earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Especificaciones

Especificaciones


Productos RP-C
Funcionalidades: Ingeniería, Hardware
Versión del producto: 2024
13/08/2024

SpaceLogic RP-C Pro

 
action_zoom_plus_stroke RP-C-16B-F-24V
Figura: RP-C-16B-F-24V

Introducción

SpaceLogic™ RP-C Pro is a high-power, fully programmable, IP based field controller that offers a multi-room connectivity hub for Connected Room Solutions.

The RP-C Pro controller has greater memory space for large room and luxury suite applications.

RP-C Pro comes either as a 24 VAC/DC or 230 VAC controller with 16 I/O points.

The controller is integrated into Connected Room Solutions and EcoStruxure Building Operation and is positioned for room control as well as well-being, comfort of occupants in an energy-efficient way.

The RP-C Pro controller can also be reconfigured through the EcoStruxure Building Operation software to support BACnet MS/TP, instead of BACnet/IP.

The controller can either be used as a standalone BACnet/IP field controller, BACnet/SC node, or as part of an EcoStruxure BMS with a SpaceLogic AS-P or AS-B server or an Enterprise Server as the parent server.

The controller features a wireless chip, which enables commissioning of the controller with the Commission mobile application and allows tenants to change the room comfort settings using their smartphones with the Engage mobile application.

Web services enable web access directly to the controller, making the controller an open IoT hub in the room or space area.

El RP-C Pro tiene las siguientes características:

  • Conectividad IP Ethernet, con puerto dual.

  • Nodo BACnet/SC

  • Gama completa de modelos de controladores

  • Una versatil combinación de puntos E/S

  • Cubiertas opcionales

  • Conexión inalámbrica

  • Supervisión avanzada

  • Dos puertos RS-485 configurables

  • Sensor bus para sensores SmartX Living

  • Room bus para la Connected Room Solutions

  • Subred Modbus RTU

  • Compatibilidad con KNX (se requiere pasarela KNX Modbus)

  • Compatible con BACnet MS/TP (requiere adaptador)

  • Conectar aplicaciones móviles para la configuración del confort en la sala

  • Aplicación móvil Commission para la puesta en marcha del controlador antes de que se instale el BMS

  • Soporte para el software de EcoStruxure Building Operation, que proporciona herramientas de ingeniería eficientes.

  • Servicios web a través de API RESTful

Conectividad IP, topologías de red flexibles y compatibilidad con aplicaciones BACnet/SC

The BACnet/IP controllers are based on open protocols that simplify interoperability, IP configuration, and device management, and can be enabled as BACnet/SC nodes for increased cybersecurity:

  • IP addressing

  • BACnet/IP or BACnet/SC communications

  • DHCP for easy network configuration

The BACnet/IP controllers have a dual-port Ethernet switch, which enables flexible network topologies:

  • Star

  • Daisy chain

  • Rapid Spanning Tree Protocol (RSTP) ring

In a star topology, the controller and the parent EcoStruxure BMS server are individually connected to an Ethernet switch. Daisy-chain multiple controllers together to reduce installation time and cost. When using a ring network topology, in the event of a broken IP network or a non-operational controller, RSTP will enable rapid identification of the location of the detected error while maintaining communication with the controllers on either side of the break.

Compatibilidad con BACnet/SC (Secure Connect)

The BACnet/IP controllers support BACnet/SC applications as a BACnet/SC node. This allows the controllers to be used in a BACnet/SC network, which allows secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

Modelos de controlador

La gama RP-C Pro incluye dos modelos diferentes, que ofrecen el mismo conjunto de puntos de E/S tipo, denominado 16B, pero con soporte para diferentes tensiones de alimentación. El modelo RP-C-16B-F-24V admite una alimentación de 24 VCA/CC, mientras que el modelo RP-C-16B-F-230V es un modelo de 230 VCA.

 
action_zoom_plus_stroke

Totalmente programable

Los modelos RP-C, totalmente programables, proporcionan flexibilidad gracias a la compatibilidad con las opciones de programación de scripts y bloques de funciones. El RP-C fomenta la eficiencia y la estandarización mediante el uso de aplicaciones estándar.

