Concept

Concept


Products: RP-V
Functionalities: Hardware
Product version: 2023, 2024
5/16/2024

RP-V Models

The RP-V controller is available in two models that support both BACnet/IP and MS/TP communication. These two models offer two different combinations (sets) of the number of I/O points and types of I/O points. The RP-V controller also comes in a model that only supports BACnet MS/TP communication.

Table: RP-V Models

Range

Model

BACnet

I/O Set

I/O Points

SpaceLogic RP-V Advanced

RP-V-4A

IP or MS/TP a

4A

4

SpaceLogic RP-V Advanced

RP-V-5A

IP or MS/TP a

5A

5

EasyLogic RP-V

RP-V-5C-M

MS/TP

5C

5

  1. Adapter required: Isolated RS-485 Adapter (SXWISORS48510001), Non-isolated RS-485 Adapter (SXWNISORS48510001), or RS-485 Power Adapter (SXWNISORS485P10001).

For more information, see RP-V Onboard I/O .

The RP-V controllers have the same compact design and approximately the same dimensions as the MP-V controllers and a majority of the Schneider Electric VAV controller models from Andover Continuum, TAC Vista, and TAC I/A Series product lines. You can use the RP-V controllers for both cooling and heating applications.

The EasyLogic RP-V model differs significantly from the SpaceLogic RP-V models not only in terms of the supported BACnet communication protocol(s), but also with regards to the set of communication ports and several other features.

Note:

The EasyLogic models have an “-M” in the product name.

Table: Differences Between SpaceLogic RP-V and EasyLogic RP-V Models

Feature

RP-V-4A, RP-V-5A

RP-V-5C-M

Built-in wireless connectivity

yes

no a

Ethernet ports

2

0

USB ports

1 b

0

RS-485 ports with RJ45 interface

2 (Com A, Com B) c

1 (Com A) d

RS-485 ports supporting Isolated RS-485 Adapter e

Com B

-

RS-485 ports supporting Non-isolated RS-485 Adapter or RS-485 Power Adapter f

Com A, Com B

Com A

RS-485 port with screw terminals

0

1 g

I/O and power input terminals/connectors

Fixed screw terminals

Fixed screw terminals

MS/TP address configuration

Software

DIP switch

Room bus support

yes

no

Sensor bus support

yes

yes h

Modbus support

yes i

yes h j

RTD sensor support

yes

no

LED(s)

1 k

1 k

Real-time clock

yes

no

Input power

24 VAC

24 VAC

Power input type

Isolated

Isolated

CPU type

Single-core

Single-core

Memory (RAM / NOR flash / FRAM)

6 MB / 48 MB / 128 kB

6 MB / 32 MB / 128 kB l

  1. The SpaceLogic Bluetooth Adapter (SXWBTAECXX10001) can be used to add wireless connnectivity to the controller. The adapter is connected to a SpaceLogic Sensor on the Sensor Bus.
  2. USB Host port.
  3. Load: max. 3 W per port, max. 4 W total load.
  4. Load: max. 3 W.
  5. Isolated RS-485 Adapter (SXWISORS48510001) can be used for converting the RS-485 port with RJ45 interface to screw terminals.
  6. Non-isolated RS-485 Adapter (SXWNISORS48510001) and RS-485 Power Adapter (SXWNISORS485P10001) can be used for converting the RS-485 port with RJ45 interface to screw terminals. RS-485 Power Adapter (SXWNISORS485P10001) can also be used for power injecton on Room Bus or Sensor Bus.
  7. Dedicated for BACnet MS/TP bus. Removable 3-pole screw terminal block.
  8. The RS-485 Com A port can be configured for either Sensor Bus or Modbus.
  9. Either the RS-485 Com A port (Sensor Bus) or RS-485 Com B port (Room Bus) can be reconfigured for Modbus.
  10. The KNX Modbus Gateway (RP-C-EXT-KNX) is not supported.
  11. Status LED.
  12. RP-V-5C-M with hardware version earlier than 05 has a FRAM memory with a size of 8 kB. For these hardware versions, the use of Script programs is recommended to save FRAM memory space.
  • Hardware Overview
  • RP-V Controllers
  • RP-V Onboard I/O