation
version 4.0.1 and later
MS/TP communication via Bluetooth connectivity
EcoStruxure Building Operation
version 4.0.1 and later
EasyLogic RP-V communication
EcoStruxure Building Operation
version 4.0.3 and later
EasyLogic RP-C, MP-C, and RP-IO communication
EcoStruxure Building Operation
version 5.0.1 and later
IP connection security
Having a secured IP connection to the site is the responsibility of the user.
SpaceLogic Bluetooth Adapter
Electrical
DC input power consumption
Maximum 0.25 W
DC input supply voltage
5.0 to 5.5 VDC (powered by the SpaceLogic Sensor)
Communications
Wireless communications
Bluetooth ® 4.2 Low Energy compliant
  
Bluetooth ® 5 Advertising
  
Frequency: 2.4 GHz
  
Line-of-sight range: max. 50 m (164 ft)
SpaceLogic communications
RS-485, proprietary Sensor Bus protocol
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Dimensions
70 W x 32 H x 12 D mm (2.8 W x 1.3 H x 0.5 D in.)
Weight
0.02 kg (0.05 lb) with lanyard
Agency compliances
EMC
EN 301 489-1 V2.2.0; EN 301 489-17 V3.2.0; EN 55032:2012; EN 55035:2017; FCC Part 15, Subparts B and C, Class B; ICES-003, Class B
Radio
EN 300 328 V2.2.0
Safety standards
BS/EN 62368-1:2014; BS/EN 62311:2008; BS/EN 62479:2010
FCC ID
QOQ11
ISED certification number
IC: 5123A-11
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
38.4 MHz
SRAM (embedded)
32 KB
Flash memory (embedded)
256 KB
Flash memory (serial)
1 MB
Status indicator
LED (blue)
Button
Momentary push-button switch
Compatibility
Commission mobile application
EcoStruxure Building Operation
version 3.1.1 and later
BACnet/IP Controller communication
EcoStruxure Building Operation
version 3.0.2 and later
Part numbers
SpaceLogic Bluetooth Adapter
SXWBTAECXX10001
  • SpaceLogic RP-C Advanced
  • SpaceLogic RP-C Pro
  • SpaceLogic RP-C Pro Plus
  • SpaceLogic RP-V Advanced
  • SpaceLogic MP-C Pro
  • SpaceLogic MP-V
  • SpaceLogic IP-IO