Modelos con una versátil combinación de puntos de E/S

Los modelos RP-C-16B-F-24V y RP-C-16B-F-230V proporcionan 16 puntos de E/S, que constan de cuatro conjuntos diferentes de tipos de puntos de E/S. La versátil combinación de puntos de E/S combinan con una gran cantidad de aplicaciones. Las entradas o salidas universales son muy flexibles y se pueden configurar tanto como entradas como salidas.

Tabla: I/O Point Types by RP-C Models

I/O Point Types

RP-C-16B-F-24V

RP-C-16B-F-230V

Universal I/O

Type Ub

8

8

Solid-state relay outputs

(MOSFET)

4

4

Relay outputs

Form A

3

3

High power relay outputs

Form C

1

1

Tabla: Configurations by I/O Point Types

Configurations

Universal I/O

Type Ub

Solid-state Relay Outputs

(MOSFET)

Relay Outputs

Form A

High Power Relay Outputs

Form C

Digital inputs

yes

-

-

-

Counter inputs

yes

-

-

-

Supervised inputs

yes

-

-

-

Voltage inputs

(0 to 10 VDC)

yes

-

-

-

Current inputs

(0 to 20 mA)

yes

-

-

-

Temperature inputs

yes

-

-

-

Resistive inputs

yes

-

-

-

2-wire RTD temperature inputs

yes

-

-

-

Voltage outputs

(0 to 10 VDC)

yes

-

-

-

Digital outputs

-

yes

yes

yes

Digital pulsed outputs

-

yes

yes

yes

PWM outputs

-

yes

yes

yes

Tristate outputs

-

yes

yes

-

Tristate pulsed outputs

-

yes

yes

-

Entradas/salidas universales

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the universal inputs/outputs.

Salidas de relés de estado sólido

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

Salidas de relé

The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.

Salida con relé de alta potencia

The high power relay output is of type Form C. The normally-open (NO) contact is ideal for switching resistive loads of up to 12 A, such as electrical heating elements. The normally-closed (NC) contact can be used to switch inductive loads of up to 3 A.

Cubiertas opcionales

Todos los modelos del RP-C pueden equiparse con cubiertas opcionales para evitar el contacto directo con los borneros y los cables.

 
action_zoom_plus_stroke RP-C con cubiertas opcionales
Figura: RP-C con cubiertas opcionales

Conexión inalámbrica

El RP-C dispone de tecnología Bluetooth de baja energía (BLE). Puede utilizar esta opción de conectividad inalámbrica para conectar el RP-C con un smartphone o una tableta que ejecute la aplicación móvil Commission o la aplicación móvil Engage para configurar el confort de la habitación.

Through Wireless Adapter - Advanced connected to the host USB port, Zigbee TM wireless connectivity can be enabled for the RP controller. The controller can extend its point count through the Zigbee wireless network and bring flexibility in your applications. The RP controller equipped with the adapter is a Zigbee Certified Product that is compliant with Zigbee 3.0. For more information on the adapter and supported wireless devices, see the Wireless Adapter - Advanced Specification Sheet.

Supervisión avanzada

The BACnet/IP controllers support local trends, schedules, and alarms, enabling local operation when the controller is offline or used in standalone applications.

The battery-free power backup of the memory and real-time clock helps prevent data loss and allows seamless and quick recovery after a power disruption.

In WorkStation, you update the firmware of multiple BACnet/IP controllers at the same time and with minimum down time. The EcoStruxure BMS server keeps track of the installed firmware to support backup, restore, and replacement of the controllers and sensors. The server can host controllers of different firmware versions.

Dos puertos RS-485 configurables

El controlador RP-C tiene dos puertos RS-485 configurables, que pueden ser configurados para soportar tres tipos diferentes de redes:

  • Sensor bus

  • Room bus

  • Red Modbus

The controller can host two networks, but only one of each network type.

One of the RS-485 ports can alternatively be configured to support BACnet MS/TP network communication with the automation server, instead of BACnet/IP. For more information, see section “BACnet MS/TP support”. The other RS-485 port can then be configured to support either sensor bus, room bus, or Modbus network.

