Displaying a List of Devices in WebStation

You display a list of devices so that you can check the status, invalid or offline, of the devices in the system.

For example, Zigbee devices, BACnet devices like MP-C and RP-C, and Central IO modules that are invalid or offline are displayed in the list.

Mostrar más
action_close

Diagnostics in WebStation is a method of check the health of your system. Using Diagnostics you can also resolve several issues in the system, for example unconfigured trend log and forced values. You can check the following using diagnostics in WebStation:

  • Disabled alarms

  • Objects in the system that require change control

  • Offline or invalid devices

  • Objects that require uploading or downloading to be synchronized with the current configuration

  • Forced values

  • Communication issues between servers

  • Unconfigured and stopped trendlogs

  • Time and time zone settings

  • Logged in users

  • Zoning issues

To display a list of devices in WebStation
  1. In WebStation, click the Workspace menu.

  2. Expand the server.

  3. Click System .

  4. In the List view, click Diagnostics .

  5. Click Devices .

  • Diagnostics in WebStation