The RP-C-EXT-IS-BLE Insight-Sensor connects to the RP controllers and is used for people counting, infrared motion detection, and luminosity and sound pressure level measurements, and supports Bluetooth Low Energy based applications such as beaconing and remote control communication.
The Insight-Sensor provides real-time occupant information that enables immediate control of HVAC for optimized energy consumption and indoor environment, for example, by adapting the fan speed to occupancy level or turning off the lights when unoccupied.
The Insight-Sensor is connected to the RP controller using an RJ45 type quick connector.
The Insight-Sensor's three flexible mounting brackets (springs) enable quick and easy installation on a suspended ceiling tile. The Insight-Sensor also comes with a mounting ring, which allows the device to be installed in open ceiling applications.
The Insight-Sensor is a Bluetooth Low Energy (BLE) device. The Insight-Sensor support for Bluetooth beacon enables nearby mobile devices with a specific app installed to interact when in close proximity to the broadcasting Insight-Sensor. The Bluetooth beacon can be used for services such as indoor positioning of the mobile device. The service and mobile app need to be provided by a third party. The Bluetooth connection can also be used for communication with the RP-C-RC-BLE remote control, which makes it possible to control the lighting, blinds, and air conditioning in a zone of an office building.
The Insight-Sensor is part of the RP controller expansion modules product range. The Insight-Sensor can be combined with the RP controller expansion modules for lighting and blind control to provide a connected room solution.
The Insight-Sensor supports people counting through a thermal image sensor.
Para obtener más información, consulte People Counting .
The RP controller expansion sensor modules support motion detection through a passive infrared sensor.
Para obtener más información, consulte Motion Detection .
The RP controller expansion sensor modules support luminosity measurements through an ambient light sensor.
Para obtener más información, consulte Luminosity Measurement .
The Insight-Sensor supports sound pressure level measurements through a microelectromechanical system (MEMS) acoustic sensor.
Para obtener más información, consulte Sound Pressure Level Measurement .
The Insight-Sensor supports temperature and humidity measurements through a single integrated circuit, consisting of a bandgap temperature sensor and a capacitive humidity sensor.
Para obtener más información, consulte Temperature and Humidity Measurement .
RP controller expansion modules have two types of memory, flash memory and RAM.
Para obtener más información, consulte RP Controller Expansion Module Memory .
The RP controller expansion sensor modules, such as the Multi-sensor and Insight-Sensor, are Bluetooth Low Energy (BLE) devices, which support applications such as beaconing and remote control communication.
Para obtener más información, consulte RP Controller Expansion Sensor Module Wireless Connectivity .
The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.
Para obtener más información, consulte RP-C Room Bus .
Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.
Para obtener más información, consulte RP-C Room Bus .
The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.
Para obtener más información, consulte RP-C Room Bus .
There is one LED on the RP controller expansion sensor modules. The LED is integrated with the Set button.
Para obtener más información, consulte RP Controller Expansion Sensor Module LED .
The RP controller expansion sensor modules have a Set button on the front. The Set button is reserved for future use.
Para obtener más información, consulte RP Controller Expansion Sensor Module Set Button .
The RP controller expansion Insight-Sensor can be installed on a dropped (suspended) ceiling, a drywall ceiling, or a junction (gang) box.
Para obtener más información, consulte RP Controller Expansion Insight-Sensor Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
Para obtener más información, consulte Wiring .
The RP controller expansion modules support different modes that can be used for maintenance purposes.
Para obtener más información, consulte RP Controller Expansion Module Maintenance Modes .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
Para obtener más información, consulte BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion sensor modules of the Insight-Sensor model.
Para obtener más información, consulte RP Controller Expansion Insight-Sensor Regulatory Compliance and Approvals .
Electrical | |||||||||||||
DC input supply voltage
|
24 VDC
|
||||||||||||
Powered by the RP controller through the room bus (RJ45)
|
|||||||||||||
Maximum power consumption
|
0.35 W
|
||||||||||||
Environment | |||||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
||||||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
||||||||||||
Humidity
|
20 to 90 % RH non-condensing
|
||||||||||||
Material | |||||||||||||
Plastic flame rating
|
UL94 V-0
|
||||||||||||
Ingress protection rating
|
IP 20
|
||||||||||||
Cover color
|
Signal white (RAL9003)
|
||||||||||||
Mechanical | |||||||||||||
|
|||||||||||||
Overall external diameter
|
97.5 mm (3.84 in.)
|
||||||||||||
Diameter of mounting clearance hole
|
75.0 to 76.0 mm (2.95 to 3.00 in.)