Sensor Bus para Living Space Sensors

The BACnet/IP controllers provide an interface designed for the SpaceLogic Sensor family of living space sensors. The SpaceLogic Sensor devices offer an efficient way to sense the temperature, humidity, CO 2 , and occupancy in a room. The SpaceLogic Sensor devices are available with different combinations of sensor types and various covers and user interface options, such as touchscreen, setpoint and override buttons, and blank covers.

 
action_zoom_plus_stroke Dispositivos SpaceLogic Sensor
Figura: Dispositivos SpaceLogic Sensor

The RP controller sensor bus provides both power and communications for up to four sensors that are daisy-chained using standard Cat 5 (or higher) cables. This maximum number of sensors that can be connected to a controller is regardless of the sensor model and the combination of cover and sensor base type:

  • Blank covers: Up to four sensors of any combination of sensor base types

  • 3-button and touchscreen covers: Up to four sensors of any combination of sensor base types

  • SpaceLogic LCD temperature sensors: Up to four sensors are supported

The maximum total length of the sensor bus is 61 m (200 ft). For more information, see the SpaceLogic Sensors - SXWS Sensors for MP and RP IP Controllers - Specification Sheet.

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

Room Bus para Connected Room Solutions

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

The RP-C Pro controller room bus supports up to nine connected RP controller expansion modules with the following restrictions:

  • Maximum of two DALI light modules

  • Maximum of two SMI blind modules

  • Maximum of seven Multi-sensor or Insight-Sensor devices

Maximum total length of the room bus is 72 m (236 ft).

The RS-485 Power Adapter can be used for injecting 24 VDC from an external 24 VDC power supply to the bus. For more information, see the RS-485 Adapters Specification Sheet.

Si desea más información, consulte las hojas de especificaciones de los módulos de expansión del controlador RP.

Subred Modbus RTU

The RP controller Modbus network allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.

The Modbus RTU protocol is used for the communication. The RP controller acts as the Modbus client and the connected devices act as servers.

For connection to Modbus devices, it is recommended to use the non-isolated RS-485 adapter to provide screw termination. The adapter converts an RS-485 RJ45 interface to screw terminals. The adapter can be ordered from Schneider Electric. For more information, see the RS-485 Adapters Specification Sheet.

To connect the adapter, it is recommended that you use a Cat 5 (or higher) UTP cable with eight conductors and RJ45 connectors. The cable should be rated for the target environment and have a maximum length of 0.3 m (12 in.). The cable is not included and needs to be purchased separately.

The maximum number of Modbus devices that can be connected to an RP controller depends on the type of Modbus device and the number of Modbus registers.

The RP-C Pro controller Modbus network supports up to 20 connected Modbus devices with the following restrictions:

  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)

  • Maximum of 1,000 Modbus registers per network

64-bit Modbus registers are supported, which can be used in energy metering.

Tipos de dispositivos Modbus

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions. For information on the Modbus devices supported using Modbus device types, see the document EcoStruxure Building - Modbus Device Integration - Supported Device Brochure.

Compatibilidad con KNX

Through the KNX Modbus gateway (RP-C-EXT-KNX), the RP controller can communicate with KNX devices such as push-buttons and sensors.

The KNX Modbus gateway provides a KNX to Modbus interface that connects to one of the RP controller's configurable RS-485 ports.

For more information, see the RP-C-EXT-KNX Specification Sheet.

Compatibilidad con BACnet MS/TP

The RP controllers support both BACnet IP and MS/TP protocols. The controller can be configured to use either protocol. This feature enables both retrofitting of MNB and b3 BACnet devices while reusing parts of the existing cabling and equipment, as well as a later transition from the BACnet MS/TP (RS-485) network to an IP based network.

An RJ45 to screw terminal block adapter is required to connect the RP controller to the BACnet MS/TP network of the AS-P or AS-B server. The adapter can be ordered from Schneider Electric. The adapter is available in two models, with an isolated or non-isolated RS-485 interface. For more information, see the RS-485 Adapters Specification Sheet.

To connect the adapter, it is recommended that you use a Cat 5 (or higher) UTP cable with eight conductors and RJ45 connectors. The cable should be rated for the target environment and have a maximum length of 0.3 m (12 in.). The cable is not included and needs to be purchased separately.

In retrofit projects with MNB devices, the RP controllers can be mixed with MNB devices on the BACnet MS/TP network. The isolated adapter is used for connection of a controller. The adapter is connected to the RS-485 Com B port on the controller.

