Concept

Concept


Produits : RP-V
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
16/05/2024

RP-V Models

The RP-V controller is available in two models that support both BACnet/IP and MS/TP communication. These two models offer two different combinations (sets) of the number of I/O points and types of I/O points. The RP-V controller also comes in a model that only supports BACnet MS/TP communication.

Table : RP-V Models

Range

Model

BACnet

I/O Set

I/O Points

SpaceLogic RP-V Advanced

RP-V-4A

IP or MS/TP a

4A

4

SpaceLogic RP-V Advanced

RP-V-5A

IP or MS/TP a

5A

5

EasyLogic RP-V

RP-V-5C-M

MS/TP

5C

5

  1. Adapter required: Isolated RS-485 Adapter (SXWISORS48510001), Non-isolated RS-485 Adapter (SXWNISORS48510001), or RS-485 Power Adapter (SXWNISORS485P10001).

Pour plus d'informations, voir RP-V Onboard I/O .

The RP-V controllers have the same compact design and approximately the same dimensions as the MP-V controllers and a majority of the Schneider Electric VAV controller models from Andover Continuum, TAC Vista, and TAC I/A Series product lines. You can use the RP-V controllers for both cooling and heating applications.

The EasyLogic RP-V model differs significantly from the SpaceLogic RP-V models not only in terms of the supported BACnet communication protocol(s), but also with regards to the set of communication ports and several other features.

Déclaration

The EasyLogic models have an “-M” in the product name.

Table : Differences Between SpaceLogic RP-V and EasyLogic RP-V Models

Feature

RP-V-4A, RP-V-5A

RP-V-5C-M

Built-in wireless connectivity

yes

no a

Ethernet ports

2

0

USB ports

1 b

0

RS-485 ports with RJ45 interface

2 (Com A, Com B) c

1 (Com A) d

RS-485 ports supporting Isolated RS-485 Adapter e

Com B

-

RS-485 ports supporting Non-isolated RS-485 Adapter or RS-485 Power Adapter f

Com A, Com B

Com A

RS-485 port with screw terminals

0

1 g

I/O and power input terminals/connectors

Fixed screw terminals

Fixed screw terminals

MS/TP address configuration

Software

DIP switch

Room bus support

yes

no

Sensor bus support

yes

yes h

Modbus support

yes i

yes h j

RTD sensor support

yes

no

LED(s)

1 k

1 k

Real-time clock

yes

no

Input power

24 VAC

24 VAC

Power input type

Isolated

Isolated

CPU type

Single-core

Single-core

Memory (RAM / NOR flash / FRAM)

6 MB / 48 MB / 128 kB

6 MB / 32 MB / 128 kB l

  1. The SpaceLogic Bluetooth Adapter (SXWBTAECXX10001) can be used to add wireless connnectivity to the controller. The adapter is connected to a SpaceLogic Sensor on the Sensor Bus.
  2. USB Host port.
  3. Load: max. 3 W per port, max. 4 W total load.
  4. Load: max. 3 W.
  5. Isolated RS-485 Adapter (SXWISORS48510001) can be used for converting the RS-485 port with RJ45 interface to screw terminals.
  6. Non-isolated RS-485 Adapter (SXWNISORS48510001) and RS-485 Power Adapter (SXWNISORS485P10001) can be used for converting the RS-485 port with RJ45 interface to screw terminals. RS-485 Power Adapter (SXWNISORS485P10001) can also be used for power injecton on Room Bus or Sensor Bus.
  7. Dedicated for BACnet MS/TP bus. Removable 3-pole screw terminal block.
  8. The RS-485 Com A port can be configured for either Sensor Bus or Modbus.
  9. Either the RS-485 Com A port (Sensor Bus) or RS-485 Com B port (Room Bus) can be reconfigured for Modbus.
  10. The KNX Modbus Gateway (RP-C-EXT-KNX) is not supported.
  11. Status LED.
  12. RP-V-5C-M with hardware version earlier than 05 has a FRAM memory with a size of 8 kB. For these hardware versions, the use of Script programs is recommended to save FRAM memory space.
  • Hardware Overview
  • RP-V Controllers
  • RP-V Onboard I/O