Concept

Concept


Produits : RP-V
Fonctionnalités : Matériel
Version produit : 2022, 2023, 2024, 7.0
10/03/2025

Communication Ports on RP-V-4A and -5A

arrow1_rotationEthernet Ports arrow1_rotationUSB Port arrow1_rotationRS-485 Ports

The RP-V-4A and RP-V-5A models provide the following combination of communication ports:

  • Two Ethernet ports

  • One USB port

  • Two RS-485 ports (RJ45)

Ethernet Ports

The two Ethernet ports are labeled:

  • Ethernet 1

  • Ethernet 2

The two Ethernet ports are 10/100BASE-TX (RJ45) ports.

The Ethernet interface is IEEE 802.3 compliant.

When both Ethernet ports are enabled, they function as an onboard Ethernet switch. Disabling the second Ethernet port disables the switching function. The switching function enables flexible network topologies. Pour plus d'informations, voir BACnet/IP Controller Network Topologies . The second port also provides a connection point for a laptop running the Commission mobile application.

Pour plus d'informations, voir Communication Port Wiring .

USB Port

The USB port is labeled:

  • Host

The USB host port is a USB 2.0 type-A port, which is rated 2.5 W. The USB host port can be used for connection of Wireless Adapter - Advanced to add Zigbee TM wireless connectivity to the RP controller. The adapter can be used to extend the controller's point count and bring flexibility in retrofit applications. Pour plus d'informations, voir Wireless Adapter - Advanced .

Pour plus d'informations, voir Communication Port Wiring .

RS-485 Ports

The two RS-485 ports are labeled:

  • RS-485 Com A

  • RS-485 Com B

The RS-485 ports are rated for a maximum load of 3 W (24 VDC) per RS-485 port with a maximum total load of 4 W for the two RS-485 ports.

The two RS-485 ports are RJ45 ports. Pour plus d'informations, voir RJ45 Pinout for the RS-485 Port(s) of the RP-V Controllers .

Each port can be configured to use one of the following communication protocols for different types of networks:

  • Sensor bus

  • Room bus

  • Modbus

Déclaration

An RP controller can have only one of each network type.

The sensor bus is designed for communication with SpaceLogic Sensor devices. Pour plus d'informations, voir RP-V Sensor Bus .

The room bus is designed for communication with RP controller expansion modules for connected room solutions. Pour plus d'informations, voir RP-V Room Bus .

The Modbus (RTU) network can be used for communication with the KNX Modbus gateway (RP-C-EXT-KNX) and standard Modbus devices. Pour plus d'informations, voir RP-V Modbus .

One of the RS-485 ports can also be configured to support BACnet MS/TP network communication with the automation server. Pour plus d'informations, voir RP-V BACnet MS/TP Support . The other RS-485 port can then be configured to support either sensor bus, room bus, or Modbus network.

Pour plus d'informations, voir Allocating Flexible Ports .

Default configurations:

  • Sensor bus on the RS-485 Com A port

  • Room bus on the RS-485 Com B port

Pour plus d'informations, voir Communication Port Wiring .

  • Hardware Overview
  • RP-V Communication Ports
  • RP-V Controllers
  • BACnet/IP Controller Network Topologies
  • RP-V Sensor Bus
  • RP-V Room Bus
  • RP-V Modbus
  • RP-V BACnet MS/TP Support
  • Wireless Adapter - Advanced
  • KNX Modbus Gateway RP-C-EXT-KNX
  • RJ45 Pinout for the RS-485 Port(s) of the RP-V Controllers
  • Allocating Flexible Ports
  • Communication Port Wiring