earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
硬件安装

硬件安装


产品: MP-V, RP-C, RP-V
功能: 硬件
产品版本: 2022, 2023, 2024, 7.0
2025/7/8

SpaceLogic™ RS-485 Power Adapter

Part number: SXWNISORS485P10001

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Installing the Adapter

 
action_zoom_plus_stroke

Connecting the Adapter to a Controller for RS-485 Bus Communication

通知

EQUIPMENT DAMAGE OR LOSS OF COMMUNICATION

Do not use the adapter to connect an MP or RP controller to a BACnet MS/TP (RS-485) bus for communication with an automation server.

Failure to follow these instructions can result in equipment damage or loss of communication.

 
action_zoom_plus_stroke

Connecting the Adapter to an External 24 VDC Supply for RS-485 Bus Extension for a Controller

 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.5 Nm (4.5 lbf.in)

For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

Part Numbers

Product

Part number

RS-485 power adapter (cable not included)
SXWNISORS485P10001

规格

Required external power supply ratings
Output
Regulated 24 VDC
 
action_zoom_plus_stroke
  
Isolated (non-grounded) terminals
Safety class
IEC protection class II
Output power
Minimum 3 W (125 mA)
  
Maximum 100 W or 100 VA
Maximum out port bus load
3 W
Hardware
Connectors
RS-485, 4-pole screw terminal block
  
RS-485, dual RJ45 ports
Switch
2-pole slide switch
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
  
Indoor use only
Humidity
Maximum 95 % RH non-condensing
Mechanical
Weight
24 g (0.84 oz)
Ingress protection rating
IP 20
Plastic flame rating
UL94 V-0
Plenum rating
UL 2043 (Approved for plenum installations)

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke
  • Installing an RS-485 Power Adapter
  • Convert a BACnet/IP Controller RS-485 Interface
  • RS-485 Power Adapter
  • Hardware Overview