In retrofit projects with b3 BACnet devices, the RP controllers can be mixed with b3 BACnet devices on the BACnet MS/TP network. The non-isolated adapter is used for connection of a controller. The adapter can be connected to either the RS-485 Com A or Com B port on the controller.

In retrofit projects with only RP controllers on the BACnet MS/TP network, the non-isolated adapter is used for connection of a controller. The adapter can be connected to either the RS-485 Com A or Com B port on the controller.

Conectividad con aplicaciones móviles

The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP controller.

The Engage mobile application is free and available for download from Google Play and Apple App Store.

For more information, see the Engage Specification Sheet.

Aplicación móvil Comission

La aplicación móvil Commission está diseñada para la configuración local, uso de campo e iniciación de módulos BACnet/IP. La aplicación móvil reduce el tiempo de puesta en marcha, permite flexibilidad en la ejecución de proyectos y reduce la dependencia de la infraestructura de red.

The mobile application is designed for use with Android, Apple (iOS), and Microsoft Windows 10 and Windows 11 devices. For more information, see the EcoStruxure Building Commission Specification Sheet.

 
action_zoom_plus_stroke Aplicación móvil Comission
Figura: Aplicación móvil Comission

Using the Commission mobile application, you can connect to one or many RP controllers. You can connect to a single RP controller using the controller's built-in Bluetooth connectivity or using the SpaceLogic Bluetooth Adapter connected to a SpaceLogic Sensor. Using a wireless access point or a network switch, you can connect to a network of RP controllers on the local IP network.

Configuración del dispositivo

With the Commission mobile application, you can easily discover BACnet/IP controllers on the IP network. You can change the configuration of each controller, including the BACnet and IP network settings, location, and parent server. To save engineering time, you can save common device settings and then reuse them for controllers of the same model.

Despliegue en campo y comprobación E/S

The Commission mobile application does not require an EcoStruxure BMS server or a network infrastructure to be in place. You can use the mobile application to load the controller application directly into the local BACnet/IP controller and deploy the controller. The controller application can be created offline using Project Configuration Tool or WorkStation. You can use the mobile application to change the behavior of an installed standard controller application, such as configuring temperature setpoints. You can also perform an I/O checkout to verify that the controller's I/O points are configured, wired, and operating correctly.

You can perform I/O checkout on the RP controller room bus to verify proper communication over the room bus between the RP controller and the associated RP controller expansion modules. Module type mismatches or address mismatches can then be resolved. After wiring the physical inputs and outputs of the RP controller expansion modules, you can perform the following tasks on the different modules:

  • DALI light modules: discover, wink, and associate DALI lights with the logical software points, and test individual lights

  • 0-10V light modules: test individual lights

  • Blind modules: calibrate and test blinds

  • Relay module: test outputs

Soporte total en EcoStruxure Building Operation

The power of the RP controller is fully realized when it is part of an EcoStruxure BMS, which provides the following benefits:

  • WorkStation/WebStation interface

  • Script and Function Block programming options

  • Device discovery

  • Engineering efficiency

  • Preconfigured BMS applications for HVAC and Connected Room Solutions

  • Zoning option

Interfaz de WorkStation/WebStation

WorkStation and WebStation provide a consistent user experience regardless of which EcoStruxure BMS server the user is logged on to. The user can log on to the parent EcoStruxure BMS server to engineer, commission, supervise, and monitor the BACnet/IP controller and its I/O as well as its attached SpaceLogic Sensor devices. For more information, see the WorkStation and WebStation specification sheets.

Opciones de programación de Function Block y Scripts.

The fully programmable RP and MP controller models have both Script and Function Block programming options. Existing programs can easily be reused between the EcoStruxure BMS server and the controller.

Detección de dispositivos

The enhanced Device Discovery in WorkStation enables you to easily identify BACnet/IP controllers on a BACnet network and to associate the controllers with their parent server.

Eficiencia en ingeniería

The engineering and maintenance of BACnet/IP controllers can be done very efficiently using the EcoStruxure Building Operation reusability features. With these features, you can create library items (Custom Types) for a complete controller application that contains programs and all necessary objects such as trends, alarms, and schedules. The controller application in the Custom Types library is reusable across all controllers of the same model. You can use the controller application as a base for creating new controllers intended for similar applications. You can then edit the controller application, and the changes are automatically replicated to all controllers, while each controller keeps its local values.