|
||||||||||||
External washer thickness
|
12 mm (0.47 in.)
|
||||||||||||
Overall external thickness
|
19 mm (0.75 in.)
|
||||||||||||
Internal thickness
|
20 mm (0.79 in.)
|
||||||||||||
Overall internal depth
|
28 mm (1.10 in.)
|
||||||||||||
Weight, Insight-Sensor with mounting springs (3x)
|
0.088 kg (0.194 lb)
|
||||||||||||
Weight, Insight-Sensor with mounting ring
|
0.098 kg (0.216 lb)
|
||||||||||||
Installation
|
Plastic unit to be fitted flush in a suspended ceiling tile with a thickness of up to 45 mm (1.77 in.)
|
||||||||||||
The mounting springs enable quick and easy installation in a suspended celing. The mounting ring allows the device to be installed in a ceiling with drywall anchors or to a 102 mm (4 in.) junction box. | |||||||||||||
Communication ports | |||||||||||||
Room bus
|
RS-485
|
||||||||||||
Dual RJ45 ports for daisy-chain configurations
|
|||||||||||||
Use a Cat 5 (or higher) cable
|
|||||||||||||
Maximum total length of the room bus: 72 m (236 ft)
|
|||||||||||||
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
||||||||||||
Wireless connectivity | |||||||||||||
Bluetooth Low Energy | |||||||||||||
Communication protocol
|
Bluetooth
®
5.1 Low Energy compliant
|
||||||||||||
Frequency
|
2.402 to 2.480 GHz
|
||||||||||||
Maximum communication distance
|
Line-of-sight: 50 m (164 ft)
|
||||||||||||
Maximum output power
|
3 dBm
|
||||||||||||
Antenna
|
Integrated antenna
|
||||||||||||
Beacon protocol
|
iBeacon
|
||||||||||||
Hardware | |||||||||||||
Main microcontroller | |||||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||||||||
Frequency
|
38.4 MHz
|
||||||||||||
SRAM (embedded)
|
256 KB
|
||||||||||||
Flash memory (embedded)
|
1024 KB
|
||||||||||||
Flash memory (serial)
|
16 MB
|
||||||||||||
Sub microcontroller | |||||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||||||||
Frequency
|
80 MHz
|
||||||||||||
SRAM (embedded)
|
320 KB
|
||||||||||||
Flash memory (embedded)
|
1 MB
|
||||||||||||
Flash memory (serial)
|
2 MB
|
||||||||||||
Additional hardware | |||||||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
||||||||||||
Address switch
|
Rotary switch 0 to 9
|
||||||||||||
Set button
|
Push-button switch
|
||||||||||||
People counting | |||||||||||||
Sensor
|
Longwave infrared (LWIR) microbolometer
|
||||||||||||
Detection range
|
See image and table below.
|
||||||||||||
|
|||||||||||||
|
|||||||||||||
a) At the level of 1 m (3.3 ft) above the floor. | |||||||||||||
Average counting accuracy
a
|
Up to 90%
|
||||||||||||
a) Correct installation and configuration required. | |||||||||||||
Motion detection | |||||||||||||
Sensor
|
Quad-type passive infrared (PIR) sensor with Fresnel lens
|
||||||||||||
Detection range
|
See image and table below.
|
||||||||||||
|
|||||||||||||
|
|||||||||||||
Luminosity measurements | |||||||||||||
Sensor
|
Ambient Light Sensor (ALS)
|
||||||||||||
|
|||||||||||||
Spectral response
|
Human eye
|
||||||||||||
Luminosity range
|
0 to 10,000 lux
|
||||||||||||
Field of view
|
30 degrees from vertical
|
||||||||||||
Sound pressure level measurements | |||||||||||||
Sensor
|
Microelectromechanical system (MEMS) acoustic sensor
|
||||||||||||
Dynamic pressure
|
35 to 79 dBA
|
||||||||||||
Accuracy
|
+/- 3 dBA
|
||||||||||||
Bandwidth
|
10 Hz to 8 kHz
|
||||||||||||
Temperature measurements | |||||||||||||
Range
|
0 to 50 °C (32 to 122 °F)
|
||||||||||||
Accuracy
|
+/-1 °C (+/-1.8 °F)
|
||||||||||||
Humidity measurements | |||||||||||||
Range
|
0 to 100% RH
|
||||||||||||
Accuracy
|
+/-4% (within the range of 20 to 80% RH)
|
||||||||||||
+/-6% (outside the range of 20 to 80% RH)
|
The RP-C-EXT-IS-BLE internal configuration with regards to the signal ground is shown in the following figure.