earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: MP-V, RP-C, RP-V
功能: 硬件
产品版本: 2022, 2023, 2024, 7.0
2023/9/12

Isolated RS-485 Adapter

The Isolated RS-485 Adapter (SXWISORS48510001) is used when connecting a BACnet/IP controller that supports reconfiguration for BACnet MS/TP communication to a BACnet MS/TP (RS-485) network. The Isolated RS-485 Adapter has an isolated RS-485 transceiver and is used when the BACnet MS/TP (RS-485) network is comprised of isolated controllers, such as MNB BACnet devices (zone controllers) and selected others.

 
action_zoom_plus_stroke Isolated RS-485 Adapter
图: Isolated RS-485 Adapter

The adapter converts the BACnet/IP controller RS-485 Com port RJ45 interface to screw terminals, which is required to be able to connect the controller to a BACnet MS/TP network and the RS-485 Com port screw terminals of an automation server.

A separate connection cable is required to connect the adapter to the controller. The cable is not included and needs to be purchased separately.

The RS-485 Adapter can be used with BACnet/IP controller models that support reconfiguration for BACnet MS/TP communication. 有关更多信息,请参阅 SpaceLogic RS-485 A适配器 .

The BACnet/IP controller needs to be reconfigured to communicate with automation servers based on the BACnet MS/TP protocol, instead of the BACnet/IP protocol. 有关更多信息,请参阅 RP-C BACnet MS/TP Support .

RS-485 Adapter Device Installation

The RS-485 adapter has a protruding bracket on each long side with a mounting hole to facilitate installation of the device with two screws (not included). The device can also be fastened using cable ties or mounted in line with a cable run. The RS-485 adapter is suitable for plenum use.

有关更多信息,请参阅 Installing an RS-485 Adapter .

Isolated RS-485 Adapter Connection and Wiring

The Isolated RS-485 Adapter is equipped with an RJ45 port for connection to a BACnet/IP controller RS-485 Com port and a 4-position removable screw terminal block for connection to a BACnet MS/TP (RS-485) network.

有关更多信息,请参阅 Isolated RS-485 Adapter Connection and Wiring .

RS-485 Adapter Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RS-485 Adapters.

有关更多信息,请参阅 RS-485 Adapter Regulatory Compliance and Approvals .

规格

Electrical
DC input supply voltage
24 VDC (powered by the BACnet/IP controller)
Maximum power consumption
0.4 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Humidity
Maximum 95 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043
Ingress protection rating
IP 20
Mechanical
Dimensions
See drawing below
 
action_zoom_plus_stroke
Weight
80 g (2.82 oz)
Installation
Connection to RS-485 Com B via Cat 5 UTP cable (not included) a
Installation options
The adapter can be fastened using screws or cable ties or mounted in line with a cable run. a
  
Approved for plenum installation (UL 2043)
Maximum Cat 5 UTP cable length
0.3 m (12 inches)
The Cat 5 UTP cable is not included.
Hardware
Connectors
RS-485, 4-pole removable screw terminal block
  
RS-485, RJ45 port
RS-485 transceiver characteristics
Transceiver type
Failsafe
  
Isolated
External biasing
None required
Total Unit Load (UL) per device
0.18 UL
  • Hardware Overview
  • RS-485 Adapters
  • RP-C BACnet MS/TP Support
  • Installing an RS-485 Adapter
  • Isolated RS-485 Adapter Connection and Wiring
  • RS-485 Adapter Regulatory Compliance and Approvals
  • RS-485 Communications
  • Wiring