Produkte: MP-V
Funktionen: Hardware
Produktversion: 2023, 2024, 7.0
10.03.2025

MP-V Communication Ports

arrow1_rotationEthernet Ports arrow1_rotationUSB Ports arrow1_rotationRS-485 Port

The MP-V provides the following combination of communication ports:

  • Two Ethernet ports

  • Two USB ports

  • One RS-485 port

Ethernet Ports

The two Ethernet ports are labeled:

  • Ethernet 1

  • Ethernet 2

The two Ethernet ports are 10/100BASE-TX (RJ45) ports.

The Ethernet interface is IEEE 802.3 compliant.

When both Ethernet ports are enabled, they function as an onboard Ethernet switch. Disabling the second Ethernet port disables the switching function. The switching function enables flexible network topologies. Für weitere Informationen siehe BACnet/IP Controller Network Topologies . The second port also provides a connection point for a laptop running the Commission mobile application.

Für weitere Informationen siehe Communication Port Wiring .

USB Ports

The two USB ports are of different types:

  • USB host port

  • USB device port

The USB host port is a USB 2.0 type-A port, which is rated 2.5 W. The USB host port is reserved for future use.

The USB device port is a USB 2.0 mini-B port. The USB device port is reserved for future use.

Für weitere Informationen siehe Communication Port Wiring .

RS-485 Port

Hinweis

The following description applies only for MP-V controllers with part numbers SXWMPV7AX10002 and SXWMPV9AX10002. Für weitere Informationen siehe Differences Between MP-V Hardware Versions .

The RS-485 port is labeled:

  • RS-485 Com A

The RS-485 port is rated 2 W (24 VDC).

The RS-485 port is an RJ45 port. Für weitere Informationen siehe RJ45 Pinout for the RS-485 Port of the MP-V Controller .

The RS-485 port can be configured to use one of the following two communication protocols for different types of networks:

  • Sensor bus

  • Modbus

The sensor bus is designed for communication with SpaceLogic Sensor devices. Für weitere Informationen siehe MP-V Sensor Bus .

The Modbus (RTU) network can be used for communication with standard Modbus devices. Für weitere Informationen siehe MP-V Modbus .

The RS-485 port can also be configured to support BACnet MS/TP network communication with the hosting server. Für weitere Informationen siehe MP-V BACnet MS/TP Support .

Für weitere Informationen siehe Allocating Flexible Ports .

The RS-485 port is by default configured to use the following network communication protocol:

  • Sensor bus

Für weitere Informationen siehe Communication Port Wiring .

  • Hardware Overview
  • MP-V Controllers
  • BACnet/IP Controller Network Topologies
  • MP-V Sensor Bus
  • MP-V Modbus
  • MP-V BACnet MS/TP Support
  • RJ45 Pinout for the RS-485 Port of the MP-V Controller
  • Differences Between MP-V Hardware Versions
  • Allocating Flexible Ports
  • Communication Port Wiring