earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos MP-V, RP-C, RP-V
Funcionalidades: Hardware
Versión del producto: 2022, 2023, 2024
01/11/2024

Non-isolated RS-485 Adapter

The Non-isolated RS-485 Adapter (SXWNISORS48510001) is used when connecting an RP or MP controller to the following networks:

  • BACnet MS/TP (RS-485) network including non-isolated controllers

  • Modbus RTU (RS-485) subnetwork including Modbus devices

 
action_zoom_plus_stroke Non-isolated RS-485 Adapter
Figura: Non-isolated RS-485 Adapter

The adapter converts the controller RS-485 Com port RJ45 interface to screw terminals, which is required to be able to connect the controller to a BACnet MS/TP or Modbus RTU subnetwork.

A separate connection cable is required to connect the adapter to the controller. The cable is not included and needs to be purchased separately.

BACnet MS/TP network including non-isolated controllers

The Non-isolated RS-485 Adapter is used when connecting an IP based RP or MP controller (BACnet/IP controller) to a BACnet MS/TP network that includes non-isolated controllers, such as the b3 BACnet family of zone controllers.

The adapter can be used with BACnet/IP controller models that support reconfiguration for BACnet MS/TP communication. Para obtener más información, consulte Adaptadores RS-485 SpaceLogic .

The BACnet/IP controller needs to be reconfigured to communicate with automation servers based on the BACnet MS/TP protocol, instead of the BACnet/IP protocol. Para obtener más información, consulte Allocating Flexible Ports .

Modbus RTU subnetwork including Modbus devices

The Non-isolated RS-485 Adapter is used when connecting an RP or MP controller to a Modbus RTU subnetwork that includes Modbus devices that are non-isolated or isolated.

The adapter can be used with RP and MP controller models that support Modbus RTU communication. Para obtener más información, consulte Adaptadores RS-485 SpaceLogic .

One of the controller's RS-485 port(s) needs to be configured for Modbus RTU communication. Para obtener más información, consulte Allocating Flexible Ports .

RS-485 Adapter Device Installation

The RS-485 adapter has a protruding bracket on each long side with a mounting hole to facilitate installation of the device with two screws (not included). The device can also be fastened using cable ties or mounted in line with a cable run. The RS-485 adapter is suitable for plenum use.

Para obtener más información, consulte Installing an RS-485 Adapter .

Non-isolated RS-485 Adapter Connection and Wiring

The Non-isolated RS-485 Adapter is equipped with an RJ45 port for connection to an RP or MP controller RS-485 Com port and a 4-position removable screw terminal block for connection to a BACnet MS/TP (RS-485) network or Modbus RTU (RS-485) subnetwork.

Para obtener más información, consulte Non-isolated RS-485 Adapter Connection and Wiring .

RS-485 Adapter Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RS-485 Adapters.

Para obtener más información, consulte RS-485 Adapter Regulatory Compliance and Approvals .

Especificaciones

Electrical
DC input supply voltage
0 V
Maximum power consumption
0 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Humidity
Maximum 95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043
Ingress protection rating
IP 20
Mechanical
Dimensions
See drawing below
 
action_zoom_plus_stroke
Weight
40 g (1.41 oz)
Installation
Connection to RS-485 Com A or Com B via Cat 5 UTP cable (not included) a
Installation options
The adapter can be fastened using screws or cable ties or mounted in line with a cable run. a
  
Approved for plenum installation (UL 2043)
Maximum Cat 5 UTP cable length
0.3 m (12 inches)
The Cat 5 UTP cable is not included.
Hardware
Connectors
RS-485, 4-pole removable screw terminal block
  
RS-485, RJ45 port
  • Hardware Overview
  • RS-485 Adapters
  • Adaptadores RS-485 SpaceLogic
  • RP-C BACnet MS/TP Support
  • Allocating Flexible Ports
  • Installing an RS-485 Adapter
  • Non-isolated RS-485 Adapter Connection and Wiring
  • RS-485 Adapter Regulatory Compliance and Approvals
  • RS-485 Communications
  • Wiring