WorkStation supports both online and offline engineering of BACnet/IP controllers. You can make the configuration changes online or use database mode to make the changes offline. In database mode, the changes are saved to the EcoStruxure Building Operation database so that you can apply the changes to the controllers later.

Project Configuration Tool enables you to perform all the engineering off site, without the need for physical hardware, which minimizes the time you need to spend on site. You can run the EcoStruxure BMS servers virtually and engineer the BACnet/IP controllers before you deploy your server and controller applications to the servers and controllers on site. For more information, see the Project Configuration Tool specification sheet.

Aplicaciones BMS preconfiguradas para soluciones de HVAC y Connected Room Solutions

To improve engineering efficiency and standardize engineering practices, fully designed and tested controller applications are available at bms-applications.schneider-electric.com for use with the RP controllers. This library contains applications for different RP controller models and application types, such as fan coil units, ceiling solutions, lights and blinds. These preconfigured controller applications are packages that include all software programs, and for example graphics, alarms, and documentation such as functional specifications and I/O wiring schedules, that are needed for your projects. The online repository can be accessed using common web browsers on Windows PCs as well as mobile devices running Apple iOS 11.3 (or later) and Android 6.0 Marshmallow (or later).

 
action_zoom_plus_stroke Página de descarga de aplicaciones BMS preconfiguradas
Figura: Página de descarga de aplicaciones BMS preconfiguradas
Opción de zonificación

The Zoning option for WorkStation and WebStation provides access to an interactive zoning tool that enables easy reconfiguration of Connected Room Solutions and flexibility when switching between zones. The WebStation zoning tool provides a graphical interface that enables quick editing of zones from any web browser device.

The RP-C-16B-F-24V and RP-C-16B-F-230V models support up to eight segments, which can be used to support rezoning in a building.

Servicios web

The RP controller uses the RESTful API, which allows IT web services to easily interact with software applications. The flexibility of the RESTful API allows the RP controller to handle multiple types of input and return different data formats. With Web services, clients can read/write data (BACnet values) directly from/to the controller. Web services use resource methods GET, PUT, POST, and DELETE to access and use the data. HTTPS is used for communication between the client and the controller.

The Web services function is disabled by default. When enabled, it requires approximately 200 kB of RP controller memory.

Tabla: Referencias para RP-C Pro

Producto

Referencia

RP-C-16B-F-24V
SXWRCF16B10001
RP-C-16B-F-230V
SXWRCF16B10002

Tabla: Números de referencia de los accesorios RP-C

Producto

Número de referencia

Optional covers
SXWRPCCOV10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001
Isolated RS-485 adapter
SXWISORS48510001
Non-isolated RS-485 adapter
SXWNISORS48510001
RS-485 power adapter
SXWNISORS485P10001
SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001
SpaceLogic Bluetooth Adapter
SXWBTAECXX10001

For more information on part numbers for Network Connectivity Accessories, see the Para obtener más información, consulte Product Selection Guide - EcoStruxure Building ..

Especificaciones

AC input
RP-C-16B-F-24V
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
30 VA
Power input protection
MOV suppression and internal fuse
RP-C-16B-F-230V
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 W
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
Overvoltage category
III
Pollution degree
2
DC input
RP-C-16B-F-24V
Nominal voltage
24 to 30 VDC
Operating voltage range
23.5 to 33 VDC
Maximum power consumption
16 W
Power input protection
MOV suppression and internal fuse
AC output
RP-C-16B-F-230V
Type
Isolated Class 2 output
Nominal voltage
24.0 VAC a
Minimum voltage
19.8 VAC a
Maximum voltage
30.8 VAC a
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
RP-C-16B-F-24V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
RP-C-16B-F-230V
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-C-16B-F-24V
0.390 kg (0.860 lb)
Weight, RP-C-16B-F-230V
0.720 kg (1.587 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Fixed
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, optional covers
0.070 kg (0.154 lb)
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 4.0.1 and later
BACnet MS/TP network support
EcoStruxure Building Operation
version 4.0.2 and later
Modbus 64-bit register support
EcoStruxure Building Operation
version 5.0.1 and later
BACnet/SC network support
EcoStruxure Building Operation
version 6.0.1 and later
Agency compliances
RP-C-16B-F-24V
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Subparts B and C, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Radio
ETSI EN 300 328 V2.2.2
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed a
FCC ID
DVE-RPC24
ISED certification number
IC: 24775-RPC24
Fire performance in air-handling spaces a
UL 2043
RP-C-16B-F-230V
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Radio
ETSI EN 300 328 V2.2.2
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3
Energy
eu.bac Certified Product (Licence No. 211113); BS/EN 15500-1
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485 port Com A
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 port Com B
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 transceiver characteristics
Transceiver type
Failsafe
  
