earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : RP-C
Fonctionnalités : Matériel
Version produit : 2022, 2023, 2024, 7.0
30/03/2023

Differences Between RP-C Hardware Versions

There are a number of differences in hardware between different hardware versions of the RP-C-12A-F-24V, RP-C-12B-F-24V, RP-C-12C-F-24V, and RP-C-16A-F-230V controller models.

Table : Differences Between RP-C Hardware Versions

Hardware Feature

SpaceLogic RP-C

Part Number a : SXWRCF12A10002, SXWRCF12B10002, SXWRCF12C10002, and SXWRCF16A10003

Hardware Version a : 10 and Later

SmartX IP Controller – RP-C

Part Number a : SXWRCF12A10001, SXWRCF12B10001, SXWRCF12C10001, and SXWRCF16A10002

Hardware Version a : 9 and Earlier

DC input, operating voltage range (RP-C-12A-F-24V, RP-C-12B-F-24V, and RP-C-12C-F-24V models only)

23.5 to 33 VDC b

23 to 33 VDC

Screw terminal number 3 (RP-C-16A-F-230V model only)

Protective earth ground

 
action_zoom_plus_stroke

Screw terminal number 3 must be connected to protective earth ground (PE) for safety reasons. Pour plus d'informations, voir Grounding and Power for Systems with RP-C 230 V Controller Models .

Not connected internally

 
action_zoom_plus_stroke

RS-485 Com A port c , rating

24 VDC, 3 W

24 VDC, 2 W

RS-485 Com A and B ports c , BACnet MS/TP support

yes d

no e

Universal I/O (Ub), voltage output rating f

Range: 0 to 10 VDC

Minimum load resistance: 2.4 kohm

Source current: +4.2 mA

Sink current:

  • -1 mA (0 to 0.4 VDC)

  • -4.2 mA (0.4 to 10 VDC)

Range: 0 to 10 VDC

Minimum load resistance: 5 kohm

Source current: +2 mA

Sink current:

  • -1 mA (0 to 10 VDC)

Universal I/O (Ub), voltage input impedance

1 Mohm

100 kohm

NOR flash memory

48 MB

32 MB

  1. The part number and hardware version are shown on the label on the side of the RP-C-12A-F-24V, RP-C-12B-F-24V, RP-C-12C-F-24V, and RP-C-16A-F-230V controllers models. If the side of the device is not accessible, the text on the front can be used to identify the hardware version. For example, “SpaceLogic RP-C” is displayed on devices of hardware version 10 and later, while “SmartX IP Controller” is printed on devices of hardware version 9 and earlier.
  2. 23.5 VDC is required to obtain sufficient output voltage on the RS-485 Com A and Com B ports. Apart from that, the RP-C still works with 23 VDC supply.
  3. In previous hardware versions, the RS-485 Com A and Com B port are labelled “Sensor Bus” and “Room Bus” respectively.
  4. The RS-485 Com A and B ports on RP-C controllers (part numbers SXWRCF12A10002, SXWRCF12B10002, SXWRCF12C10002, and SXWRCF16A10003) of hardware version 10 and later are prepared for BACnet MS/TP (RS-485) network communication through modified pin configuration. An RJ45 to screw terminal block adapter is required to connect the RP-C controller to the BACnet MS/TP network for communication with the AS-P or AS-B server. The adapter can be ordered from Schneider Electric. In addition, a Cat 5 (or higher) UTP cable with RJ45 connectors is required to connect the adapter. The recommended maximum cable length is 0.3 m (12 inches). The cable should be rated for the target environment. The cable is not included with the adapter but needs to be purchased separately.
  5. The RS-485 Com A and B ports on RP-C controllers (part numbers SXWRCF12A10001, SXWRCF12B10001, SXWRCF12C10001, and SXWRCF16A10002) of hardware version 9 and earlier does not support BACnet MS/TP (RS-485) network communication.
  6. The modified rating does not reflect any changes in the hardware design.
  • RP-C Controllers
  • RP-C Models
  • RP-C-16A-F-230V Screw Terminals
  • Universal Inputs/Outputs
  • Communication Ports on RP-C Models with “-F” in the Product Name
  • RP-C Sensor Bus
  • RJ45 Pinout for the RS-485 Port(s) of the RP-C Controllers
  • Memory in RP and MP Controllers and I/O Modules