Non-isolated
External biasing
None required
Total Unit Load (UL) per device
Maximum 0.5 UL
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
  
BACnet MS/TP, maximum bus length: 1200 m (4000 ft), maximum baud rate: 76800
  
BTL B-AAC (BACnet Advanced Application Controller) a
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.1 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB a
NOR flash memory
64 MB
Memory backup
128 kB, FRAM, non-volatile
Universal inputs/outputs
Channels
8 Ub, Ub1 to Ub8
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Universal input/output protection
Transient voltage suppressor on each universal input/output
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
150 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
1.0 mV
Impedance
1 Mohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature inputs
Supported RTDs
Pt1000, Ni1000, and LG-Ni1000
Pt1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +70 °C (-58 to +158 °F)

+/-0.5 °C (+/-0.9 °F)

0 to 50 °C (32 to 122 °F)

70 to 150 °C (158 to 302 °F)

+/-0.7 °C (+/-1.3 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-1.0 °C (+/-1.8 °F)

Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

LG-Ni1000
Sensor range
-50 to +150 °C (-58 to +302 °F)

BACnet/IP device environment

Sensor range

Measurement accuracy

0 to 50 °C (32 to 122 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

-40 to +60 °C (-40 to +140 °F)

-50 to +150 °C (-58 to +302 °F)

+/-0.5 °C (+/-0.9 °F)

RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
2.4 kohm
Source current
+4.2 mA
Sink current
-1 mA (0 to 0.4 VDC)
  
-4.2 mA (0.4 to 10 VDC)
Relay outputs, DO
Channels
3, DO5 to DO7
Contact rating
Pilot Duty (C300)
  
Resistive load: 250 VAC/30 VDC, 4 A (cos phi = 1)
  
Inductive load: 250 VAC/30 VDC, 4 A (cos phi = 0.4)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Commons
COM3 for DO5, DO6, and DO7
Isolation contact to system ground
3,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
High power relay outputs, DO
Channels
1, DO8
Contact rating
Pilot Duty (B300)
  
Minimum current: 100 mA (5 VDC)
  
Normally Open contact, resistive load: 250 VAC/24 VDC, 12 A (cos phi = 1)
  
Normally Closed contact, inductive load: 250 VAC/24 VDC, 3 A (cos phi = 0.4)
Switch type
Form C Relay
  
Single Pole Double Throw
  
Normally Open and Normally Closed
Isolation contact to system ground
5,000 VAC
Cycle life
At least 100,000 cycles
Minimum pulse width
100 ms
Solid-state relay outputs, DO
Channels
4, DO1 to DO4
Output rating
Maximum 2 A load per output
  
Maximum 4 A total load for the 4 outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
Commons
COM1 for DO1 and DO2
  
COM2 for DO3 and DO4
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC.
Common voltage range (AC)
0 to 30 VAC
Common voltage range (DC)
-30 to +30 VDC
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output

Terminales

For more information on wiring, see the SpaceLogic Hardware Reference Guide.

 
action_zoom_plus_stroke Modelo RP-C-16B-F-24V (24 VCA/CC)
Figura: Modelo RP-C-16B-F-24V (24 VCA/CC)
 
action_zoom_plus_stroke Modelo RP-C-16B-F-230V (230 VCA)
Figura: Modelo RP-C-16B-F-230V (230 VCA)

Tabla: Part Numbers for SpaceLogic Sensor Devices, Sensor Bases

Product

Part number

Sensor base with temperature sensor

SXWSBTXXXSXX

Sensor base with temperature and humidity sensors

SXWSBTHXXSXX

Sensor base with temperature and CO 2 sensors

SXWSBTXCXSXX

Sensor base with temperature, humidity, and CO 2 sensors

SXWSBTHCXSXX

Tabla: Part Numbers for SpaceLogic Sensor Devices, Covers

Product

Housing

Part number

Blank cover

Medium matte white

SXWSCBXSELXX

Blank cover

Optimum glass white

SXWSCBXSELXW

Blank cover

Optimum glass black

SXWSCBXSELXB

Blank cover with occupancy sensor

Medium matte white

SXWSCBPSELXX

Blank cover with occupancy sensor

Optimum glass white

SXWSCBPSELXW

Blank cover with occupancy sensor

Optimum glass black

SXWSCBPSELXB

3-button cover

Medium matte white

SXWSC3XSELXX

3-button cover

Optimum glass white

SXWSC3XSELXW

3-button cover

Optimum glass black

SXWSC3XSELXB

3-button cover with occupancy sensor

Medium matte white

SXWSC3PSELXX

3-button cover with occupancy sensor

Optimum glass white

SXWSC3PSELXW

3-button cover with occupancy sensor

Optimum glass black

SXWSC3PSELXB

Touchscreen display cover

Medium matte white

SXWSCDXSELXX

Touchscreen display cover

Optimum glass white

SXWSCDXSELXW

Touchscreen display cover

Optimum glass black

SXWSCDXSELXB

Touchscreen display cover with occupancy sensor

Medium matte white

SXWSCDPSELXX

Touchscreen display cover with occupancy sensor

Optimum glass white

SXWSCDPSELXW

Touchscreen display cover with occupancy sensor

Optimum glass black

SXWSCDPSELXB

Touchscreen display cover with light control buttons

Optimum glass white

SXWSC2XSELXW

Touchscreen display cover with light control buttons

Optimum glass black

SXWSC2XSELXB

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass white

SXWSC2PSELXW

Touchscreen display cover with light control buttons and occupancy sensor

Optimum glass black

SXWSC2PSELXB

Touchscreen display cover with light and blind control buttons

Optimum glass white

SXWSC4XSELXW

Touchscreen display cover with light and blind control buttons

Optimum glass black

SXWSC4XSELXB

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass white

SXWSC4PSELXW

Touchscreen display cover with light and blind control buttons and occupancy sensor

Optimum glass black

SXWSC4PSELXB

Tabla: Part Numbers for SpaceLogic Sensor Devices, Combination Models

Product

Housing

Part number

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Medium matte white

SXWSATXXXSLX

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass white

SXWSATXXXSLW

Complete SpaceLogic Sensor model with temperature sensor, buttons for override and setpoint control, and LCD display cover

Optimum glass black

SXWSATXXXSLB

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Medium matte white

SLASXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass white

SLAWXXX

Complete non-communicating a SpaceLogic Sensor model with resistive temperature sensor (10 kohm type 3 thermistor) and blank cover

Optimum glass black

SLABXXX

  1. The SpaceLogic resistive temperature sensor (SLA...) is designed to be connected to I/O points/terminals on RP or MP controllers, or I/O modules. The sensor requires an analog input (temperature input).
  • Enterprise Server
  • SpaceLogic AS-P
  • SpaceLogic AS-B
  • WorkStation
  • WebStation
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-MS-BLE
  • SpaceLogic RP-C-EXT-DALI-M-PD
  • SpaceLogic RP-C-EXT-DALI
  • SpaceLogic RP-C-EXT-0-10V-4-PD
  • SpaceLogic RP-C-EXT-0-10V-4
  • SpaceLogic RP-C-EXT-BL-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-2-LV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-4-HV-PD
  • SpaceLogic RP-C-EXT-BL-SMI-2-LV-PD
  • SpaceLogic RP-C-EXT-REL-4
  • CRS-HH-REL-10
  • RP-C-EXT-KNX
  • Adaptador inalámbrico SpaceLogic - Avanzado
  • RP-C-EXT-ZB-DALI
  • RP-C-EXT-ZB-0-10V
  • RP-C-RC-BLE
  • Puesta en marcha
  • Engage
  • Project Configuration Tool: versión 2
  • Automated Engineering Tool